Inspected a home today built in 58'. The sub-panel within the home had been updated to Square-D at some point. From reading previous posts I understand the pictures I've attached likely show "tin coated copper conductors" or TCCW as it may be referred to. Appears the home is partially wired with TCCW and modern romex. The two main conductors were fed from the main distribution panel located on the exterior of the home. This main panel was a FPE stab-lok panel with a 70amp main circuit breaker. I wasn't able to remove the deadfront cover since the tab the screw engaged was snapped off. I plan to recommend further evaluation of the main stab-lok distribution panel. Also planned to recommend further evaluation on the TCCW - appears pretty deteriorated - but I wanted to bounce it off some veterans. Thanks in advance.
|
| Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Since that's a subpanel the EGC's and neutrals are required to be separate and the bonding screw needs to be removed. from the neutral bus. If all of those cables are in a single raceway you could have some derating issues as well.
|
|
#3
|
||||
|
||||
|
Some of that is older then 1958 I am sure 1958 was all copper and Plastic bushing came along I think a little later the 58 . I started in `1951 We had 25 cycle when I started the trade and wasbeing converted to 60 cy..
Tinned copper was just about over by then . I think it could be a time to upgrade . Roy Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#4
|
|||
|
|||
|
Quote:
To me it looks like additional circuits have been added, and possibly could overload the feeder to this panel, which in turn, may or may not trip the FPE outside. Anyway, a 4 wire new conductor to this panel would be best if it is deteriorated, then seperate grounds and neutrals, and bring wires in through there own connections. This should have been done since it is a newer panel and would require 4 wire today. |
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Yes, I missed the fact that this is a 3-wire feeder and left the 4-wire part out of my post. The feeder should be replaced. So some of the potential problems: -No 4-wire feeder -Multiple EGC's twisted together under one screw -Derating issue with all conductors in one raceway -Bonded neutral bus |
|
#6
|
||||
|
||||
|
Thanks for your input guys.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Braided Ground wire in the service panel | rdrangstveit | Electrical Inspections | 4 | 4/9/10 8:48 AM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 5 | 3/25/07 10:41 PM |