While this question is not specific to the Pushmatic Bulldog, what do you think?
Attachment 795 Attachment 796 Attachment 797 The copper stranded counductors, where connected to the breakers and neutral bus had some strands cut away in order to help the conductors fit in the holes. OK or not? I would say no. Also, about 6 splices in the panel and only 2 of the required 6 screws holding it. Seller's agent produced a letter from an 'electrician' (no license number or insurance cert on the letterhead) saying that the panel complied with NEC and local codes. Also stated that there were no splices in the panel. I, being the jerk I am, showed her the splices. She could not seem to understand that there was anything other than 'code' and a letter from G-d only know who (he was obviously no electrician). Comments. How should I write this one. BTW: I hate (personal experience) Pushmatics. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! Last edited by wdecker; 3/4/06 at 5:24 PM.. |
|
#2
|
||||
|
||||
|
Come on, guys. I need and answer.
Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#3
|
|||
|
|||
|
As far as I know.
You can not trim wires. Splices are OK as long as it's not 2 hots, neutrals or grounds spliced into one (like a pigtail) fed from a breaker or neutral/ ground bar ie. one wire feeding two circuts. All of the panel cover screws should be there. Hope this helps. Hopefully one of the resident sparkies will chime in to correct me if I am wrong. |
|
#4
|
||||
|
||||
|
Tnanks, Todd. Oh, and thanks again for the convention admission.
Owe you one and one half. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#5
|
|||
|
|||
|
My pleasure.
|
|
#6
|
||||
|
||||
|
Will,
The splices in the box are not a problem, however, reducing the wire size by trimming strands is not okay. I'm sure one of our experts can give you a reference for that. . . IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
|||
|
|||
|
Quote:
are you saying it is okay to have one wire from a breaker feed 2 circuts?? |
|
#8
|
|||
|
|||
|
I was just looking at your pics and I notice that there are wires from one buss crossing the other buss.
I am thinking this is not OK. I think they sould be routed around the bottom of the panel instead. Where are the Sparkies?? |
|
#9
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
See Table 8 in Chapter 9 in the NEC for the number of strands, either as one or 7, 19, 37, etc.
NO TRIMMING IS ALLOWED EVER! http://www.reporthost.com/tedesco/ |
|
#10
|
||||
|
||||
|
Quote:
I was speaking generally about splices in a panel box. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#11
|
|||
|
|||
|
Quote:
Thanks. |
|
#12
|
||||
|
||||
|
No, I mean I can't see pictures at all. I only see text in Wills original post.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#13
|
||||
|
||||
|
Todd,
If you are asking if two cables entering an electrical panel can have their hots co-joined with each other, and a third conductor co-jojned with them going to a circuit breaker, then the answer is yes, it can. Was this your question? |
|
#14
|
|||
|
|||
|
So, two circuts, one for the bedrooms and one for the living room can be spliced together and attached to one breaker??
That is what I wanted clarified. |
|