Default A/C Circuit Breaker

I find this quite often and wondered if you are finding this also. On the air conditioning unit the data plate said recommended breaker size-40 amps. Maximum breaker size 40 amps. The breaker in the service panel is only 30 amps which is undersized. Many times I find units labeled for a 20 amp breaker on the data plate and 30 amp in the panel. I write it up every time. Anybody else see this or am I missing something?
Reply With Quote
Find an InterNACHI certified Wyoming Home Inspector (and anywhere else in North America)
  #2  
Old 12/17/09, 3:53 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C Circuit Breaker

Quote:
Originally Posted by dlee2 View Post
I find this quite often and wondered if you are finding this also. On the air conditioning unit the data plate said recommended breaker size-40 amps. Maximum breaker size 40 amps. The breaker in the service panel is only 30 amps which is undersized. Many times I find units labeled for a 20 amp breaker on the data plate and 30 amp in the panel. I write it up every time. Anybody else see this or am I missing something?
Which of these concerns you (you asked about both)?

Max breaker (per data plate) of 40A and a 30A in the panel.
No issue here.

or

Max breaker (per data plate) of 20A and a 30A in the panel.
Write it up
Reply With Quote
  #3  
Old 12/17/09, 3:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: A/C Circuit Breaker

There is a minimum circuit ampacity and a maximum allowable circuit breaker size.

The breaker size is not allowed to exceed the maximum capacity requirement, but it does not necessarily need to meet the max. size.

The minimum tells you what the minimum conductor size needs to be, even if the breaker is oversized for the conductor.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 12/17/09, 3:59 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C Circuit Breaker

Quote:
Originally Posted by rmaday View Post
Which of these concerns you (you asked about both)?

Max breaker (per data plate) of 40A and a 30A in the panel.
No issue here. Agree

or

Max breaker (per data plate) of 20A and a 30A in the panel.
Write it up unless the proper size is in the disconnect
.......
Reply With Quote
  #5  
Old 12/17/09, 5:17 PM
David K. Lee David K. Lee is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Florence, Ky
Posts: 97
Default Re: A/C Circuit Breaker

Thanks for the advice
Reply With Quote
  #6  
Old 12/18/09, 12:40 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A/C Circuit Breaker

David,

Just make sure the MCA is a conductor that can handle the MCA listed and make sure that on the MOP does not exceed the listing given.

MCA : 28A ( would install a 10 AWG )
MOP : 40A ( would install a 40A or less breaker/fuse if it will hold )

It would also be important to remind everyone that IF the AC Compressor says "Fuse Only" then fuses must be in the system. Either at the panel or a the units disconnect. This does not mean the disconnect at the AC Compressor is required to be fused at all as it can be non-fused ( simple pull out ) but let say the nameplate says "Fuse Only" and you have a circuit breaker in th electrical panel...how would you comply. Simply change the non-fused disconnect to a fused disconnect and it would be compliant.

Just a tidbit of additional information.....in brief form.



Paul W. Abernathy

Last edited by pabernathy; 12/18/09 at 12:44 AM..
Reply With Quote
  #7  
Old 12/18/09, 12:47 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C Circuit Breaker

Paul, on this topic, why can the conductor sizes for AC units vary from the common 14 AWG for 15 A breaker, etc?

I know the proper answer is "because the manufactiurer says so", but why!?

TIA
Reply With Quote
  #8  
Old 12/18/09, 1:55 AM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,274
Default Re: A/C Circuit Breaker

Start up if I remember right.



Paul Pendley
Premier Property Inspections
866-458-8516
Reply With Quote
  #9  
Old 12/18/09, 7:18 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C Circuit Breaker

Rick, wire sizing for AC are sized based on Article 440. The OCP is to allow the compressor to be able to start without tripping the breaker. This is a short term event. The wire is sized for the running current of the unit which is less than what is used at startup.
Reply With Quote
  #10  
Old 12/21/09, 8:12 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A/C Circuit Breaker

Jim...is your name Paul....lol.....just kidding fella......Answer Away



Paul W. Abernathy
Reply With Quote
  #11  
Old 12/21/09, 10:14 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C Circuit Breaker

I'll leave you the tough ones for the Guru site.
Reply With Quote
  #12  
Old 12/21/09, 11:18 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A/C Circuit Breaker

lol.....Aint no tough ones over there......



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Article 240 : Overcurrent Protection Article pabernathy Electrical Inspections 0 5/23/07 11:40 AM


All times are GMT -4. The time now is 5:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts