Default Breakers with lockouts

Would a breaker with a lockout be OK for installation under the latest NEC for an airhandler installed out of view of the panel with no other disconnect except in the unit?
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/21/11, 5:50 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Breakers with lockouts

Without looking it up, I'd say yes. It is OK to do a water heater that way.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 3/21/11, 5:53 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Breakers with lockouts

Yes,
Why the Lockout (LOTO) would be Present.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #4  
Old 3/21/11, 6:49 PM
Brian C. Hoagland Brian C. Hoagland is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Cocoa, FL
Posts: 3,410
Default Re: Breakers with lockouts

I thought they were going to do away with that in favor of in sight disconnects. New construction today I was just double checking, I don't have a copy of the NEC for the 2007 Fl. code and revision.
Reply With Quote
  #5  
Old 3/21/11, 7:08 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Breakers with lockouts

Yes, unless changed. Happened to me about 7 years ago building a school cafeteria kitchen and we had no room for the 200 amp disconnect for the water booster in the kitchen.
Electric inspector allow us to have a lockout tag out breaker on the main panel.
Reply With Quote
  #6  
Old 3/21/11, 7:22 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Breakers with lockouts

I am only Referencing what I know
from Commercial Industrial Petrochemical Work
LOTO
at the Source with Lock of Contactor and Each Individual Working
Company Lock
can only be removed
after all others



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #7  
Old 3/21/11, 7:29 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Breakers with lockouts

Quote:
Originally Posted by bhoagland View Post
Would a breaker with a lockout be OK for installation under the latest NEC for an airhandler installed out of view of the panel with no other disconnect except in the unit?
If the disconnect is within the unit then nothing else is required.
Reply With Quote
  #8  
Old 3/21/11, 7:34 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Breakers with lockouts

Robert, I have always seen a disconnect with the Air handlers, is that a specification item by the engineer or just standard by the manufacturers?

Reply With Quote
  #9  
Old 3/21/11, 7:40 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Breakers with lockouts

Quote:
Originally Posted by mcyr View Post
Robert, I have always seen a disconnect with the Air handlers, is that a specification item by the engineer or just standard by the manufacturers?

Good question. I'm unsure if it's a design option required by the engineer writing the specifications or not. Could also be part of the listing but I don't really know. Here's a photo of an integral disconnect within the unit:

Reply With Quote
  #10  
Old 3/21/11, 7:45 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Breakers with lockouts

Yes I am familiar with them. Always took it for granted that a disconnect is on the unit. I have seen in instances, depending on the equipment, that a disconnect is mounted on a pedestal near or on the unit also.
A service outlet is always required also. WP Thanks
Reply With Quote
  #11  
Old 3/21/11, 8:33 PM
Brian C. Hoagland Brian C. Hoagland is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Cocoa, FL
Posts: 3,410
Default Re: Breakers with lockouts

Quote:
Originally Posted by Robert Meier View Post
If the disconnect is within the unit then nothing else is required.
I beg to differ with you on this, I would not approve it without the lockout on the breaker since the circuit would be active through the frame and the internal connections not visible. I would have preferred that a seperate pull type or breaker or even a switch be installed as a disconnect within view of the unit so that sevice personell could be certain the power could not be turned on. Code or not.
Reply With Quote
  #12  
Old 3/21/11, 8:38 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Breakers with lockouts

http://www.osha.gov/SLTC/controlhaza...rgy/index.html

If having employees.... essential
to be familiar with...



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #13  
Old 3/21/11, 8:39 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Breakers with lockouts

Quote:
Originally Posted by bhoagland View Post
I beg to differ with you on this, I would not approve it without the lockout on the breaker since the circuit would be active through the frame and the internal connections not visible. I would have preferred that a seperate pull type or breaker or even a switch be installed as a disconnect within view of the unit so that sevice personell could be certain the power could not be turned on. Code or not.
Preferred and required are two different things. An integral disconnecting means satisfies the requirement and is permitted without any additional external disconnecting means by the NEC.
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/27/11, 10:57 AM
Rollie Meyers Rollie Meyers is offline
New User
 
Join Date: Jul 2007
Location: People's Republic of Chico,CA
Posts: 40
Please Note: Rollie Meyers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Breakers with lockouts

Quote:
Originally Posted by Robert Meier View Post
Good question. I'm unsure if it's a design option required by the engineer writing the specifications or not. Could also be part of the listing but I don't really know. Here's a photo of an integral disconnect within the unit:

That would not qualify as a disconnect since there is no means to lock it out, it is just a switch..
Reply With Quote
  #15  
Old 3/27/11, 1:30 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Breakers with lockouts

Quote:
Originally Posted by Rollie Meyers View Post
That would not qualify as a disconnect since there is no means to lock it out, it is just a switch..

The locking provision is if it's not within sight of the equipment. A unit switch on or in the equipment does not require a locking means. Same thing would apply to a disconnect within sight of the equipment, no locking means required.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Siemens recalls circuit breakers due to fire hazard. gromicko Electrical Inspections 3 9/24/10 7:36 AM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
Counterfeit Breakers jallingham Electrical Inspections 0 5/27/08 4:25 PM


All times are GMT -4. The time now is 5:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts