Old 4/16/09, 8:58 PM
nbhi's Avatar
nbhi nbhi is offline
Default Breakers
Breakers are feed with aluminum wiring. The markings on the breaker say, CLT? Are these rated for aluminum?
"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison
www.newbeginningshomeinspection.com
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
Old 4/16/09, 9:12 PM
Default Re: Breakers
CTL is a model or style, UL Listing Code and so on. If the breaker is rated for AL wiring it will say things like
AL/CU, AL, AL9CU and so on....I dont believe CTL means anything in regards to the acceptance of AL wiring.
U.L. Listed suitable for use as service equipment, complies fully with NEC and UL requirements for Class CTL
From UL- CTL Circuit Breaker — has physical size, configuration or other means which, in conjunction with the physical means provided in a Class CTL assembly, is designed to prevent the installation of more circuit breaker poles than the number for which the assembly is designed and rated.
Paul W. Abernathy
Old 4/16/09, 9:26 PM
Christopher Currins's Avatar
"CTL means "Circuit Total Limiting". "Circuit Total Limiting" (CTL) was introduced when the words "A lighting and appliance branch-circuit panelboard shall be provided with physical means to prevent the installation of more overcurrent devices than that number for which the panelboard was designed, rated, and approved" was added to Section 384-15 in the 1965 NEC".
Circuit Breakers: CTL Assemblies Mike Holt
Belleville Home Inspector
Christopher Currins
Certified, Licensed
Old 4/16/09, 9:43 PM
nbhi's Avatar
Paul
The breakers had no other markings?
Old 4/16/09, 9:44 PM
Then assume CU only and 60 Degree Ampacity ratings.
Paul W. Abernathy
Old 4/21/09, 9:39 PM
nbhi's Avatar
CU only means copper connections correct? Did an inspection that had aluminum wiring with these types of breakers.
Old 4/21/09, 10:47 PM
Jeffrey R. Pope's Avatar
CU means "copper," yes. AL means "aluminum." Some will be marked CU/AL - copper or aluminum.
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 4/22/09, 9:42 PM
I have never seen a termination that was not marked for cu or al or both. The markings are probably on the side or near the termination, where they can't be seen without removing the breaker. I seriously doubt there are residential breakers out there not rated for both.
Old 4/23/09, 7:04 PM
Brian I a not sure but in an older breaker that has no markings at all on it ( yes, there are some out there ) might not have a temp rating, Conductor type or even an AIC rating....so we ( in the teaching world ) assume 60 Degree, CU and 5,000 AIC when it is not showing anything.
Paul W. Abernathy
FYI - Counterfeit Circuit Breakers Recalled By Specialty Lamp International Due to Fi rmaday Electrical Inspections 0 5/28/08 10:03 AM
Counterfeit Breakers jallingham Electrical Inspections 0 5/27/08 4:25 PM