#1
|
||||
|
||||
|
I inspected a home yesterday the had a 60 amp breaker in the distribution panel for the air conditioners. This fed another breaker panel near the condensing units that had one 35 amp breaker and one 45 amp breaker (the max breaker sizes for the units) installed for the condensing units.
Does this meet the requirements or should I recommend having an electrician inspect it? Robert Sole, CMI 407-637-7288 Florida license numbers HI 169 and MRSA 92 Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties. RobertSole@REMinspections.com Check out my blog orlandohomeinspections.info/ REMinspections.com OrlandoHomeInspector.net |
|
#2
|
||||
|
||||
|
Please Note:
rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
It should be OK. The chance of both breakers using the maximum at the same time is slim.
|
|
#3
|
||||
|
||||
|
Thanks for the reply. I didn't address it with the buyer but wanted to make sure I was looking at it correctly.
Robert Sole, CMI 407-637-7288 Florida license numbers HI 169 and MRSA 92 Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties. RobertSole@REMinspections.com Check out my blog orlandohomeinspections.info/ REMinspections.com OrlandoHomeInspector.net |
|
#4
|
||||
|
||||
|
Typically, the condensers are fed by individual circuits, but that's not necessarily required. I would have been more concerned with the minimum circuit ampacity rating for each unit.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
|||
|
|||
|
Please Note:
John E. Gibson, #2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Is the wiring the right size for the breakers. The 60 amp would need a #4 wire coming out of it and the 35 amp breaker would need a #8 wire, and the 45 amp breaker will need a #6 or bigger in all three cases.
John |
|
#6
|
|||
|
|||
|
Please Note:
Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The NEC code cover this pretty well it will be in Art 430 and 440 Most electricians will wired min { running amps } and max ocpd listed Merci,Marc |
|
#7
|
|||
|
|||
|
The breaker for air conditioners and motor loads do not need to match the wire size. For example the a/c nameplate reads max. breaker size 40amps and the min. wire size #10. The breaker is for short circuit protection. a/c compressors and motors have internal protection or in some cases motor starters that protect the wire. The wire size for an a/c is 125% of the full load amps or current (FLA or FLC) the breaker size is 175% of the FLA or FLC.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AC Unit Maximum Breaker | jchamp | Inspecting HVAC Systems | 17 | 11/28/10 1:10 AM |
| Sprinkler System Vacuum Breaker Valve | sbenson | Plumbing Inspections | 5 | 9/12/08 2:41 PM |
| Electrical Guru Question? Breaker lock outs | pdoane | Electrical Inspections | 4 | 9/7/07 2:05 PM |
| Double Tapped Breaker | tjohnson3 | Electrical Inspections | 8 | 4/20/07 9:04 AM |