#16
|
||||
|
||||
|
Thanks Paul, that cleared it up
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
| Find an InterNACHI certified Iowa Home Inspector (and anywhere else in North America) |
|
#17
|
||||
|
||||
|
As clear as MUD...right...lol
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#18
|
||||
|
||||
|
Yep. As I suspected, Gerry and I are correct
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#19
|
||||
|
||||
|
lol....I did not read it....what did you all say..
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#20
|
||||
|
||||
|
We are on opposite sides of the fence. . .
I said "no good," he said "no problem." IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#21
|
||||
|
||||
|
Quote:
BTW: I read Pauls opinion, then I took 2 advil and laid down for a while Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#22
|
||||
|
||||
|
Quote:
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#23
|
||||
|
||||
|
Quote:
You gotta read the tread (at least look at the pics) and give us your opinion. Jeff and I seldom differ on these issues, but this is an odd set up Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#24
|
||||
|
||||
|
I will accept Paul's opinion as the Supreme Law of the Land
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#25
|
||||
|
||||
|
LOL, so will I mate, I mean who can argue with the Grand Master of Electrical Guruism
Now if he'll just get off the fence, put the splinters out from his arse and give us a nice clean definative answer (that proves I'm right) we can all move on Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#26
|
||||
|
||||
|
lol...I thought it was clear.....the bussbar is not a feeder and it is not a feeder tap so the conductor feeding the 30A circuit would need an OCPD ahead of the conductors. Based on the letters and chats with the NFPA they are clear that feeder taps must tap a conductor and a feeder is a conductor between the service disconnection means and the final branch circuit overcurrent device.....so conductors must be protected at their ampacity...so I dont like the application...lol
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#27
|
||||
|
||||
|
Hi Paul,
thanks for that, now I get it. Good call Jeff Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#28
|
||||
|
||||
|
Don't give in so FAST my floridian friend....lol
The main thing here is where reality arrives at functionality. In reality the load is limited by the 30A OCPD that is at the disconnect and is clearly the part that Gerry was ok with and in reality it is probably ok as again the load would be limited. The functionality of the code is that I dont ( and again my opinions are mine alone, not gospel) believe the tap rules can apply here because the NEC does not provide us with tapping rules other than the ones given in 210.19 and 240.21 and these do not meet the situation. In some cases we (today) see panels with "feed-thru" type lugs which are part of the bussbar assembly and are designed to extend the bussbar to another enclosure many times because of a need for additional circuit spaces. This issue has also been made easier now since the 42 space limitation has been lifted for the 2008 NEC on panelboards ( except for Lighting & Applicance Panelboards which remains 42 spaces, so not much of a change just cleaned it up a bit ). Anyway, these feed-thru panels are rated as such and traditionally the feed-thru conductors are sized the same as the service conductors supplying the main panel. My personal feelings ( yes, they are mine alone ) is that approved lugs or taps on the buss of a panelboard ( manufacturer installed ) should be considered a TAP location and the rules of 240.21 should apply where applicable and give more open acceptance of this application. Why do I care if we tap a "feeder" or the "bus" in this application? Personally, I would prefer to use proper lugs and follow the tap rule versus trying to actually tap a conductor in the panelboard but thats appears to be just me with that opinion...or at least it is something I have not attempted to submit to the NFPA CMP before so who knows and I am sure brighter people than me have tried. Does the panelboard have any information about the lugs on the panel listings? So in reality I would give POINTS to both Gerry and Jeff on this debate because I can make compelling arguements for both...BUT I have to fall on the side of "CODE" but you can be sure I will look into this more as with anything the NEC is a thick book and I might be able to pull something out of it to contradict itself. If not, what the HECK are the lugs their for..right! Here is where it gets MUDDY.......when looking at the feeder taps rules, what if we use the lugs to extend to another panel and the main panel is rated for feed-thru lugs then the tap rules would apply because the panel is designed for this application ( I dont know if the Pushamtic are to be honest with you...could be ) and as long as you had disconnection means in compliance with the tap rules it could possibly apply. Just figured I would muddy it up for you even more.....lol WAIT...........WAIT........I may just flip flop on you all now that I actually went and looked at the picture...lol...lets see if 240.21 may apply. (1) Taps Not over 3 m (10 ft) Long. Where the length of the tap conductors does not exceed 3 m (10 ft) and the tap conductors comply with all of the following: (1) The ampacity of the tap conductors is
a. Not less than the combined calculated loads on the circuits supplied by the tap conductors, and b. Not less than the rating of the device supplied by the tap conductors or not less than the rating of the overcurrent protective device at the termination of the tap conductors. A (2) The tap conductors do not extend beyond the switchboard, panelboard, disconnecting means, or control devices they supply. A (3) Except at the point of connection to the feeder, the tap conductors are enclosed in a raceway, which shall extend from the tap to the enclosure of an enclosed switchboard, panelboard, or control devices, or to the back of an open switchboard. A (4) For field installations where the tap conductors leave the enclosure or vault in which the tap is made, the rating of the overcurrent device on the line side of the tap conductors shall not exceed 10 times the ampacity of the tap conductor. A Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 7/4/09 at 10:02 AM.. |
| Find an InterNACHI certified Iowa Home Inspector (and anywhere else in North America) |
|
#29
|
||||
|
||||
|
I can see I'm going to need more Advil
Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#30
|
||||
|
||||
|
lol....I intentionally posted a few long winded posts here to bring Mr. pope and you around this issue because I kinda like this one. And I happen to be in a camp that believes that 240.21 needs to be re-written much clearer. If the "TAP" took place ahead of the service disconnection means then Article 240 would not even apply but from what I can gather from the image it is after the 200A main disconnect so 240 rules do apply.
The argument made to the NFPA a few times was is the "bussbar" a feeder in the purest of the sense. Let me see if I have the e-mail they send me.... Quote:
So if we examine what they are saying is at the lugs the it would be a "feeder" and not a feeder tap and and tapping another conductor which is a feeder would be a "feeder tap". Personally, I believe 240.21 rules should apply to the load side of the lugs as well if they are available but thats just me. The debate goes to is the bussbar a "feeder", it is conductive in all cases ( obvioulsy ) and many panels are designed with Feed-Thru lugs that make it UL Listed for feed-thru connections ( which I dont think this case is mind you ).... SO what are the LUGS their for.........my personal feelings is as long as the rules of 240.21(B)(1) are met I would not loose any sleep over it, it appears in THIS case the rules are met. I don't know what the panel schedule says about those lugs and their intent so it has been a GREAT debate.....I can tell you this post this on Mike Holts site and they will have no problem at all with the installation and applying 240.21(B)(1) to this application. All I am saying is I have been fighting this one for a long time and once I got an "informal" opinion from a senior electrical engineer at the NFPA I started to question the way it was written. Is it likely to cause a fire......I dont think so. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Electric Panel | dmozzillo | Electrical Inspections | 26 | 1/26/09 2:18 PM |
| Panel Questions - main, mid, sub | lfoster | Electrical Inspections | 6 | 11/11/08 10:42 PM |
| Subpanel wired as main panel. | jlybolt | Electrical Inspections | 15 | 5/23/07 5:10 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |