  #1  
Old 9/13/07, 1:15 PM
David A. Nice's Avatar
David A. Nice David A. Nice is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Wauwatosa, WI
Posts: 1,678
Default A/C Breaker size

Large carrier A/C unit calls for Max breaker size of 58 amps. Is a 60 amp breaker in the main panel a problem?



David Nice
National Certified Inspection Services, Inc.
Wauwatosa, WI

http://www.nationalcertified.com
414-979-6900
President WiNACHI
http://www.winachi.org
Wisconsin InterNACHI Chapter
414-979-6053
Reply With Quote
  #2  
Old 9/13/07, 1:37 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,219
Default Re: A/C Breaker size

Are you sure it had 58 amps listed? Very weird.

60 amp breaker is above the limit and technically wrong but anyone who writes this up needs to spend more time looking for something that matters.

Lots of inspectors agree that going up to 5 amps over the limit is ok and necessary due to the available breaker sizes.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #3  
Old 9/13/07, 4:14 PM
David A. Nice's Avatar
David A. Nice David A. Nice is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Wauwatosa, WI
Posts: 1,678
Default Re: A/C Breaker size

Quote:
Originally Posted by bking
Are you sure it had 58 amps listed? Very weird.

60 amp breaker is above the limit and technically wrong but anyone who writes this up needs to spend more time looking for something that matters.

Lots of inspectors agree that going up to 5 amps over the limit is ok and necessary due to the available breaker sizes.
Yes, it is a brand new Carrier A/C unit and it's prety large. It really says 58 amp max. I'm not "writing it up", I'm just including the data in the report.

It's new construction and everything else is near flawless.



David Nice
National Certified Inspection Services, Inc.
Wauwatosa, WI

http://www.nationalcertified.com
414-979-6900
President WiNACHI
http://www.winachi.org
Wisconsin InterNACHI Chapter
414-979-6053
Reply With Quote
  #4  
Old 9/13/07, 4:19 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,096
Default Re: A/C Breaker size

That would have to be one honker of a system. Any idea as to the tonnage?
Reply With Quote
  #5  
Old 9/13/07, 4:27 PM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 751
Default Re: A/C Breaker size

Bruce,

This does matter, a breaker that is larger than the data plate has labled will void the manufacturers warranty and it will void a home warranty plan as well (Anything to get out of paying a claim)

All A/C manufacturers have a phone# for tech support, they are more than happy to answer any questions for home inspectors, A/C techs ect.

Call the manufacturer and give them the model #
Reply With Quote
  #6  
Old 9/13/07, 4:36 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: A/C Breaker size

There may be more or less than a 2 amp difference depending on the voltage supplied.

Is your meter true RMS? Or are you assuming it's 110, 120, 128 VAC. What effect does voltage drop have on the supply...

I agree, lets worry about the more important stuff.
A mechanical contractor is the one in contact with the Mfg. and I don't see too many 58 amp breakers out there. What standard size breaker would you recommend, other than 60?
Reply With Quote
  #7  
Old 9/13/07, 4:42 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C Breaker size

I too find this weird. When stating "minimum circuit ampacity" they typically give the actual number.
When stating "Max fuse or breaker size" they usually do use a standard size.

If it did in fact say 58 amps max fuse or breaker then 60 IS appropriate.
Not to get all NEC on you but it is clearly explained that if no standard breaker exists for a given circuit size/wire ampacity then we round UP to the nearest "stock" size.
Reply With Quote
  #8  
Old 9/13/07, 4:49 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 137
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C Breaker size

May i step in for a min guys ;

for the Central Air conding units ,, for the outdoor units they will useally listed both max and min rating so you can used the running amp and go up to max rating. but it can be allow to round up to next standard size

like this unit if say 58 amp you can use the 60 breaker that is fine


merci , Marc
Reply With Quote
  #9  
Old 9/13/07, 5:36 PM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 751
Default Re: A/C Breaker size

Many times I see data plates that says max breaker 30-amps and the unit will be on a 35 or 40-amp breaker. Per manufacturer this is wrong and will void their warranty. I heard of home warranty companies voiding their warranty as well

I have not seen a 58-amp max yet. I know there are some brands you have to round up to get the tons as well.
Reply With Quote
  #10  
Old 9/13/07, 5:50 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 505
Default Re: A/C Breaker size

I agree about the warranty if the nameplate or instructions say 30 A max BREAKER. However, if it states that the max LOAD is 58 A that is another story, IMHO. Since the is no 58 A breaker, you must use 60, because any smaller would result in nusiance tripping at or near rated load.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #11  
Old 9/14/07, 12:22 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C Breaker size

I think someone mis-read the dataplate. Got a picture? The 58 number sounds more typical of the number that would be in the LRA blank of the dataplate. When I did HVAC work, Carrier was my line. I never saw an odd number like that in the 'max fuse or breaker size' blank. I'd rather think that's the LRA for the unit in question.
Reply With Quote
  #12  
Old 9/14/07, 8:24 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: A/C Breaker size

Quote:
I have not seen a 58-amp max yet. I know there are some brands you have to round up to get the tons as well.
Carrier is notorious for "off numbers" but I think your on line Marc.
Reply With Quote
  #13  
Old 9/14/07, 8:55 AM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: A/C Breaker size

We see that situation all the time. There is no such thing as a 58 amp breaker, so they go to the next size up, which is a 60 amp breaker. Anything higher will cause a problem.
Reply With Quote
  #14  
Old 9/18/07, 8:01 AM
rgallahorn rgallahorn is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Charleston, SC
Posts: 58
Default Re: A/C Breaker size

What part of "maximum" do we not understand? I agree 58 is an odd spec, but if it is as such, then the breaker must be smaller.
Reply With Quote
  #15  
Old 9/18/07, 9:29 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: A/C Breaker size

Quote:
Originally Posted by rgallahorn
What part of "maximum" do we not understand? I agree 58 is an odd spec, but if it is as such, then the breaker must be smaller.
I would reconsider that statement....

(B) Devices Rated 800 Amperes or Less.
The next higher
standard overcurrent device rating (above the ampacity of
the conductors being protected) shall be permitted to be
used, provided all of the following conditions are met:
(1) The conductors being protected are not part of a multioutlet
branch circuit supplying receptacles for cordand-
plug-connected portable loads.
(2) The ampacity of the conductors does not correspond
with the standard ampere rating of a fuse or a circuit
breaker without overload trip adjustments above its rating
(but that shall be permitted to have other trip or
rating adjustments).
(3) The next higher standard rating selected does not exceed
800 amperes.




Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Tell me again what size wire goes on a 100 amp breaker? jfunderburk Electrical 3 8/20/07 11:39 PM
Minimum Size Breaker for Sub Panel rmoewe Electrical 7 5/21/07 7:24 PM
Service wire size to breaker panel sfalvey Electrical 12 10/31/06 5:28 PM
30 amp breaker wire size kweiss Electrical 18 10/10/06 10:53 PM
Main Breaker Size cpennick Electrical 13 9/20/06 11:56 PM


All times are GMT -4. The time now is 9:36 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts