InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Electrical

Notices

Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera.

Reply
 
LinkBack Thread Tools
  #31  
Old 7/4/09, 10:49 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,747
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Bulldog Pushmatic panel main bus bar terminals

Quote:
Originally Posted by pabernathy View Post
Is it likely to cause a fire......I dont think so.
hi Mate

that was part of my rationale, I couldn't see any obvious dangers to either personel or equipment, normaly when we see these odd looking taps they leave down stream panels energized even when the main is thrown, that isn't the case here.

So long as the feeder IS of the correct gauge for 30amp, thats the bit that would concern me.

It's an interesting issue.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #32  
Old 7/4/09, 11:15 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Bulldog Pushmatic panel main bus bar terminals

Yep....see this is what forums are for....bringing out issues.

When we see a feed-thru panel, traditionally this panels additional lugs are designed to actually extend the panel to another panel and not really for applications of the "Tap" rules the way the code is written right now. Many will TWIST the code to say the bussbar is a conductor, the lugs are a conductor and then try to bring in "websters dictionary" logic into the term of conductor. The fact is the NFPA to the BEST of my knowledge consider a conductor as what it is...a conductor. IN some areas of the code we have busway applications that are being considered as conductors and they define that in their own article and sections as such and are specific to their application but unless we change the wording of the definitions of "feeders" and "feeder taps" we are bound by their application.

The principle concept of protection is that all conductors shall be protected at their ampacity ( nope, thats no cut and paste..I wrote that...) and so we so need the applications of 240.21 (A-H) in order to actually apply taps so it's a good thing but probably way to deep for HI's to venture into, heck it is starting to seem way to deep for ME to venture into. I am always learning and as I said I fall into the camp that believes the tap rules should apply to the lugs since the busbar is in my mind a conductor of sorts and it is on the load side of the disconnection means so if the tap rule mathmatics apply I don't really loose sleep over it but as we see some engineers disagree and say taps must tap feeders to be feeder taps and thus feeder tap rules can only apply to feeders. How was that for a toungue twister.

Here is exactly what the NEC says and you be the judge:

Tap Conductors.
As used in this article, a tap conductor is

defined as a conductor, other than a service conductor, that

has overcurrent protection ahead of its point of supply that
exceeds the value permitted for similar conductors that are
protected as described elsewhere in 240.4.


Feeder.

All circuit conductors between the service equipment,
the source of a separately derived system, or other

power supply source and the final branch-circuit overcurrent
device.

The I posted earlier what an "informal" Senior Electrical Engineer stated in regards to defining feeders and feeder taps....so you be the judge. What I can tell you is that many, many and many electricians and engineers differ on this one and if someone tells you that you are wrong or right.....I can point you to many well known guys who disagree on this issue.


This is a GREAT subject and has spawned a few proposals of my own for the next code cycle.


Here is what the NEC gives us -
Conductor, Bare. A conductor having no covering or electrical
insulation whatsoever.



Conductor, Covered. A conductor encased within material
of composition or thickness that is not recognized by this
Code as electrical insulation.



Conductor, Insulated. A conductor encased within material
of composition and thickness that is recognized by this
Code as electrical insulation.



BUT it never actually tells us what a conductor IS in itself. Can it be a bussbar in a panelboard?. Does it mean lugs are conductors?
You tell me what YOU think it means..........




Here is what websters says about it....( Yes, I Cut and Pasted this from Websters Online to KEEP people happy )

Main Entry: con·duc·tor Pronunciation: \kən-ˈdək-tər\ Function: nounDate: 15th century: one that conducts: as a: guide b: a collector of fares in a public conveyance c: the leader of a musical ensemble d (1): a material or object that permits an electric current to flow easily — compare insulator, semiconductor (2): a material capable of transmitting another form of energy (as heat or sound)

So since the NEC style manual says websters can be used.....and since the NEC uses the term alot I would think it would define it within it's own scope and maybe propose this new definition to the NEC.

Conductor.Bare,Covered or Insulated-a material or object that permits an electric current to flow easily as it applies to the application of an electrical installation.


What do ya think.......should I submit it or do ya think it is needed?



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 7/4/09 at 11:36 AM..
Reply With Quote
  #33  
Old 7/4/09, 12:01 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Bulldog Pushmatic panel main bus bar terminals

UNCLE - I give!

Do you have anything stronger than Advil Gerry?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #34  
Old 7/4/09, 12:25 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Bulldog Pushmatic panel main bus bar terminals

Ask him if he has any Diprivan, an anesthetic widely used in operating rooms to induce unconsciousness and I hear it is quite powerful. But it is only advised to be used in the presence of a famous doctor.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #35  
Old 7/4/09, 5:15 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,747
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Bulldog Pushmatic panel main bus bar terminals

Quote:
Originally Posted by jpope View Post
UNCLE - I give!

Do you have anything stronger than Advil Gerry?
I switched to Scotch hours ago Jeff

Hic

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Panel dmozzillo Electrical 26 1/26/09 2:18 PM
Panel Questions - main, mid, sub lfoster Electrical 6 11/11/08 10:42 PM
Subpanel wired as main panel. jlybolt Electrical 15 5/23/07 5:10 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 8:49 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts