I know that knob and tube wiring should not be covered. Even if it's like this situation?? Can anyone explain the real purpose why it can be covered?? One other thing, what is the approved method for splicing into knob and tube with newer wiring. (special wire nuts, in a juction box, etc.)
|
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Your picture is a textbook example of nonconforming insulation of cavities containing concealed knob and tube wiring. Knob and tube is reliant on being in free air to dissipate heat. When the cavity is insulated, the conductor insulation will degrade, which can present a hazard.
In years past, taps and section replacements on K&T were made with an "End-O" fitting on type AC or type NM cable. In modern times, we must bring the K&T into a more traditional junction box, with the appropriate conductor supports, loom, and proper fittings. Read about that procedure here. Last edited by Marc D. Shunk; 2/12/07 at 8:39 PM.. |
|
#3
|
|||
|
|||
|
Please Note:
brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thank you Marc, so when I see any insulation around k&t, I should call it out as wrong and recommend insulation be removed correct?
|
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
I note the new junction box in the photo. Is the old K&T still in use?
|
|
#6
|
|||
|
|||
|
If one recommended a qualifed electrician evaluate the K & T wiring, the electrician could make the call after seeing the condition of the wiring.
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#7
|
|||
|
|||
|
Please Note:
sspradling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marc,
You always post helpful, thoughtful information. Your responses to the point, are not arrogant, like we should already know the answer. You don't quote code ad nauseum, or try to sell us anything. I have benefitted from your efforts, and I'm sure others have also. Thank you. Stu |
|
#8
|
||||
|
||||
|
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#9
|
||||
|
||||
|
Quote:
Peter Doane Realty Check Inspection Service NACHI ID# 05120681
|
|
#10
|
|||
|
|||
|
Please Note:
mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
I was surprised to learn that opinion on this question is less cut-and-dried than I had supposed:
http://www.waptac.org/sp.asp?id=7190 |
|
#11
|
||||
|
||||
|
Please Note:
tneyedli1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Well spoken.
My exact sentiments as well. Marc does us all well with his comments. T.Neyedli www.alphahomeinspections.ca |
|
#12
|
|||
|
|||
|
Please Note:
brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Michael Thomas, Great article, lots of info. Please just tell me in your words what you would state if found K&T wiring with any type of insulation around it. Thanks to all and Marc I agree with the good things being said also.
|
|
#13
|
||||
|
||||
|
Usually the addition of insulation is always a case of being done many years after the intent of the wiring method. The client probably paid a fortune in heating and cooling bills and simply had someone come in and insulate which defeats the purpose of the K & T Wiring to be effective as it again as marc stated is designed to be in a free air space.
In most cases today we simply see the addition of junction boxes to make these changeovers and corrections and more so making it easier with the use of Nonmetallic boxes. Yes, you should call out K & T all the time for exaluation but when you start to see K & T in attics and other places and jamed in insulation it is very important that your reports 1.) reflect the environment you see the wiring and type of wiring 2.) The condition that makes the wire a problem Here is some info on K & T also in HI Translation: http://www.allaroundthehouse.com/lib.def.na10.htm Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 2/13/07 at 9:05 AM.. |
|
#14
|
|||
|
|||
|
Please Note:
mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
“Please just tell me in your words what you would state if found K&T wiring
with any type of insulation around it…” =========== Further evaluation of Knob and Tube Wiring: The Knob and Tube Wiring (K&T) [at location] is surrounded by [type] insulation. Since 1987, national standards have prohibited the installation of new insulation in contact with knob-and-tube wiring. Some authorities are concerned that insulation surrounding K&T wiring may raise its operating temperature, possibly shortening its service life and/or increasing the likelihood hazardous conditions may develop. Additional information regarding these concerns is available at: http://www.waptac.org/sp.asp?id=7190 Where the K&T wiring is surrounded by insulation, I was not able to visually observe the extent or condition of the wiring. In houses where K&T wiring is present, I often observe defects in the condition, installation or connections of the wiring. In my opinion and experience it is prudent to assume that such defects may also be present in sections of K&T wiring I cannot visually inspect because they are obstructed by insulation. Where K&T is present individual exposed wires are strung between ceramic insulators. As the wires are unprotected they are subject to damage if disturbed. The risk of such damage is increased when the wiring is not visible (as for example where it is installed under or behind insulation). In addition, K&T wiring is frequently incorrectly modified and/or incorrectly connected to newer wiring. Where K&T wiring has been damaged or incorrectly modified or connected, it poses a risk of electrocution and/or fire. I recommend that all K&T wiring be inspected by a qualified, licensed and insured electrician, and that you obtain their advice as to 1) what portion (if any) of the insulation covering the K&T wiring should be removed to allow its inspection and/or reduce its operating temperature, and 2) what modifications (if any) should be made to this wiring to increase its serviceability or safety. |
|
#15
|
||||
|
||||
|
Quote:
"The residence is wired with suspect knob-and-tube wiring, which was commonly installed prior to 1950. It is ungrounded and over time the wire's insulation may become brittle and fall apart or wear thin, resulting in exposed conductors and a risk of shock and/or fire. The hazard is increased by covering it with insulation (a common practice), and incorrectly tapping new wiring into it. The wiring should be evaluated by an electrician and certified as being safe or replaced." “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| K&T splice. | egarcia1 | Electrical Inspections | 13 | 2/3/07 7:36 AM |
| Insulated Knob and Tube? | scosta | Electrical Inspections | 6 | 2/3/07 7:22 AM |
| Knob and tube | wblakey | Electrical Inspections | 17 | 11/14/06 8:41 PM |
| Knob and tube: heat's the main problem? | kshepard | Electrical Inspections | 21 | 6/27/06 10:51 AM |