Default Braided Cloth Wire/ TCCW

Inspected a home today built in 58'. The sub-panel within the home had been updated to Square-D at some point. From reading previous posts I understand the pictures I've attached likely show "tin coated copper conductors" or TCCW as it may be referred to. Appears the home is partially wired with TCCW and modern romex. The two main conductors were fed from the main distribution panel located on the exterior of the home. This main panel was a FPE stab-lok panel with a 70amp main circuit breaker. I wasn't able to remove the deadfront cover since the tab the screw engaged was snapped off. I plan to recommend further evaluation of the main stab-lok distribution panel. Also planned to recommend further evaluation on the TCCW - appears pretty deteriorated - but I wanted to bounce it off some veterans. Thanks in advance.
Attached Thumbnails
braided-cloth-wire-tccw-img_4582.jpg   braided-cloth-wire-tccw-img_4583.jpg   braided-cloth-wire-tccw-img_4587.jpg   braided-cloth-wire-tccw-img_4580.jpg   braided-cloth-wire-tccw-img_4571.jpg  

Reply With Quote
Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/4/11, 9:06 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Braided Cloth Wire/ TCCW

Since that's a subpanel the EGC's and neutrals are required to be separate and the bonding screw needs to be removed. from the neutral bus. If all of those cables are in a single raceway you could have some derating issues as well.
Reply With Quote
  #3  
Old 4/4/11, 9:14 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Braided Cloth Wire/ TCCW

Some of that is older then 1958 I am sure 1958 was all copper and Plastic bushing came along I think a little later the 58 . I started in `1951 We had 25 cycle when I started the trade and wasbeing converted to 60 cy..
Tinned copper was just about over by then .
I think it could be a time to upgrade .
Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #4  
Old 4/4/11, 11:12 PM
mwolff mwolff is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Kodak, Tennessee
Posts: 47
Default Re: Braided Cloth Wire/ TCCW

Quote:
Originally Posted by Robert Meier View Post
Since that's a subpanel the EGC's and neutrals are required to be separate and the bonding screw needs to be removed. from the neutral bus. If all of those cables are in a single raceway you could have some derating issues as well.
This is a 3 wire sub panel, if you remove the bonding screw, you will no longer be grounding the enclosure. So grounds and neutrals all feed back on the bare neutral. Otherwise, lets face it, you would have no ground here. TCCW would not be a concern to me unless the insulation on it was cracked, broken, charred, or no longer pliable.
To me it looks like additional circuits have been added, and possibly could overload the feeder to this panel, which in turn, may or may not trip the FPE outside. Anyway, a 4 wire new conductor to this panel would be best if it is deteriorated, then seperate grounds and neutrals, and bring wires in through there own connections. This should have been done since it is a newer panel and would require 4 wire today.
Reply With Quote
  #5  
Old 4/5/11, 5:03 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Braided Cloth Wire/ TCCW

Quote:
Originally Posted by mwolff View Post
This is a 3 wire sub panel, if you remove the bonding screw, you will no longer be grounding the enclosure. So grounds and neutrals all feed back on the bare neutral. Otherwise, lets face it, you would have no ground here. TCCW would not be a concern to me unless the insulation on it was cracked, broken, charred, or no longer pliable.
To me it looks like additional circuits have been added, and possibly could overload the feeder to this panel, which in turn, may or may not trip the FPE outside. Anyway, a 4 wire new conductor to this panel would be best if it is deteriorated, then separate grounds and neutrals, and bring wires in through there own connections. This should have been done since it is a newer panel and would require 4 wire today.

Yes, I missed the fact that this is a 3-wire feeder and left the 4-wire part out of my post. The feeder should be replaced. So some of the potential problems:
-No 4-wire feeder
-Multiple EGC's twisted together under one screw
-Derating issue with all conductors in one raceway
-Bonded neutral bus
Reply With Quote
  #6  
Old 4/5/11, 8:27 AM
Paul Maggiore's Avatar
Paul Maggiore Paul Maggiore is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Punta Gorda, Florida
Posts: 182
Default Re: Braided Cloth Wire/ TCCW

Thanks for your input guys.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Braided Ground wire in the service panel rdrangstveit Electrical Inspections 4 4/9/10 8:48 AM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM


All times are GMT -4. The time now is 5:42 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts