The air handler unit at todays inspection is a Lennox unit with a 7.5 KW heat strips. The unit was drawing 35.2 amps and was on a 100 amp breaker.

The homeowner said he would replace the breaker and wanted to know what size breaker to install.

My question is what size breaker should it be on and am I correct by writing it up as being on an oversized breaker and succeptible to damage. I tried calling the manufacturer and was on hold forever.

Thanks in advance



Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details.



Priority Home Inspections, Inc.
321-368-9921

www.BrevardHomeInspector.com
www.AvoidAMoneyPit.com
www.BrevardInsuranceSavings.com
www.BrevardBuildersWarranty.com
www.PrioritySignPosts.com

Info@BrevardHomeInspector.com
Reply With Quote
  #2  
Old 1/14/08, 3:43 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Breaker Question

What size breaker did the data plate call for? That is the correct size to install.

You are correct to write it up if the breaker is not sized per the manufacturers instructions.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #3  
Old 1/14/08, 3:45 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Breaker Question

Quote:
Originally Posted by mhawley
The air handler unit at todays inspection is a Lennox unit with a 7.5 KW heat strips. The unit was drawing 35.2 amps and was on a 100 amp breaker.

The homeowner said he would replace the breaker and wanted to know what size breaker to install.

My question is what size breaker should it be on and am I correct by writing it up as being on an oversized breaker and succeptible to damage. I tried calling the manufacturer and was on hold forever.

Thanks in advance
The recommended breaker size should be noted on the manufacturers data tag inside the casing somewhere.
Reply With Quote
  #4  
Old 1/14/08, 4:20 PM
Mathew Hawley Mathew Hawley is offline
Active Poster
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Breaker Question

David & Blaine

Thank you very much for your reply. I did not get the info off of the data plate. I usually take photos of the data plates. I only took a pic of the condensing unit data plate I forgot the AHU data plate.

I will advise the homeowner to look at the plate or make a trip back out to the home.

Thanks again for your reply



Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details.



Priority Home Inspections, Inc.
321-368-9921

www.BrevardHomeInspector.com
www.AvoidAMoneyPit.com
www.BrevardInsuranceSavings.com
www.BrevardBuildersWarranty.com
www.PrioritySignPosts.com

Info@BrevardHomeInspector.com
Reply With Quote
  #5  
Old 1/14/08, 4:22 PM
Mathew Hawley Mathew Hawley is offline
Active Poster
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Breaker Question

Shooting from the hip, I would think a 40 amp would do. Ahh, I better go back out there.



Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details.



Priority Home Inspections, Inc.
321-368-9921

www.BrevardHomeInspector.com
www.AvoidAMoneyPit.com
www.BrevardInsuranceSavings.com
www.BrevardBuildersWarranty.com
www.PrioritySignPosts.com

Info@BrevardHomeInspector.com
Reply With Quote
  #6  
Old 1/14/08, 4:25 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Breaker Question

Quote:
Originally Posted by mhawley
Shooting from the hip, I would think a 40 amp would do. Ahh, I better go back out there.
Good idea. The data plate on my Lennox A/H with 10kw calls for a minimum 50 and a maximum 60 amp breaker.

It is also advisable to make a standard practice of checking that the circuit breaker in the service panel, or at the equipment disconnect is rated within the manufacturers specs.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
AC Unit Maximum Breaker jchamp Inspecting HVAC Systems 17 11/28/10 2:10 AM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 3:05 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 10:04 AM


All times are GMT -4. The time now is 9:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts