Breakers are feed with aluminum wiring. The markings on the breaker say, CLT? Are these rated for aluminum?
"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
| Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
CTL is a model or style, UL Listing Code and so on. If the breaker is rated for AL wiring it will say things like
AL/CU, AL, AL9CU and so on....I dont believe CTL means anything in regards to the acceptance of AL wiring. U.L. Listed suitable for use as service equipment, complies fully with NEC and UL requirements for Class CTL From UL- CTL Circuit Breaker — has physical size, configuration or other means which, in conjunction with the physical means provided in a Class CTL assembly, is designed to prevent the installation of more circuit breaker poles than the number for which the assembly is designed and rated. Paul W. Abernathy Last edited by pabernathy; 4/16/09 at 9:18 PM.. |
|
#3
|
||||
|
||||
|
"CTL means "Circuit Total Limiting". "Circuit Total Limiting" (CTL) was introduced when the words "A lighting and appliance branch-circuit panelboard shall be provided with physical means to prevent the installation of more overcurrent devices than that number for which the panelboard was designed, rated, and approved" was added to Section 384-15 in the 1965 NEC".
Circuit Breakers: CTL Assemblies Mike Holt Belleville Home Inspector Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#4
|
||||
|
||||
|
Paul
The breakers had no other markings? "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#5
|
|||
|
|||
|
Then assume CU only and 60 Degree Ampacity ratings.
Paul W. Abernathy |
|
#6
|
||||
|
||||
|
CU only means copper connections correct? Did an inspection that had aluminum wiring with these types of breakers.
"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#7
|
||||
|
||||
|
CU means "copper," yes. AL means "aluminum." Some will be marked CU/AL - copper or aluminum.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
I have never seen a termination that was not marked for cu or al or both. The markings are probably on the side or near the termination, where they can't be seen without removing the breaker. I seriously doubt there are residential breakers out there not rated for both.
|
|
#9
|
|||
|
|||
|
Brian I a not sure but in an older breaker that has no markings at all on it ( yes, there are some out there ) might not have a temp rating, Conductor type or even an AIC rating....so we ( in the teaching world ) assume 60 Degree, CU and 5,000 AIC when it is not showing anything.