Default Bulldog Pushmatic panel main bus bar terminals

What are the two terminals above the main breaker used for? For adding a distribution panel ?

In this case there supplying the water heater breaker, which I know isn't right, but I was just curious what they would be used for.

Thanks in advance.
Attached Thumbnails
bulldog-pushmatic-panel-main-bus-bar-terminals-7757-providence-neapolis-swanton-road-120.jpg  
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #2  
Old 7/1/09, 10:55 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 4,961
Default Re: Bulldog Pushmatic panel main bus bar terminals

I'm not sure what they were intended for, but they were certainly NOT intended for a direct tap like that. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 7/2/09, 12:11 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bulldog Pushmatic panel main bus bar terminals

I have not observed idea why they have terminal screws there either ,but am also wondering why there are fuses on the right side of the picture with red wire behind them.
Reply With Quote
  #4  
Old 7/2/09, 12:30 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 4,961
Default Re: Bulldog Pushmatic panel main bus bar terminals

Spare parts, is my guess. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 7/2/09, 11:08 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,721
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Bulldog Pushmatic panel main bus bar terminals

Hi to all,

I'm just not seeing a problem there, the top breaker is back-feeding the panel, and the top lugs are feeding the adjacent breaker panel that's all.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #6  
Old 7/2/09, 11:18 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,663
Default Re: Bulldog Pushmatic panel main bus bar terminals

Quote:
Originally Posted by gbeaumont View Post
Hi to all,

I'm just not seeing a problem there, the top breaker is back-feeding the panel, and the top lugs are feeding the adjacent breaker panel that's all.

Regards

Gerry

Gerry, my eyes cannot see where the wires go but, Joshua said:

Quote:
Originally Posted by jfrederick View Post
What are the two terminals above the main breaker used for?

In this case there supplying the water heater breaker...



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #7  
Old 7/2/09, 12:11 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 264
Send a message via AIM to jfrederick
Default Re: Bulldog Pushmatic panel main bus bar terminals

The wires were feeding the water heater breaker panel in the lower right corner.
Reply With Quote
  #8  
Old 7/2/09, 12:15 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,721
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Bulldog Pushmatic panel main bus bar terminals

Quote:
Originally Posted by lkage View Post
Gerry, my eyes cannot see where the wires go but, Joshua said:
I hear you Larry, I had to blow it up, but that's where they go.

As to the intent of the top lugs, I don't know, maybe it was designed for the configuration it is in, my point was that electrically there appears to be nothing wrong with the set up as the main will disconnect those lugs.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #9  
Old 7/2/09, 12:31 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bulldog Pushmatic panel main bus bar terminals

Quote:
Originally Posted by gbeaumont View Post
I hear you Larry, I had to blow it up, but that's where they go.

As to the intent of the top lugs, I don't know, maybe it was designed for the configuration it is in, my point was that electrically there appears to be nothing wrong with the set up as the main will disconnect those lugs.

Regards

Gerry
Makes sense as the feeders go straight to the main and not the breaker bar.
Reply With Quote
  #10  
Old 7/2/09, 12:38 PM
Andrew Rook Andrew Rook is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Hamilton, NJ
Posts: 199
Default Re: Bulldog Pushmatic panel main bus bar terminals

Quote:
Originally Posted by gbeaumont View Post

and the top lugs are feeding the adjacent breaker panel that's all.
So what protects these wires from overcurrent and possible fire?



Andrew Rook
NJ Home Inspector
License # 24GI00063600

Rook Home Inspections LLC
Hamilton NJ
(609) 588 - 0125
www.RookInspections.com
www.MercerCountyHomeInspection.com

Be Smart, Be Sure, Be Inspected TM
Reply With Quote
  #11  
Old 7/2/09, 12:45 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 4,961
Default Re: Bulldog Pushmatic panel main bus bar terminals

I don't like it.

I hear what you're saying Gerry, but (IMHO) there should be no direct taps from those bus bars. I know it's a short run, but those 12AWG or 10AWG conductors are essentially "protected" by a 100 amp (guessing) breaker.

It's been my experience that taps to the bus bars are generally reserved for components "within" the same panel, such as with split bus panels.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #12  
Old 7/2/09, 3:33 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,721
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Bulldog Pushmatic panel main bus bar terminals

Quote:
Originally Posted by jpope View Post
I don't like it.

I hear what you're saying Gerry, but (IMHO) there should be no direct taps from those bus bars. I know it's a short run, but those 12AWG or 10AWG conductors are essentially "protected" by a 100 amp (guessing) breaker.

It's been my experience that taps to the bus bars are generally reserved for components "within" the same panel, such as with split bus panels.
I hear you Jeff, the conductors appear to be 10's minimum as they are stranded, they could be an 8 but I don't think so, the panel they feed is reported as a water heater which are normally 30 amp, I would contend that the feeders are drawing their overcurrent protection from the water heater breaker rather than the 100 amp main.

I'm like you I can rationalise it all day long, but it still "looks" wrong, maybe one of our electrical pros will comment further.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Last edited by gbeaumont; 7/2/09 at 4:32 PM.. Reason: spelink
Reply With Quote
  #13  
Old 7/2/09, 3:41 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 264
Send a message via AIM to jfrederick
Default Re: Bulldog Pushmatic panel main bus bar terminals

Another pic, close up. I believe its 12 THHN wire. This was going to the water heater breaker (box) and then left that breaker with proper 10 ga. for the 30 amp breaker to the water heater.
Attached Thumbnails
bulldog-pushmatic-panel-main-bus-bar-terminals-7757-providence-neapolis-swanton-road-123.jpg  
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #14  
Old 7/2/09, 5:30 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,301
Default Re: Bulldog Pushmatic panel main bus bar terminals

Not sure about this setup but when I used to inspect industrial machinery short runs were allowed under certain conditions as long as they terminated at a correctly sized breaker.

NFPA 79 was the standard I used.

I no longer have a copy unfortunately.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #15  
Old 7/3/09, 11:43 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,524
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Bulldog Pushmatic panel main bus bar terminals

Ok...in this senerio ( which is a GOOD one BTW ) one has to determine if the tap rules of 240.21 apply and if the tap rules of 210.19 apply.

Firstly while I have had much debate with the NFPA over this issue, the logic of today is a feeder tap can only be the tapping of a Feeder which is a conductor in itself. They currently do not recognize the busbar as a feeder which it rightly so is not. The application in regards to XFMRS and secondary "taps" is different so we can't lump the two.

The NEC tells us that we have to protect a conductor at it's ampacity and only allows for no overcurrent protection at the "tap" provided it meets the requirements of the NEC in the references I gave prior. So, lets " Cut and Paste" some code..

II. Location.
240.21 Location in Circuit.
Overcurrent protection shall
be provided in each ungrounded circuit conductor and shall
be located at the point where the conductors receive their
supply except as specified in 240.21(A) through (H). Conductors
supplied under the provisions of 240.21(A) through (H)
shall not supply another conductor except through an overcurrent
protective device meeting the requirements of 240.4.

(A) Branch-Circuit Conductors.
Branch-circuit tap conductors
meeting the requirements specified in 210.19 shall
be permitted to have overcurrent protection as specified in
210.20.

(B) Feeder Taps.
Conductors shall be permitted to be
tapped, without overcurrent protection at the tap, to a feeder as

specified in 240.21(B)(1) through (B)(5). The provisions of
240.4(B) shall not be permitted for tap conductors.

Lets define a feeder....
Feeder.
All circuit conductors between the service equipment,
the source of a separately derived system, or other
power supply source and the final branch-circuit overcurrent
device.

And just for clarification, I am in the camp that believes the bus is the best place to tap if the buss is designed to allow it and apply the rules of 240.21 but right now it appears only Mike Holt and Me agree....the NFPA does not...which is all good as I can enforce anything they would like as I govern the word and not my wishes.

Obviously if the conductors ( and my eyes are not that good ) is a 12 AWG then we have a problem unless of course 240.21 would apply....and I do not believe under the NFPA's view it applies. Opinions are like...well.....everyone has one and thats perfectly great. BTW...it is always perfectly acceptable to disagree with me dispite what some might say.

So does 210.19 apply, lets look at a bit of "Cut and Paste" on that also-

Nah.....since we are not talking about a "Branch Circuit" in this case we wont even dabble into that part to save time and the effort to Cut and Paste by the C & P king himself...




Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Panel dmozzillo Electrical 26 1/26/09 2:18 PM
Panel Questions - main, mid, sub lfoster Electrical 6 11/11/08 10:42 PM
Subpanel wired as main panel. jlybolt Electrical 15 5/23/07 5:10 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 8:28 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts