Default A/C box

This is from todays inspection. House is wired with aluminum wiring. As you can see from the pics, that the COP ALUM devise is not in place. Also, the cover inside the electrical panel is broken.
When the home owner was asked the question whether or not the house as the proper connections, he said they had replaced several.
Do they make switches and receptacles to accept aluminum wire, or does the installation have to be preformed using the COP ALUM connection?
Should the cover inside the disconnect be in place or a lock put on the cover?

Attachment 19759

Attachment 19760

Thanks



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 7/8/08 at 8:41 AM..
Reply With Quote
  #2  
Old 3/22/08, 2:09 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C box

The dead front cover is simply broken and needs to be replaced. No other answer. The servicer needs access to that pullout without the fear of contacting the hot lugs. That is the reason you have a disconnect.

If there are no aluminum wires in those red wirenuts you are fine with these connections. "Lug" type terminations were never a problem.
Reply With Quote
  #3  
Old 3/22/08, 2:31 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: A/C box

Greg
There is aluminum wire in those wire connectors. The whole house is aluminum.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #4  
Old 3/22/08, 2:41 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C box

There is your violation (beyond the broken cover). Red wirenuts, all of them, are only listed copper/copper.

The purple ones are legal but unpopular if you believe "Inspect-NY".

There is a listed split bolt that will work (ugly because you need to tape it up) and you have several lug types these days.
The King Industries Alumiconn is the new one and you have some from Ilsco and Polari$ (Oh my god! expensive) for large wires.

Then if you are doing the whole house you have the proprietary, pay a franchise holder, Copalum system.
Reply With Quote
  #5  
Old 3/22/08, 2:45 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: A/C box

Greg
I suspect that the whole house needs to be evaluated by a license electrician. The home owner said he changed several? Is there devises that would work for aluminum wire, without the use of COP-ALUM connections?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #6  
Old 3/22/08, 3:04 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C box

There are devices listed for use with AL conductors. The are label CO/ALR. There is no need to pigtail with copper for these devices.

It looks like the low voltage wires may be in the same raceway as the power conductors. It is hard to tell if the cable feeding the AC unit is NM or UF. If it is NM it is improper.
Reply With Quote
  #7  
Old 3/23/08, 9:12 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: A/C box

Jim
The wire feeding the AC unit is NM. Even though it is protected, it still would be wrong and should be flagged?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #8  
Old 3/23/08, 11:13 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C box

If these are fuses that will be installed in a fuseholder designed for their use, then these fuseholders may not be of the proper type, or the incorrect fuses were used.

Check Bussmann for the specifications
Reply With Quote
  #9  
Old 3/24/08, 7:19 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C box

It looks to me as though the wirenuts in the picture are splicing the lowvoltage wiring, not any power conductors.

As far as I am aware, there are no listed wirenuts for Al to Al connections. Up until 1993, the red "Bcaps" were listed for such use, then UL changed the standard.

There are millions of splices of Al using the Bcap wirenut that are still in place and are still in good shape.

Like any other splice, most failures are due to the installer, not the product itself.
Reply With Quote
  #10  
Old 3/24/08, 9:50 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C box

Quote:
Originally Posted by nbhi
Jim
The wire feeding the AC unit is NM. Even though it is protected, it still would be wrong and should be flagged?
If the wiring is going from the disconnect to the unit it is wrong if it is NM. NM is not listed for exterior usages and shuold be flagged.. UF could be used as well as single conductors with a W rating like THWN.
Reply With Quote
  #11  
Old 3/28/08, 7:14 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: A/C box

I hand out this when I inspect a house with aluminum wiring.
Attached Files
File Type: pdf Aluminum Wiring.pdf (71.2 KB, 154 views)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 2:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts