Default Breaker Lockout

A Condo Board Member came by and insisted I disassemble the Breaker Lockout for the Water Heater.

I asked why?

She told me an "Electrician" told her that these lockout devices could lock the Breaker Open and "Burn down the House".

I asked here if the "Electrician" left her a written report about these?

She says well, it may not have been an "Electrician", it was someone that changed out a Water Heater for a Neighbor that told the Neighbor about the "Danger".

I can not find a recall, nor can I find anything relating to these devices being a hazard.

I left mine as is, I printed the link below and passed it on to the Board Member.

Anyone heard or these Lock Outs being problematic?




http://static.schneider-electric.us/...840-215-01.pdf
Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/14/11, 2:53 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Breaker Lockout

Brian, I am sure that you know it is virtually impossible to "lock open" (I assume... lock on) a breaker. The position of the handle has no bearing on the breaker performing it's job. If it's gonna trip, it's gonna trip.

Besides, when a breaker is "open" is when it is "off". Am I wrong here?
Reply With Quote
  #3  
Old 4/14/11, 3:09 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Breaker Lockout

Quote:
Originally Posted by jjonas View Post
Brian, I am sure that you know it is virtually impossible to "lock open" (I assume... lock on) a breaker. The position of the handle has no bearing on the breaker performing it's job. If it's gonna trip, it's gonna trip.

Besides, when a breaker is "open" is when it is "off". Am I wrong here?
I agree Jeffrey.

I think some Yahoo in a truck got this woman all excited, and I suggested she slow down on telling all the Condo Owners to remove/disassemble the Listed Breaker Lockouts.
Reply With Quote
  #4  
Old 4/14/11, 3:28 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Breaker Lockout

Open circuit no electricity, closed circuit power available.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #5  
Old 4/14/11, 3:43 PM
David Hays David Hays is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: Breaker Lockout

Just wondering why you would have a breaker lockout on a water heater.



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org
Reply With Quote
  #6  
Old 4/14/11, 3:47 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Breaker Lockout

Quote:
Originally Posted by kwood View Post
Open circuit no electricity, closed circuit power available.
Exactly!

And what I don't understand, why would the Condo WH's be "locked-out" anyway? They would have to be turned off to be locked-out. And if they were because the unit was empty, why does this person even care? Doesnt make sense to me.
Reply With Quote
  #7  
Old 4/14/11, 3:48 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Breaker Lockout

Quote:
Originally Posted by dhays View Post
Just wondering why you would have a breaker lockout on a water heater.
A locking mechanism on the circuit breaker is permitted in lieu of a within sight disconnecting means for the water heater.
Reply With Quote
  #8  
Old 4/14/11, 4:15 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Breaker Lockout

Quote:
Originally Posted by Robert Meier View Post
A locking mechanism on the circuit breaker is permitted in lieu of a within sight disconnecting means for the water heater.
Correct Robert, been that way a few years now as I recall.

In my search I can not find anything to suggest that this product does not function as intended, nor has it been the recalled.

I believe that asking all the Condo Owners to remove/disassemble these lockouts is Bad Advice.
Reply With Quote
  #9  
Old 4/14/11, 4:21 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Breaker Lockout

Quote:
Originally Posted by bkelly2 View Post

I believe that asking all the Condo Owners to remove/disassemble these lockouts is Bad Advice.
I agree, as mentioned the CB is designed to trip even if locked in the Closed or ON position. There are sections of the NEC that actually require CB's to be locked in the ON position. Sounds like the electrician is mistaken in his analysis.
Reply With Quote
  #10  
Old 4/14/11, 4:33 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Breaker Lockout

Quote:
Originally Posted by Robert Meier View Post
I agree, as mentioned the CB is designed to trip even if locked in the Closed or ON position. There are sections of the NEC that actually require CB's to be locked in the ON position. Sounds like the electrician is mistaken in his analysis.
I am not sure it was even an Electrician Robert, it was some guy that changed out a Neighbors Water Heater. (I believe an Electrician would know better)

I got the info third hand myself and suggested to the Woman that told me, she may want to reconsider advising all the Condo Owners that they should remove/disassemble the Lockout due to it being a Fire/Safety Hazard, because that is not true.

Removing it makes it a Shock Hazard though for anyone working on the Water Heaters.

Last edited by bkelly2; 4/14/11 at 4:46 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
Re-Inspection apolillo Electrical Inspections 7 11/14/09 7:01 PM
Breaker Question mhawley Electrical Inspections 5 1/14/08 3:25 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 2:05 PM