Default Burn marks at hot bus bar?

Would anyone consider these burn marks, where apparently a breaker at one time was installed, enough to warrant further evaluation of panel?

The panel is an ITE Pushmatic, aluminum bus, approx. 40 yrs old. No other visible problems noted.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 4/20/11 at 12:52 PM..
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/19/11, 2:47 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is online now
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Burn marks at hot bus bar?

I always call out a panel with arc marks. But be ready for the electrician to bad mouth you. They are going to say it was probably during a modification or install that the arcing occurred and they will say your just making a mountain out of a mole hill. I always tell the client that I would rather be safe than sorry and to have it evalauted.



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #3  
Old 4/19/11, 3:20 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Burn marks at hot bus bar?

I would note it for what it is, and let the buyer know that it is an old panel and will likely have additional failures in the future. It does appear that there was a breaker that failed at some point and it was taken care of. Tell them to have the hole covered with an insert, and monitor it for signs of failure. (buzzing, humming, crackling, popping etc.)

Some things are what they are. This is an old panel, and is showing it's age. (Probably right along with the rest of the home.) After all they are buying an old house, and old houses need to have things replaced.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #4  
Old 4/19/11, 3:49 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Burn marks at hot bus bar?

It looks like a breaker fried and died at that location and was removed.

If I saw no other damage, I would note the lack of a snap in cover over the opening and the arc marks at some time in it's past.

From the pics it looks like the problem was removed.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 4/19/11, 4:09 PM
Harry E. McClard's Avatar
Harry E. McClard Harry E. McClard is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Raymond, NH
Posts: 103
Default Re: Burn marks at hot bus bar?

Is there a blanking cover over the slot where the breaker was removed? First picture looks like it's an open slot.



Harry "Bud" McClard
Serving All of New Hampshire
Reply With Quote
  #6  
Old 4/19/11, 4:28 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Burn marks at hot bus bar?

Quote:
Originally Posted by mlarson View Post
It looks like a breaker fried and died at that location and was removed.

If I saw no other damage, I would note the lack of a snap in cover over the opening and the arc marks at some time in it's past.

From the pics it looks like the problem was removed.
This was basically my viewpoint. Of course I noted missing cover. No visible damage, but can't see behind breakers, that was my concern.

Like mentioned it is an older home (1980), also first time buyers, don't want to alarm them if not warranted. The rest of the house was in pretty good shape, minus open ground 3-prongs and low water pressure at some locations.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #7  
Old 4/19/11, 7:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Burn marks at hot bus bar?

Quote:
Originally Posted by mlarson View Post
It looks like a breaker fried and died at that location and was removed.

If I saw no other damage, I would note the lack of a snap in cover over the opening and the arc marks at some time in it's past.

From the pics it looks like the problem was removed.
I agree.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 4/20/11, 10:52 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Burn marks at hot bus bar?

Quote:
Originally Posted by ccurrins View Post
Would anyone consider these burn marks, where apparently a breaker at one time was installed, enough to warrant further evaluation of panel?

The panel is an ITE Pushmatic, aluminum bus, approx. 40 yrs old. No other visible problems noted.
Ahhh my old favorites the Bull Dog Push O Matics. The problem is that even if the burn marks are from an issue in the past the fact remains that the Hot Bus bar has lost some of its intended integrity and needs to be replaced plain and simple. When dealing with the heart of the electrical system there is no room for guessing or assuming. A burned buss bar needs to be repaired period.

Jim




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
  #9  
Old 4/20/11, 11:03 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Burn marks at hot bus bar?

Quote:
Originally Posted by ccurrins View Post
Here's what it looks like.
304K guy told me FHA/HUD wants Pushmatics replaced.
Reply With Quote
  #10  
Old 4/20/11, 11:10 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Burn marks at hot bus bar?

Quote:
Originally Posted by belliott View Post
304K guy told me FHA/HUD wants Pushmatics replaced.
Thanks, I'll remember that.

I've been seeing a lot of them in the last year, homes built in 70's, 80's. Usually there are enough "other" reasons, rust, burnt wires, etc., to recommend replacement or further evaluation by an electrical contractor. The burn mark was the only issue with this one, minus age.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #11  
Old 4/21/11, 5:05 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burn marks at hot bus bar?

Quote:
Originally Posted by belliott View Post
304K guy told me FHA/HUD wants Pushmatics replaced.
Is there a specific problem with those breakers? Seems to me that they're better than a stab-in style breaker because there bolted right to the bus.
Reply With Quote
  #12  
Old 4/27/11, 7:02 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burn marks at hot bus bar?

Thermally damaged copper and aluminium loses its strength.
Thermally damaged plastic insulating parts, which may be under the bus, can become semi-conductive.
Thermally damaged fish paper, which may be under older buses, can become nearly completely conductive.

Replace thermally damaged parts. Period. It's code-required anyhow.

NFPA 70-2011
110.12 Mechanical Execution of Work.
Electrical equipment
shall be installed in a neat and workmanlike manner.
Informational Note: Accepted industry practices are described
in ANSI/NECA 1-2006, Standard Practices for
Good Workmanship in Electrical Contracting, and other
ANSI-approved installation standards.
(A) Unused Openings. Unused openings, other than those
intended for the operation of equipment, those intended for
mounting purposes, or those permitted as part of the design
for listed equipment, shall be closed to afford protection substantially
equivalent to the wall of the equipment. Where metallic
plugs or plates are used with nonmetallic enclosures,
they shall be recessed at least 6 mm (1⁄4 in.) from the outer
surface of the enclosure.
(B) Integrity of Electrical Equipment and Connections.
Internal parts of electrical equipment, including busbars,
wiring terminals, insulators, and other surfaces, shall not be
damaged or contaminated by foreign materials such as
paint, plaster, cleaners, abrasives, or corrosive residues.
There shall be no damaged parts that may adversely affect
safe operation or mechanical strength of the equipment
such as parts that are broken; bent; cut; or deteriorated by
corrosion, chemical action, or overheating.
Reply With Quote
  #13  
Old 4/27/11, 7:08 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burn marks at hot bus bar?

Quote:
Originally Posted by Robert Meier View Post
Is there a specific problem with those breakers? Seems to me that they're better than a stab-in style breaker because there bolted right to the bus.
No. They were quite possibly the finest panel ever made for residential use. They're just getting so old that they're at or near the end of their useful life. People have reported difficulty operating the pushbutton mechanism in Pushmatic panels installed outdoors or damp ambients.
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/27/11, 7:25 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burn marks at hot bus bar?

Quote:
Originally Posted by Marc D. Shunk View Post
No. They were quite possibly the finest panel ever made for residential use. They're just getting so old that they're at or near the end of their useful life. People have reported difficulty operating the pushbutton mechanism in Pushmatic panels installed outdoors or damp ambients.
I've found that they can be difficult to manually cycle on and off. Some times they shut off but won't go back on. Most likely due to the fact that no one has touched them in decades.
Reply With Quote
  #15  
Old 4/27/11, 7:59 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Burn marks at hot bus bar?

Quote:
Originally Posted by Marc D. Shunk View Post
No. They were quite possibly the finest panel ever made for residential use. They're just getting so old that they're at or near the end of their useful life. People have reported difficulty operating the pushbutton mechanism in Pushmatic panels installed outdoors or damp ambients.
Welcome back Marc! Good to see you posting again!



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Outlet with burn marks pnarron Electrical Inspections 5 3/21/10 9:18 AM
Why you should not burn Candles rcooke Canadian Inspectors 15 6/21/07 7:57 AM
Misuse of Title rwand1 Canadian Inspectors 40 10/15/06 8:29 AM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM