Default Bundling wires at panel

What is the rule for this? Is it only three wires per cutout through the top of the panel? I know this is wrong but do not know what the exact requirement is.
Attached Thumbnails
bundling-wires-panel-dsc061525880.jpg  



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Find an InterNACHI certified Mississippi Home Inspector (and anywhere else in North America)
  #2  
Old 6/12/09, 3:30 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 740
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bundling wires at panel

Try 312.5(C). Cables to be secured to enclosure.
Reply With Quote
  #3  
Old 6/12/09, 6:56 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,127
Default Re: Bundling wires at panel

Quote:
Originally Posted by Jim Port View Post
Try 312.5(C). Cables to be secured to enclosure.
Is that NEC cause 06 IRC does not have a 312.5(C)



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #4  
Old 6/12/09, 7:33 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 740
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bundling wires at panel

Sorry,

Yes, that is NFPA 70 or the NEC.
Reply With Quote
  #5  
Old 6/13/09, 11:59 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bundling wires at panel

in addition to 312.5(C) of the NEC , Mr. Port is 100% correct but I figured it would be an EXCELLENT time to show the exception to that requirement as well.......just in case you guys ran into this situation regarding a surface mount application like the one above. ( This exception does not apply to the picture shown....)

Exception: Cables with entirely nonmetallic sheaths shall
be permitted to enter the top of a surface-mounted enclosure
through one or more nonflexible raceways not less
than 450 mm (18 in.) and not more than 3.0 m (10 ft) in
length, provided all of the following conditions are met:

(a) Each cable is fastened within 300 mm (12 in.),
measured along the sheath, of the outer end of the raceway.

(b) The raceway extends directly above the enclosure
and does not penetrate a structural ceiling.

(c) A fitting is provided on each end of the raceway to
protect the cable(s) from abrasion and the fittings remain
accessible after installation.

(d) The raceway is sealed or plugged at the outer end
using approved means so as to prevent access to the enclosure
through the raceway.

(e) The cable sheath is continuous through the raceway
and extends into the enclosure beyond the fitting not
less than 6 mm (1.4 in.).

(f) The raceway is fastened at its outer end and at
other points in accordance with the applicable article.

(g) Where installed as conduit or tubing, the allowable
cable fill does not exceed that permitted for complete conduit
or tubing systems by Table 1 of Chapter 9 of this Code
and all applicable notes thereto.

AGAIN.....this does not apply here in your picture BUT good information to remember when you are doing those HI inspections on a panel in an unfinished basement and so on.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 12:39 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 10:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts