Default Bryant Panel and Gould Breakers

The Bryant sub panel I inspected today had a sticker...it specified that only Bryant breakers should be used w/ this panel...but it had several Gould breakers....any chance they are one and the same....?

Also, as long as we are in this panel....the ground and the neutral from the same circuit are double tapped into this buss.

And....anybody else have a problem w/ this exposed wiring in a bedroom closet? Seems unsafe to me

Ok...now tear me apart.

Thanks in advance.
Attached Thumbnails
bryant-panel-and-gould-breakers-511mtviewunit3-025.jpg   bryant-panel-and-gould-breakers-511mtviewunit3-056.jpg   bryant-panel-and-gould-breakers-511mtviewunit3-055.jpg  
Reply With Quote
  #2  
Old 4/25/06, 9:12 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Bryant Panel and Gould Breakers

Quote:
Originally Posted by tneumann

And....anybody else have a problem w/ this exposed wiring in a bedroom closet? Seems unsafe to me



Thanks in advance.
I don't have a problem with it as it is not my house Tony. But romex is supposed to be protected from physical damage, recommend conduit and an electrician......................................
Reply With Quote
  #3  
Old 4/25/06, 9:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Bryant Panel and Gould Breakers

All components are required to be used according to their listing and the manufacturers recommendations. Bryant panel boards should have Bryant breakers.

Grounds and neutrals cannot share the same termination in any panel (service or otherwise).

The grounding conductors are required to be bonded to the distribution (sub) panel and that bus bar is isolated (as it should be for the neutral conductors).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 4/25/06, 9:38 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bryant Panel and Gould Breakers

My thoughts exactly....well not exactly, my thoughts were much more discombobulated than yours as to be expected

Thanks Jeff...I was proud of myself for knowing that the bus bar was to be isolated as the panel is actually a "sub"......shame I cannot spell bus properly.

I am recommending sparky repair as necessary. There are other problems anyway......broken receptacles...etc.

Thanks again.
Reply With Quote
  #5  
Old 4/25/06, 9:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Bryant Panel and Gould Breakers

Quote:
Originally Posted by tneumann
I am recommending sparky repair as necessary.
I hate that statement. I hope you didn't really say that.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 4/25/06, 9:50 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bryant Panel and Gould Breakers

Actually I am recommending a licensed electrical contractor repair the specific problems I mentioned in my report.....faux pas in my post.

We should start a thread of trite HI statements.....

Appears to be....
repair as necessary....
etc....
Reply With Quote
  #7  
Old 4/25/06, 9:55 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Bryant Panel and Gould Breakers

Goes right up there with "Recommend further evaluation. . . blah, blah, blah."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 4/25/06, 10:01 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Bryant Panel and Gould Breakers

Appears Serviceable.......I like that one the best....it can be used in either direction.

The Zinsco Appeared Serviceable...... .....It was not on fire.....
Reply With Quote
  #9  
Old 4/25/06, 10:02 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bryant Panel and Gould Breakers

Near the end of its' useful life.....
Reply With Quote
  #10  
Old 4/25/06, 10:04 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Bryant Panel and Gould Breakers

"She Ain't What She Used To Be"
Reply With Quote
  #11  
Old 4/26/06, 5:49 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Bryant Panel and Gould Breakers

When it comes to electrical stuff, for which I am not a licensed electrician, I would use "Recommend further evaluation by a licensed electrician, and repair or replacement, as necessary."

I let the licensed electrician determine if repairs are practical or possible, or whether something needs to be replaced. That's where the "as necessary" part comes in.

And "Recommend further evaluation" means that because he is a licensed electrician, there is a great possibility that he might find more problems than a unlicensed, generalist nobody like me.

I had a real nice call from a licensed electrician yesterday who complimented me on my report and on the wording I used in my report, and then specifically thanked me for not trying to do the work of a licensed electrician. I asked him which report he had, and I was soooooooooo thankful for his unsolicited phone call because his Client is the one that I, for the first time ever, offered to return the Client's home inspection fee for a general release of all liability. She was the most difficult person I have ever dealt with outside of any religious schtick. So I know that if the licensed electrician was making an unsolicited, complimentary call to me, then he was probably saying good things about me to my Client. So maybe she will end up liking me after all, even though I have a distinct distaste in my mouth for her. I was sooooooooooo hoping she would sign the release form and send it back to me.



NACHI 2005 U.S. Member of the Year

Last edited by rray; 4/26/06 at 5:55 AM..
Reply With Quote
  #12  
Old 4/26/06, 11:23 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Bryant Panel and Gould Breakers

Quote:
Originally Posted by rray
When it comes to electrical stuff, for which I am not a licensed electrician, I would use "Recommend further evaluation by a licensed electrician, and repair or replacement, as necessary."
We've engaged on this matter before and you are comfortable with these statements where I am not.

Recommending "further evaluation" is simply a way of saying that you don't know how this should be corrected.

Granted, there are situations where "further evaluation" is warranted and I would even expect that to be followed up with "repair as necessary." However, these statements should not be used as a "catchall" for every defect we discover.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 4/26/06, 2:05 PM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bryant Panel and Gould Breakers

Quote:
Originally Posted by jpope
We've engaged on this matter before and you are comfortable with these statements where I am not.

Recommending "further evaluation" is simply a way of saying that you don't know how this should be corrected.

Granted, there are situations where "further evaluation" is warranted and I would even expect that to be followed up with "repair as necessary." However, these statements should not be used as a "catchall" for every defect we discover.
Jeff, As a licensed Journeyman electrician of 20 years, I could almost guarantee I could find things you didn't find or recommend things be done differently than you suggest to your client (unless you're an experienced electrician). Our job as HI's/generalists is to refer and defer to specialists when warranted, not go throwing our opinions around. Judging from your posts your a very competent HI but to volunteer specialist information based on an incomplete electrical inspection isn't wise in my opinion. Maybe I'm misunderstanding your position on this, but I would agree with Russell's statement, a competent electrician would probably have more complete evaluation skills of the entire electrical system just based on the amount of time a HI has to give the electrical portion of his inspection. Are you checking all of the branch circuit/device wiring, doing load and branch ckt.calcs, evaluating all aspects of the electrical system? If you tell your client what's wrong and exactly how to fix it and then the specialist comes in and tells them something different, who is the client going to believe? What if the repairs needed are much more extensive, will the client come back to you for the difference? If you had just defered to the specialist using generalist terms rather than specifics you limit your liability.
Reply With Quote
  #14  
Old 4/26/06, 4:36 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Bryant Panel and Gould Breakers

When I find 3 or 4 things wrong with a panel that's usually enough for me to call for further evaluation and repair/replacement as needed by qualified electrician.

Then I move on.
Reply With Quote
  #15  
Old 4/26/06, 5:38 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Bryant Panel and Gould Breakers

Quote:
Originally Posted by jpope
Recommending "further evaluation" is simply a way of saying that you don't know how this should be corrected.
Not by any stretch of the imagination. You make a bold presumption there.

What further evaluation means is that I, as a generalist, am not going to take the liability for determining how something should be corrected, especially in a licensed profession for which I hold no license. Having come from a large, poor, Catholic/Mormon family, I know how to do a lot of stuff. However, I have to resist practicing in certain professions because I am not licensed to practice in those professions. Now if California can get some licensing for home inspectors, it might be a different story.

As I also state in my report, "when I recommend further evaluation by a licensed professional, it is highly likely that such licensed professionals might find additional problems which a generalist home inspector would not. After all, California law implies that a licensed professional is, or at least should be, much more knowledgable about the profession in which he is licensed than a generalist home inspector would be."

A great example is that my E&O insurance company wants me to recommend AFCI upgrades. In many cases, such upgrades cannot be done practically or in a financially feasible way, and, quite frankly, it is stupid for me to recommend such upgrades. Of course, my E&O provider doesn't understand that because I'm not a licensed electrician. So they demand that I recommend "further evaluation by a licensed electrician" and let him make the call as to whether or not AFCI upgrades can be done in a reasonabe fashion.

So it has absolutely nothing to do with whether or not I know how to do something. In virtually every case, I do know how to do something, sometimes even better than the licensed professionals. However, I don't want to practice in their professions, and I sure don't want the additional liability for practicing in their professions. It is not unheard of for licensed professionals to report to the appropriate authorities unlicensed individuals practicing in professions that are licensed.

Of course, one should check with one's own attorneys to help determine one's own business, inspection, and reporting protocols.

Quote:
Originally Posted by jpope
However, these statements should not be used as a "catchall" for every defect we discover.
I agree. I use them only for licensed professions where I don't hold a license.



NACHI 2005 U.S. Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 2:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts