Large carrier A/C unit calls for Max breaker size of 58 amps. Is a 60 amp breaker in the main panel a problem?
David Nice National Certified Inspection Services, Inc. Wauwatosa, WI http://www.nationalcertified.com 414-979-6900 President WiNACHI http://www.winachi.com Wisconsin InterNACHI Chapter |
|
#2
|
||||
|
||||
|
Are you sure it had 58 amps listed? Very weird.
60 amp breaker is above the limit and technically wrong but anyone who writes this up needs to spend more time looking for something that matters. Lots of inspectors agree that going up to 5 amps over the limit is ok and necessary due to the available breaker sizes. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#3
|
||||
|
||||
|
Quote:
It's new construction and everything else is near flawless. David Nice National Certified Inspection Services, Inc. Wauwatosa, WI http://www.nationalcertified.com 414-979-6900 President WiNACHI http://www.winachi.com Wisconsin InterNACHI Chapter |
|
#4
|
||||
|
||||
|
That would have to be one honker of a system. Any idea as to the tonnage?
|
|
#5
|
|||
|
|||
|
Bruce,
This does matter, a breaker that is larger than the data plate has labled will void the manufacturers warranty and it will void a home warranty plan as well (Anything to get out of paying a claim) All A/C manufacturers have a phone# for tech support, they are more than happy to answer any questions for home inspectors, A/C techs ect. Call the manufacturer and give them the model # |
|
#6
|
||||
|
||||
|
There may be more or less than a 2 amp difference depending on the voltage supplied.
Is your meter true RMS? Or are you assuming it's 110, 120, 128 VAC. What effect does voltage drop have on the supply... I agree, lets worry about the more important stuff. A mechanical contractor is the one in contact with the Mfg. and I don't see too many 58 amp breakers out there. What standard size breaker would you recommend, other than 60? |
|
#7
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
I too find this weird. When stating "minimum circuit ampacity" they typically give the actual number.
When stating "Max fuse or breaker size" they usually do use a standard size. If it did in fact say 58 amps max fuse or breaker then 60 IS appropriate. Not to get all NEC on you but it is clearly explained that if no standard breaker exists for a given circuit size/wire ampacity then we round UP to the nearest "stock" size. |
|
#8
|
|||
|
|||
|
Please Note:
Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
May i step in for a min guys
for the Central Air conding units ,, for the outdoor units they will useally listed both max and min rating so you can used the running amp and go up to max rating. but it can be allow to round up to next standard size like this unit if say 58 amp you can use the 60 breaker that is fine merci , Marc |
|
#9
|
|||
|
|||
|
Many times I see data plates that says max breaker 30-amps and the unit will be on a 35 or 40-amp breaker. Per manufacturer this is wrong and will void their warranty. I heard of home warranty companies voiding their warranty as well
I have not seen a 58-amp max yet. I know there are some brands you have to round up to get the tons as well. |
|
#10
|
|||
|
|||
|
I agree about the warranty if the nameplate or instructions say 30 A max BREAKER. However, if it states that the max LOAD is 58 A that is another story, IMHO. Since the is no 58 A breaker, you must use 60, because any smaller would result in nusiance tripping at or near rated load.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
I think someone mis-read the dataplate. Got a picture? The 58 number sounds more typical of the number that would be in the LRA blank of the dataplate. When I did HVAC work, Carrier was my line. I never saw an odd number like that in the 'max fuse or breaker size' blank. I'd rather think that's the LRA for the unit in question.
|
|
#12
|
||||
|
||||
|
Quote:
|
|
#13
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
We see that situation all the time. There is no such thing as a 58 amp breaker, so they go to the next size up, which is a 60 amp breaker. Anything higher will cause a problem.
|
|
#14
|
|||
|
|||
|
What part of "maximum" do we not understand? I agree 58 is an odd spec, but if it is as such, then the breaker must be smaller.
|
|
#15
|
|||
|
|||
|
Quote:
(B) Devices Rated 800 Amperes or Less. The next higher standard overcurrent device rating (above the ampacity of the conductors being protected) shall be permitted to be used, provided all of the following conditions are met: (1) The conductors being protected are not part of a multioutlet branch circuit supplying receptacles for cordand- plug-connected portable loads. (2) The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker without overload trip adjustments above its rating (but that shall be permitted to have other trip or rating adjustments). (3) The next higher standard rating selected does not exceed 800 amperes. Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Tell me again what size wire goes on a 100 amp breaker? | jfunderburk | Electrical Inspections | 3 | 8/20/07 10:39 PM |
| Minimum Size Breaker for Sub Panel | rmoewe | Electrical Inspections | 7 | 5/21/07 6:24 PM |
| Service wire size to breaker panel | sfalvey | Electrical Inspections | 12 | 10/31/06 4:28 PM |
| 30 amp breaker wire size | kweiss | Electrical Inspections | 18 | 10/10/06 9:53 PM |
| Main Breaker Size | cpennick | Electrical Inspections | 13 | 9/20/06 10:56 PM |