I inspected a home yesterday the had a 60 amp breaker in the distribution panel for the air conditioners. This fed another breaker panel near the condensing units that had one 35 amp breaker and one 45 amp breaker (the max breaker sizes for the units) installed for the condensing units.

Does this meet the requirements or should I recommend having an electrician inspect it?



Robert Sole



407-637-7288


Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #2  
Old 11/23/08, 5:58 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: Breaker Question

It should be OK. The chance of both breakers using the maximum at the same time is slim.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #3  
Old 11/23/08, 6:03 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 152
Default Re: Breaker Question

Thanks for the reply. I didn't address it with the buyer but wanted to make sure I was looking at it correctly.



Robert Sole



407-637-7288


Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #4  
Old 11/23/08, 6:41 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,032
Default Re: Breaker Question

Typically, the condensers are fed by individual circuits, but that's not necessarily required. I would have been more concerned with the minimum circuit ampacity rating for each unit.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 11/23/08, 9:51 PM
John E. Gibson, #2 John E. Gibson, #2 is offline
New User
 
Join Date: Nov 2007
Posts: 12
Please Note: John E. Gibson, #2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Breaker Question

Is the wiring the right size for the breakers. The 60 amp would need a #4 wire coming out of it and the 35 amp breaker would need a #8 wire, and the 45 amp breaker will need a #6 or bigger in all three cases.

John
Reply With Quote
  #6  
Old 11/23/08, 10:41 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 137
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Breaker Question

Quote:
Originally Posted by John E. Gibson, #2 View Post
Is the wiring the right size for the breakers. The 60 amp would need a #4 wire coming out of it and the 35 amp breaker would need a #8 wire, and the 45 amp breaker will need a #6 or bigger in all three cases.

John
It may be ligit or not depending on which type of conductor it used and also in the A/C compressor motours they have diffrent rating to determed the correct size conductor per manufacter nameplate it will listed max fuse or circuit breaker listing on it and also min running or running amp list.

The NEC code cover this pretty well it will be in Art 430 and 440

Most electricians will wired min { running amps } and max ocpd listed

Merci,Marc
Reply With Quote
  #7  
Old 11/23/08, 10:57 PM
GARY R. EVANS GARY R. EVANS is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Coconut Creek, FL
Posts: 45
Default Re: Breaker Question

The breaker for air conditioners and motor loads do not need to match the wire size. For example the a/c nameplate reads max. breaker size 40amps and the min. wire size #10. The breaker is for short circuit protection. a/c compressors and motors have internal protection or in some cases motor starters that protect the wire. The wire size for an a/c is 125% of the full load amps or current (FLA or FLC) the breaker size is 175% of the FLA or FLC.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sprinkler System Vacuum Breaker Valve sbenson Plumbing 5 9/12/08 3:41 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical 4 9/7/07 3:05 PM
Double Tapped Breaker tjohnson3 Electrical 8 4/20/07 10:04 AM
AC Unit Maximum Breaker jchamp HVAC 7 4/15/06 5:13 PM


All times are GMT -4. The time now is 3:31 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts