The air handler unit at todays inspection is a Lennox unit with a 7.5 KW heat strips. The unit was drawing 35.2 amps and was on a 100 amp breaker.
The homeowner said he would replace the breaker and wanted to know what size breaker to install. My question is what size breaker should it be on and am I correct by writing it up as being on an oversized breaker and succeptible to damage. I tried calling the manufacturer and was on hold forever. Thanks in advance Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details. Priority Home Inspections, Inc. 321-368-9921 www.BrevardHomeInspector.com www.AvoidAMoneyPit.com www.BrevardInsuranceSavings.com www.BrevardBuildersWarranty.com www.PrioritySignPosts.com Info@BrevardHomeInspector.com |
|
#2
|
|||
|
|||
|
What size breaker did the data plate call for? That is the correct size to install.
You are correct to write it up if the breaker is not sized per the manufacturers instructions. Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties. Abraham Lincoln www.qualityhomeinspectionsfl.com |
|
#3
|
||||
|
||||
|
Quote:
|
|
#4
|
|||
|
|||
|
David & Blaine
Thank you very much for your reply. I did not get the info off of the data plate. I usually take photos of the data plates. I only took a pic of the condensing unit data plate I forgot the AHU data plate. I will advise the homeowner to look at the plate or make a trip back out to the home. Thanks again for your reply Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details. Priority Home Inspections, Inc. 321-368-9921 www.BrevardHomeInspector.com www.AvoidAMoneyPit.com www.BrevardInsuranceSavings.com www.BrevardBuildersWarranty.com www.PrioritySignPosts.com Info@BrevardHomeInspector.com |
|
#5
|
|||
|
|||
|
Shooting from the hip, I would think a 40 amp would do. Ahh, I better go back out there.
Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details. Priority Home Inspections, Inc. 321-368-9921 www.BrevardHomeInspector.com www.AvoidAMoneyPit.com www.BrevardInsuranceSavings.com www.BrevardBuildersWarranty.com www.PrioritySignPosts.com Info@BrevardHomeInspector.com |
|
#6
|
|||
|
|||
|
Quote:
It is also advisable to make a standard practice of checking that the circuit breaker in the service panel, or at the equipment disconnect is rated within the manufacturers specs. Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties. Abraham Lincoln www.qualityhomeinspectionsfl.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 2 | 1/8/11 8:04 PM |
| AC Unit Maximum Breaker | jchamp | Inspecting HVAC Systems | 17 | 11/28/10 2:10 AM |
| Electrical Guru Question? Breaker lock outs | pdoane | Electrical Inspections | 4 | 9/7/07 3:05 PM |
| Double Tapped Breaker | tjohnson3 | Electrical Inspections | 8 | 4/20/07 10:04 AM |