ID:	9117I know that knob and tube wiring should not be covered. Even if it's like this situation?? Can anyone explain the real purpose why it can be covered?? One other thing, what is the approved method for splicing into knob and tube with newer wiring. (special wire nuts, in a juction box, etc.)
Reply With Quote
  #2  
Old 2/12/07, 7:57 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Knob & Tube

Your picture is a textbook example of nonconforming insulation of cavities containing concealed knob and tube wiring. Knob and tube is reliant on being in free air to dissipate heat. When the cavity is insulated, the conductor insulation will degrade, which can present a hazard.

In years past, taps and section replacements on K&T were made with an "End-O" fitting on type AC or type NM cable. In modern times, we must bring the K&T into a more traditional junction box, with the appropriate conductor supports, loom, and proper fittings. Read about that procedure here.

Last edited by Marc D. Shunk; 2/12/07 at 8:39 PM..
Reply With Quote
  #3  
Old 2/12/07, 8:49 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Knob & Tube

Thank you Marc, so when I see any insulation around k&t, I should call it out as wrong and recommend insulation be removed correct?
Reply With Quote
  #4  
Old 2/12/07, 9:22 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Knob & Tube

Quote:
Originally Posted by brepanshek
Thank you Marc, so when I see any insulation around k&t, I should call it out as wrong and recommend insulation be removed correct?
I'm not sure if you were directing that question toward me or not. In case you were, I'd have to say that I'm not qualified to answer that. I'm not a home inspector. It is my opinion, as an electrician, that either the insulation or the K&T should be removed. Depending on how long the insulation has been in place, the damage may already be done. I see it's Miraflex type stuff, so it's not terribly old. I'm just not sure if you're permitted (as an HI) to recommend which remedial action; ie., removing the insulation or removing the K&T. Surely, someone else will chime in with that information.
Reply With Quote
  #5  
Old 2/12/07, 9:27 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Knob & Tube

I note the new junction box in the photo. Is the old K&T still in use?
Reply With Quote
  #6  
Old 2/12/07, 9:31 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Buried Knob & Tube

If one recommended a qualifed electrician evaluate the K & T wiring, the electrician could make the call after seeing the condition of the wiring.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #7  
Old 2/12/07, 9:38 PM
sspradling sspradling is offline
Active Poster
 
Join Date: Jan 2004
Location: Columbia, MO
Posts: 227
Please Note: sspradling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Knob & Tube

Marc,
You always post helpful, thoughtful information. Your responses to the point, are not arrogant, like we should already know the answer. You don't quote code ad nauseum, or try to sell us anything. I have benefitted from your efforts, and I'm sure others have also. Thank you.
Stu
Reply With Quote
  #8  
Old 2/12/07, 9:55 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Buried Knob & Tube

http://www.nachi.org/forum/f19/insulated-knob-and-tube-12932/



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 2/12/07, 10:54 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,054
Default Re: Buried Knob & Tube

Quote:
Originally Posted by sspradling
Marc,
You always post helpful, thoughtful information. Your responses to the point, are not arrogant, like we should already know the answer. You don't quote code ad nauseum, or try to sell us anything. I have benefitted from your efforts, and I'm sure others have also. Thank you.
Stu
Ditto Marc,.. but Stuart beat me to it! Was thinking the same thing,... very helpful electrical post by you, along with the likes of Paul A. and others. Thanks!



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #10  
Old 2/12/07, 11:03 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Knob & Tube

I was surprised to learn that opinion on this question is less cut-and-dried than I had supposed:

http://www.waptac.org/sp.asp?id=7190
Reply With Quote
  #11  
Old 2/13/07, 1:37 AM
tneyedli1's Avatar
tneyedli1 tneyedli1 is offline
Active Poster
 
Join Date: Mar 2006
Location: Port Alberni, BC
Posts: 279
Please Note: tneyedli1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Knob & Tube

Well spoken.
My exact sentiments as well.
Marc does us all well with his comments.
T.Neyedli
www.alphahomeinspections.ca
Reply With Quote
  #12  
Old 2/13/07, 8:06 AM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Knob & Tube

Michael Thomas, Great article, lots of info. Please just tell me in your words what you would state if found K&T wiring with any type of insulation around it. Thanks to all and Marc I agree with the good things being said also.
Reply With Quote
  #13  
Old 2/13/07, 8:57 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Buried Knob & Tube

Usually the addition of insulation is always a case of being done many years after the intent of the wiring method. The client probably paid a fortune in heating and cooling bills and simply had someone come in and insulate which defeats the purpose of the K & T Wiring to be effective as it again as marc stated is designed to be in a free air space.

In most cases today we simply see the addition of junction boxes to make these changeovers and corrections and more so making it easier with the use of Nonmetallic boxes.

Yes, you should call out K & T all the time for exaluation but when you start to see K & T in attics and other places and jamed in insulation it is very important that your reports 1.) reflect the environment you see the wiring and type of wiring 2.) The condition that makes the wire a problem

Here is some info on K & T also in HI Translation: http://www.allaroundthehouse.com/lib.def.na10.htm



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 2/13/07 at 9:05 AM..
Reply With Quote
  #14  
Old 2/15/07, 8:19 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Buried Knob & Tube

“Please just tell me in your words what you would state if found K&T wiring
with any type of insulation around it…”

===========

Further evaluation of Knob and Tube Wiring: The Knob and Tube Wiring (K&T) [at location] is surrounded by [type] insulation. Since 1987, national standards have prohibited the installation of new insulation in contact with knob-and-tube wiring. Some authorities are concerned that insulation surrounding K&T wiring may raise its operating temperature, possibly shortening its service life and/or increasing the likelihood hazardous conditions may develop.

Additional information regarding these concerns is available at:


http://www.waptac.org/sp.asp?id=7190

Where the K&T wiring is surrounded by insulation, I was not able to visually observe the extent or condition of the wiring. In houses where K&T wiring is present, I often observe defects in the condition, installation or connections of the wiring. In my opinion and experience it is prudent to assume that such defects may also be present in sections of K&T wiring I cannot visually inspect because they are obstructed by insulation.

Where K&T is present individual exposed wires are strung between ceramic insulators. As the wires are unprotected they are subject to damage if disturbed. The risk of such damage is increased when the wiring is not visible (as for example where it is installed under or behind insulation). In addition, K&T wiring is frequently incorrectly modified and/or incorrectly connected to newer wiring. Where K&T wiring has been damaged or incorrectly modified or connected, it poses a risk of electrocution and/or fire.

I recommend that all K&T wiring be inspected by a qualified, licensed and insured electrician, and that you obtain their advice as to 1) what portion (if any) of the insulation covering the K&T wiring should be removed to allow its inspection and/or reduce its operating temperature, and 2) what modifications (if any) should be made to this wiring to increase its serviceability or safety.
Reply With Quote
  #15  
Old 2/15/07, 10:12 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Buried Knob & Tube

Quote:
Originally Posted by brepanshek
Please just tell me in your words what you would state if found K&T wiring with any type of insulation around it.
I would say this whether it had insulation around it or not:

"The residence is wired with suspect knob-and-tube wiring, which was commonly installed prior to 1950. It is ungrounded and over time the wire's insulation may become brittle and fall apart or wear thin, resulting in exposed conductors and a risk of shock and/or fire. The hazard is increased by covering it with insulation (a common practice), and incorrectly tapping new wiring into it. The wiring should be evaluated by an electrician and certified as being safe or replaced."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
K&T splice. egarcia1 Electrical Inspections 13 2/3/07 7:36 AM
Insulated Knob and Tube? scosta Electrical Inspections 6 2/3/07 7:22 AM
Knob and tube wblakey Electrical Inspections 17 11/14/06 8:41 PM
Knob and tube: heat's the main problem? kshepard Electrical Inspections 21 6/27/06 10:51 AM


All times are GMT -4. The time now is 10:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts