Default breaker-wire connection

I inspected a bank owned foreclosure recently, and in the main electrical panel I found the following condition.
All breakers appeared to be the same, with the exception of the one pictured. I noted my observations, etc in the report.
What areas of concern or observations can you make out in the picture? The wire connection is not the same as any others or does not appear to be the same to me.
Attached Thumbnails
breaker-wire-connection-elec-panel-medium-.jpg.jpg
Views:	165
Size:	78.6 KB
ID:	43160  



Jamie R Wilks
North Star Home Inspections
VCHI #3380000351
InterNACHI #05081596
Reply With Quote
Need a home inspection in Rhode Island? Check out InterNACHI's listing of Rhode Island certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/18/11, 1:22 PM
John E. Mullarkey John E. Mullarkey is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Sarasota, Fl
Posts: 349
Default Re: breaker-wire connection

It appears to be a different type of breaker. Is it allowed for that panel? Also you have an uncoded white conductor going nto the breaker above.
Reply With Quote
  #3  
Old 3/18/11, 2:12 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: breaker-wire connection

20 AMP breaker 16 gauge or may be 14 gauge wire not acceptable and connected above the proper connector on the wrong side with no right hand electrical standard turn for proper attachment even if it was passed this is not according to proper installations today.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #4  
Old 3/18/11, 4:42 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: breaker-wire connection

I see no problem with the exception of it may be a CB not listed for use in this panel. The re-identification of the white conductor wasn't required until the adoption of the 2008 NEC, so given the age of the panel it probably is not an issue. From the photo I'm assuming that the conductor is a #12 AWG.
Reply With Quote
  #5  
Old 3/18/11, 5:11 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: breaker-wire connection

I agree with Robert, no issue unless the breaker is not listed for use in that panel. The wire can be on either side of the screw head.
Reply With Quote
  #6  
Old 3/20/11, 12:56 AM
Rollie Meyers Rollie Meyers is offline
New User
 
Join Date: Jul 2007
Location: People's Republic of Chico,CA
Posts: 40
Please Note: Rollie Meyers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: breaker-wire connection

The panel is a 1970's I-T-E, the breakers are Bryant & the single pole is a Crouse-Hinds/ Murray, do not think the breakers are UL classified for the panel.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM


All times are GMT -4. The time now is 5:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts