Default bus bar ties

I inspected a house today. That had one main 200 amp handle and two sub panels. All of the panels had the neutral and ground buses tied together. I'm not an electrician but I thought this was not allowed. What is the problem with this and why is it bad. We were always taught that only the main panel should have the neutral and ground buses tied together.
Reply With Quote
  #2  
Old 6/4/07, 7:22 PM
grusk grusk is offline
Active Poster
 
Join Date: Feb 2006
Location: FT. JENNINGS, OH
Posts: 191
Please Note: grusk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: bus bar ties

http://nachi.org/electricalcoursereleased2006.htm
Reply With Quote
  #3  
Old 6/4/07, 8:39 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: bus bar ties

I'm not sure the "Why?" question is answered in the electrical course. If it was, I don't recall it.
Reply With Quote
  #4  
Old 6/4/07, 8:49 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: bus bar ties

Rather than try to explain it I'll give credit to the NEC Handbook commentary:
(keep in mind, the "grounded conductor" they refer to is more commonly know as the "neutral")

Quote:
One major reason the grounded circuit conductor is not permitted to be grounded on the load side of the service [except as permitted in 250.30, 250.32(B)(2), and the four exceptions to 250.142(B)] is that, should the grounded service conductor become disconnected at any point on the line side of the ground, the equipment grounding conductor and all conductive parts connected to it would carry the neutral current, raising the potential to ground of exposed metal parts not normally intended to carry current. This could result in arcing in concealed spaces and could pose a severe shock hazard, particularly if the path is inadvertently opened by a person servicing or repairing piping or ductwork. Even without an open grounded conductor (usually referred to as an open neutral), the equipment grounding conductor path would become a parallel path with the grounded conductor, and there would be some potential drop on exposed and concealed dead metal parts. The magnitude of this potential difference would be determined by the relative impedances of the equipment grounding path and the grounded conductor circuits. Not only would the equipment grounding conductor path be affected, but all parallel paths not intended as equipment grounding conductors would be affected as well. This could involve current through metal building structures, piping, and ducts. The requirements of 250.30 and 250.32(B) have been revised in recent editions of the Code to prohibit the creation of parallel paths for normal neutral current.
Reply With Quote
  #5  
Old 6/4/07, 8:52 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: bus bar ties

Quote:
Originally Posted by krentz
I inspected a house today. That had one main 200 amp handle and two sub panels. All of the panels had the neutral and ground buses tied together. I'm not an electrician but I thought this was not allowed.
Beyond the service disconnect the neutrals (grounded conductors) and grounds (grounding conductors), typically, should be separated from each other and the neutrals isolated.



Quote:
Originally Posted by krentz
What is the problem with this and why is it bad. We were always taught that only the main panel should have the neutral and ground buses tied together.
I pulled this definition from somewhere:

When neutrals and grounds are bonded (connected) together, the return neutral current will split (not necessarily equally) and run on parallel paths through the grounding and neutral system back to the main panel and up the neutral to the transformer. This parallel travel can cause unbalanced conditions in the system because the current remaining in the neutral will not counterbalance the current in the hot wire. In some cases, neutral current travel on the grounding system and other metal systems, such as piping or ductwork, can be a shock hazard.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Handle ties on circuit breakers chellickson Electrical Inspections 18 5/7/07 4:20 PM
Square D breaker handle with holes for ties? kshepard Electrical Inspections 10 12/20/06 9:39 PM
Brick Ties psmothers Exterior Inspections 4 6/7/06 6:43 PM
No Brick Ties - Wall Buldge Stew Structural Inspections 1 4/22/06 6:56 AM


All times are GMT -4. The time now is 2:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts