Quote:
|
Originally Posted by Greg Fretwell
I can see this going both ways. Certainly 240.4(B) would make this OK with nothing else considered but you run up against 110.3(B). The label does say 58a Max.
|
I agree that the label controls. But in my mind
NEC 240.4.B really applies to upsizing an
OCPD for a given ampacity of wires, and not upsizing a breaker for a stated Max
OCPD from an AC condenser label (which is usually 175% to 225% of the load already per
NEC 440.22).
For AC condensers you can upsize the
OCPD from 175% of RLA, as long as it doesn't exceed 225% of the RLA per 440.22. But most manufacturers already consider this with the stated Max Breaker/Fuse Size on the equipment label.
Quote:
|
Originally Posted by dnice
Large carrier A/C unit calls for Max breaker size of 58 amps. Is a 60 amp breaker in the main panel a problem?
|
What was the model number & serial number?
Also did you note the Running Load Amps (RLA) and the Minimum Circuit Ampacity from the nameplate?
Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee