  #16  
Old 9/18/07, 1:26 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C Breaker size

I can see this going both waysCertainly 240.4(B) would make this OK with nothing else considered but you run up against 110.3(B). The label does say 58a Max.
Reply With Quote
  #17  
Old 9/18/07, 1:40 PM
rgallahorn rgallahorn is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Charleston, SC
Posts: 58
Default Re: A/C Breaker size

??

(C) Protective Device Rating Not to Exceed the Manufacturer's Values. Where maximum protective device ratings shown on a manufacturer's overload relay table for use with a motor controller are less than the rating or setting selected in accordance with 440.22(A) and (B), the protective device rating shall not exceed the manufacturer's values marked on the equipment.
Reply With Quote
  #18  
Old 9/18/07, 2:38 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A/C Breaker size

Quote:
Originally Posted by Greg Fretwell
I can see this going both waysCertainly 240.4(B) would make this OK with nothing else considered but you run up against 110.3(B). The label does say 58a Max.
AHHHH...but does it...lol.......how about some pictures of this phantom "DATA PLATE"...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #19  
Old 9/18/07, 2:43 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A/C Breaker size

Quote:
Originally Posted by rgallahorn
??

(C) Protective Device Rating Not to Exceed the Manufacturer's Values. Where maximum protective device ratings shown on a manufacturer's overload relay table for use with a motor controller are less than the rating or setting selected in accordance with 440.22(A) and (B), the protective device rating shall not exceed the manufacturer's values marked on the equipment.
To be quite honest with you....I have never seen a Manufacturer give a value that is not a standard listed value in regards to the OCPD.....remember now you are mingling OCPD's and Overload Relays in those statements...so I will assume you are just refering to the last portion.

It is important to know as greg stated that in many cases the breaker is " Increased " for specific reasons.....again I do not recall ever seeing a rating of an HVAC unit which I believe is in question here as 58A....may be the plates data for the amp draw......which then would make the "increasing" the size OCPD apply.....Now...if we are talking about multiple motors and a feeders OCPD..then that can't be increased per the NEC...so it would be a case of downsizing the breaker....but thats too much information.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #20  
Old 9/18/07, 2:49 PM
rgallahorn rgallahorn is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Charleston, SC
Posts: 58
Default Re: A/C Breaker size

Paul,
Frequently I see data plates that have a labeled max and min allowing a range.
Reply With Quote
  #21  
Old 9/18/07, 5:51 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C Breaker size

Quote:
Originally Posted by rgallahorn
Paul,
Frequently I see data plates that have a labeled max and min allowing a range.
Paul's comment was that when it is stated "Max fuse or circuit breaker", it is ALWAYS a common fuse or breaker size.
When the "Minimum circuit ampacity" is listed it is the actual circuit ampacity.

I have never seen different in the hundreds of A/C units I have wired.
Reply With Quote
  #22  
Old 9/19/07, 1:32 PM
David Nice's Avatar
David Nice David Nice is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Wauwatosa, WI
Posts: 1,697
Default Re: A/C Breaker size

Quote:
Originally Posted by pabernathy
AHHHH...but does it...lol.......how about some pictures of this phantom "DATA PLATE"...lol
For obvious reasons I don't take pictures of data plates, but I read them with a magnifying glass. It did indeed read 58 amps for MAX breaker size.



David Nice
National Certified Inspection Services, Inc.
Wauwatosa, WI

http://www.nationalcertified.com
414-979-6900
President WiNACHI
http://www.winachi.com
Wisconsin InterNACHI Chapter


Reply With Quote
  #23  
Old 9/19/07, 1:33 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,556
Default Re: A/C Breaker size

Quote:
Originally Posted by dnice
For obvious reasons I don't take pictures of data plates, ...
Not obvious to me, why?
Reply With Quote
  #24  
Old 9/19/07, 1:50 PM
David Nice's Avatar
David Nice David Nice is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Wauwatosa, WI
Posts: 1,697
Default Re: A/C Breaker size

Quote:
Originally Posted by mlarson
Not obvious to me, why?
Data Plate facing house. No room for a camera, which is often the case.



David Nice
National Certified Inspection Services, Inc.
Wauwatosa, WI

http://www.nationalcertified.com
414-979-6900
President WiNACHI
http://www.winachi.com
Wisconsin InterNACHI Chapter


Reply With Quote
  #25  
Old 9/19/07, 2:10 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,556
Default Re: A/C Breaker size

Quote:
Originally Posted by dnice
Data Plate facing house. No room for a camera, which is often the case.
I use a macro setting that focuses to less than 10 in. from the lense. Canon S2
Reply With Quote
  #26  
Old 9/19/07, 2:23 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A/C Breaker size

Quote:
Originally Posted by rgallahorn
Paul,
Frequently I see data plates that have a labeled max and min allowing a range.
Not what I am speaking of....the Max and Min refer to two different things...Minimum Ampacity and Maximum OCPD ( or fuse )...two different things.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #27  
Old 9/19/07, 2:26 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A/C Breaker size

Quote:
Originally Posted by dnice
For obvious reasons I don't take pictures of data plates, but I read them with a magnifying glass. It did indeed read 58 amps for MAX breaker size.
David,

Not for me to say the obvious...but I take pictures of them all the time and with my 5.0 megapixel camera I have no problem reading them and it is just nice to keep with the records in case you are going back to the office and possible looking up additional info...life manufacturers numbers and so on...

But then again....I am not doubting you fella....only giving education as it is not my inspection...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #28  
Old 9/19/07, 2:34 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,948
Default Re: A/C Breaker size

Quote:
Originally Posted by pabernathy
David,

Not for me to say the obvious...but I take pictures of them all the time and with my 5.0 megapixel camera I have no problem reading them and it is just nice to keep with the records in case you are going back to the office and possible looking up additional info...life manufacturers numbers and so on...

But then again....I am not doubting you fella....only giving education as it is not my inspection...
I do also take pictures mainly for my use and protection .
I get places where I can not read the oil tank or AC.
My $99:00 kodiac will go as close as 4 inches and I can blow that picture up on the Camera to confirm I have the info I need .
Liked it so much bought a spare holds 985 pictures so I can take pictures of every thing does a great job.
... Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #29  
Old 9/19/07, 2:39 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A/C Breaker size

Cool Roy....I just dont want David to think I was rippin him..I was not David. I was only saying ( in my way ) that it is very hard for someone like me or speedy to give comments on it because we see ALOT of them and in regards to dwellings I am simply not used to seeing anything that says 58A only.....chances are if it is real old....report it as beyond its life and move on....otherwise all I was saying is it is very strange to see a nameplate for an HVAC unit that does not have a Min Amp and Max OCPD rating listed on the plate...thats all.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #30  
Old 9/19/07, 2:49 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,307
Default Re: A/C Breaker size

I would make a quick call to Carrier

Here is how I read it

Max BKR does not say max current. Come down one standard size if stated current will be with in the bkr limits

What I see the Carrier doing is saying under their breath is do not use a 60 amp bkr

Sure would like to see how this one works out

rlb
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Tell me again what size wire goes on a 100 amp breaker? jfunderburk Electrical Inspections 3 8/20/07 11:39 PM
Minimum Size Breaker for Sub Panel rmoewe Electrical Inspections 7 5/21/07 7:24 PM
Service wire size to breaker panel sfalvey Electrical Inspections 12 10/31/06 5:28 PM
30 amp breaker wire size kweiss Electrical Inspections 18 10/10/06 10:53 PM
Main Breaker Size cpennick Electrical Inspections 13 9/20/06 11:56 PM


All times are GMT -4. The time now is 8:38 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts