Default Bulldog Pushmatic

I was beginning to think these weren't sold in this area of the country. I saw my first one today. I noted some aluminum wiring, two scorched/arced terminals, and some uncapped/abandonded wiring. Anyone see anything else? It is a split bus panel rated at 100 amps. Are there any issues with the performance of this brand of equipment?
Attached Thumbnails
bulldog-pushmatic-p1260461.jpg   bulldog-pushmatic-p1260462.jpg   bulldog-pushmatic-p1260466.jpg   bulldog-pushmatic-p1260463.jpg   bulldog-pushmatic-p1260464.jpg  

Reply With Quote
  #2  
Old 4/16/07, 10:02 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,646
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bulldog Pushmatic

Double tapped ground wires and improperly marked white wires into the breakes.
Reply With Quote
  #3  
Old 4/16/07, 10:04 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Bulldog Pushmatic

Yep, saw those too. I believe the doubled grounds are OK.
Reply With Quote
  #4  
Old 4/16/07, 10:06 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bulldog Pushmatic

The double grounds are likely fine as well as the whites on breakers.
The re-marking of white wires is a relatively new code. Only a few cycles old.
Reply With Quote
  #5  
Old 4/17/07, 5:26 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Bulldog Pushmatic

Bulldog and I-T-E Pushmatics are problematic panels in my area of the country. They get ranked right behind FPE, Zinsco, and Sylvania's Zinsco. I find that the push doesn't always push properly, leaving the breaker ON when it says OFF, or leaving it OFF when it says ON. They are fun to play with, though.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #6  
Old 4/17/07, 7:30 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: Bulldog Pushmatic

Quote:
Originally Posted by rray
Bulldog and I-T-E Pushmatics are problematic panels in my area of the country. They get ranked right behind FPE, Zinsco, and Sylvania's Zinsco. I find that the push doesn't always push properly, leaving the breaker ON when it says OFF, or leaving it OFF when it says ON. They are fun to play with, though.
Gee I have seen this with other breakers also .
In my opinion there is no reason to be any more concerned then with other breakers ,
Yes they have been around for a long time .
I had them in my last home and if I found the home I liked I would not hesitate in buying it .
New breakers where still available the last time I looked more expensive then some other breakers .

Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #7  
Old 4/17/07, 8:52 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bulldog Pushmatic

Guess if I was being FRISKY I would complain about the improper termination of the AL wiring onto the binding screws. AL wiring should be terminated 3/4 of the way around the screw as a good practice to ensure good contact...but not real CODIE on that...just good practice.

Is that Grounded/Grounding terminal block BONDED to the enclosure...I just can't tell from the pictures....might be.....you have to make that call from the visual inspection.

Also can't tell but it looks like it is missing a lock ring and bushing on the SEC entering the enclosure...again can't see it all that well.

Ok.....the largest problem I found with them is COST of replacement and the fact they are just OLD......i just happen to believe ( yeah I know others don't agree...but I am WAY past giving a SH*T these days ) anything over 25-30 years old should be reported as such.....might be fine to service current needs..sure......not a problem but make aware to the client that if they have intentions to add items, expand anything their options are very limited with this enclosure.....

Will the service run the current dwelling sure....it is evident because it is running NOW......but you are bound to make the client know of future expectations and needs......this service has limitations for anything other than what it is....

But other than that....the OCPD's to seem to trip fine.......but ask yourself this...are YOU as FRISKY as you were 25 years ago.......now think of OLD breakers and modern technology......are YOU willing to put all your cards in OLD equipment...

P.S. 99% of this post is for educational purposes only.......ENJOY !



Paul W. Abernathy
Reply With Quote
  #8  
Old 4/17/07, 6:50 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bulldog Pushmatic

If PushMatic's were still made today, that would be my brand of choice. I cannot remember ever having replaced a failed PushMatic breaker due to a poor buss connection, as they bolt-on like commercial panels. That was a fine idea, on their part. They were very popular in my area. I have heard of them not turning on or off when you press them, which I have experienced from time to time. Sometimes, it takes a harder press than you'd think. I have never had a PushMatic breaker be in a different state than was indicated in the window, however. It might not have "switched" when I pressed it the first time, but I've found the indicator window to be always accurate as to the true state of the breaker. Admittedly, the design could have been better.
Reply With Quote
  #9  
Old 4/18/07, 10:28 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bulldog Pushmatic

Marc,

I think the largest downfall was the size required on THOSE specific designs.....the sticking issue is normal when you talk about something 30 years old and dust and dirt and well......TIME......we all get a little "STICKY" with time.....

But probably the reason we don't see a HUGE out cry about them is that they were SOLID.......and with a few problems but overall worked very well....

Heck....ALL the manufacturers have had issues over the years.....



Paul W. Abernathy
Reply With Quote
  #10  
Old 4/18/07, 5:31 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bulldog Pushmatic

Quote:
Originally Posted by pabernathy
But probably the reason we don't see a HUGE out cry about them is that they were SOLID.......and with a few problems but overall worked very well.....
Yes, I hope some manufacturer in the future picks up that concept and makes something like them again.
Reply With Quote
  #11  
Old 4/18/07, 10:45 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Bulldog Pushmatic

Maybe it's the weather down here that results in the Pushmatics being such garbage.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #12  
Old 4/20/07, 8:57 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bulldog Pushmatic

Quote:
Originally Posted by rray
Maybe it's the weather down here that results in the Pushmatics being such garbage.
Russel ( with one l )......could possibly be in that areas with alot of salt in the air, excessive moisture and other environmental factors could easiy play a factor into a "PUSH" style breaker possibly.....

I am not expert on those factors...but I would agree it is possible.

I was in a meeting yesterday in PA with eaton and we talked about an electrician in CA that replaces 2,000-4,000 Zinsco panels a year in your area.....at $ 4,000+ a pop....some higher...I was drooling and wanting to move to CA...you do the math on those figures......

Anyway...i am sure conditions in certain area's play an effect on alot of equipment as it does near beaches and water fronts to oceans.....



Paul W. Abernathy
Reply With Quote
  #13  
Old 4/20/07, 10:13 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Bulldog Pushmatic

Quote:
Originally Posted by pabernathy
I was in a meeting yesterday in PA with eaton and we talked about an electrician in CA that replaces 2,000-4,000 Zinsco panels a year in your area.....at $ 4,000+ a pop....some higher...I was drooling and wanting to move to CA...you do the math on those figures......
I think that the numbers have been inflated while traveling the grapevine from the west coast to the east coast.

The highest figure I've ever heard of for replacing a Zinsco panel was $2,735 (parts and labor), and I'm the one who paid that because it was an emergency situation on a holiday weekend. Those triple charges on holiday weekends are he11.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 4/20/07, 5:44 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bulldog Pushmatic

Quote:
Originally Posted by rray
I think that the numbers have been inflated while traveling the grapevine from the west coast to the east coast.

The highest figure I've ever heard of for replacing a Zinsco panel was $2,735 (parts and labor), and I'm the one who paid that because it was an emergency situation on a holiday weekend. Those triple charges on holiday weekends are he11.
Got it straight from the MOUTH of the guy.......maybe he was compensating BUT I know he wanted Eaton to manufacturer him a panel JUST for his company.....and did not care if the panels cost $ 700-800 a piece....so I don't know......not sure which part of the area he is in...only passing on the info russel ( with (1) l )



Paul W. Abernathy
Reply With Quote
  #15  
Old 4/20/07, 9:29 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Bulldog Pushmatic

Quote:
Originally Posted by pabernathy
Got it straight from the MOUTH of the guy.......maybe he was compensating
Perhaps a little bragodocio involved. He wanted all the rest of you to be slightly jealous of how much money he (claimed he) was making.



NACHI 2005 U.S. Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pushmatic and service size help cbrands Electrical Inspections 10 9/23/07 9:55 PM
ITI Pushmatic panel prussell Electrical Inspections 6 4/30/07 1:43 PM
PushMatic Circuit Breakers lewens Electrical Inspections 5 8/17/06 9:59 AM
Pushmatic panel orientation bsmith Electrical Inspections 7 2/2/06 10:01 PM


All times are GMT -4. The time now is 2:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts