Default A/C electrical disconnect fuses

look what i found today .... oddly enough i rarely pull the handle out, but for some reason i did today. glad i did so!! ill have to make that part of my SOP from now on.

Reply With Quote
  #2  
Old 11/14/07, 7:05 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C electrical disconnect fuses

Could be the unit does not require fuses. Still, they should have used a non fusible disconnect as I doubt if those pieces of copper are UL listed.
Reply With Quote
  #3  
Old 11/14/07, 8:10 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: A/C electrical disconnect fuses

Nice cartridge fuses......Can you say FIRE
Reply With Quote
  #4  
Old 11/14/07, 8:25 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: A/C electrical disconnect fuses

There are proper dummy fuses unfortunately they are hard to find and A piece of copper is handy .
This system should be protected at the Panel and this is just an Isolating disconnect, to alow the service man to work on the system and know every thing is dead.

AN unfused disconnect can cost more and are not as easy to find so this is done frequently.

Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #5  
Old 11/14/07, 9:02 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C electrical disconnect fuses

Brian and Roy are right on. There is NO danger here, just a non-compliant install.
All I ever used for A/C condensors are non-fused pull-outs.

That's funny Roy. Around here I can get non-fused pullouts everywhere for around $10-$12. Fused are just as easy to get but more $$.

I bet this guys either had the disconnect but didn't have fuses, or didn't realize he bought the fused version from the home center and again, didn't have fuses with him.
Reply With Quote
  #6  
Old 11/15/07, 5:29 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: A/C electrical disconnect fuses

Quote:
Originally Posted by Speedy Petey
Brian and Roy are right on. There is NO danger here, just a non-compliant install.
All I ever used for A/C condensors are non-fused pull-outs.

That's funny Roy. Around here I can get non-fused pullouts everywhere for around $10-$12. Fused are just as easy to get but more $$.

I bet this guys either had the disconnect but didn't have fuses, or didn't realize he bought the fused version from the home center and again, didn't have fuses with him.
Huh, I never thought of it that way. I guess because I've never ran into this type of situation. I guess the most important thing to consider in this situation is whether or not it's properly protected at the SE.
Reply With Quote
  #7  
Old 11/15/07, 5:37 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: A/C electrical disconnect fuses

And by the way....Thanks for the red square guys. I really appreciate it.

Why didn't you sign your name, gutless? If you're giving out reds (free), simply sign your name like man.
Reply With Quote
  #8  
Old 11/15/07, 6:40 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: A/C electrical disconnect fuses

Quote:
Originally Posted by dvalley
And by the way....Thanks for the red square guys. I really appreciate it.

Why didn't you sign your name, gutless? If you're giving out reds (free), simply sign your name like man.
Some one called them Pea Brains and I guess it fits .
I would like to Apologize for those who feel they must attack those who might not agree with their thinking .
We all are home inspectors and need the ability to disagree some times .
This usually leads to a great discusion where we all lean.
I guess Pea brain might just fit some of them.
Last week I got three reds for posts I made and one person did the correct thing, sign their name.

.... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #9  
Old 11/15/07, 7:27 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C electrical disconnect fuses

Quote:
Originally Posted by dvalley
And by the way....Thanks for the red square guys. I really appreciate it.

Why didn't you sign your name, gutless? If you're giving out reds (free), simply sign your name like man.
It's funny, I was just last night checking my UserCP. I noticed I had another red. Again, no sig or explanation.
Like I said in an earlier thread when I asked what those little green boxes were, I really don't care what my reputation points are. But.....if I make a post that offends someone, or if I do something really wrong (posting wise) have at it, AND sign you name like a man. That's like throwing a snowball in someone's face and hiding behind a wall snickering. Childish.
Don't give me a red and not tell me what it is for just because you disagree with me.
I personally thing that whole system is totally flawed. It's like Ebay's feedback used to be. Anyone could give you a neg for no reason and it stayed forever.

Let's see how many reds this gets me.
Reply With Quote
  #10  
Old 11/15/07, 8:27 AM
bmargiotti bmargiotti is offline
New User
 
Join Date: Feb 2005
Location: Berea, OH
Posts: 66
Please Note: bmargiotti is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C electrical disconnect fuses

thanks for the replies. although i understood that the condensor is protected in the main panel, this fuseable disconnect is not being used properly. i dont like to see equipment installed and rigged together because the installer didnt have the right piece at the time.

in this case the unit was at least 60 feet away from the panel.
Reply With Quote
  #11  
Old 11/15/07, 8:31 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A/C electrical disconnect fuses

Still violated the intent of the UL approval on the piece of equipment, when we violate the intent of a product the product could cause issues. Notice the bent push in points, using a WHAT IF mentality here....I would call it out simply because it is improper installation and workmanship and a violation of the NEC®..but then again I am a NEC Junkie anyway.

The other concern is IF someone is willing to do this with a simply disconnect, we need to look at the main point of overcurrent protection and make sure it is sized properly.....it compounds the issue if for chance the OCPD is also oversized and is not offering any protection and allowing an improper installation method to well.....become a problem down the road.

Just my opinions.....I never like to see equipment installed improperly but again since I am not nostridomas I will not make comment on it's potential safety....lol



Paul W. Abernathy
Reply With Quote
  #12  
Old 11/15/07, 8:33 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: A/C electrical disconnect fuses

Quote:
Originally Posted by bmargiotti
thanks for the replies. although i understood that the condensor is protected in the main panel, this fuseable disconnect is not being used properly. i dont like to see equipment installed and rigged together because the installer didnt have the right piece at the time.

in this case the unit was at least 60 feet away from the panel.
You can buy inserts to take the place of fuses .
I agree not the best practice.
The concern is with double fusing is that if there is an over load and a fuse blow .
John Q usually does not know they had double fuses and even if the did they usually have no idea how to find a blown fuse Most just change two fuses and carry on.
In this case they would have to change ( if the saw the two fused disconnect) 4 fuses.
60 feet away and out of sight thats why an Isolating disconect is needed at the AC.
... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #13  
Old 11/15/07, 8:35 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A/C electrical disconnect fuses

Quote:
Originally Posted by Speedy Petey
It's funny, I was just last night checking my UserCP. I noticed I had another red. Again, no sig or explanation.
Like I said in an earlier thread when I asked what those little green boxes were, I really don't care what my reputation points are. But.....if I make a post that offends someone, or if I do something really wrong (posting wise) have at it, AND sign you name like a man. That's like throwing a snowball in someone's face and hiding behind a wall snickering. Childish.
Don't give me a red and not tell me what it is for just because you disagree with me.
I personally thing that whole system is totally flawed. It's like Ebay's feedback used to be. Anyone could give you a neg for no reason and it stayed forever.

Let's see how many reds this gets me.
lol.....Peter it has become a part of life on this board....I post THOUSANDS of posts I believe are helpful but only a handful of green boxes....just part of being unappreciated fella, you"ll get used to it....BUT the fact is you are appreciated and ignore the people who are vendictive my friend.......its all part of the game.



Paul W. Abernathy
Reply With Quote
  #14  
Old 11/15/07, 8:21 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: A/C electrical disconnect fuses

Bob

Can't tell you how many times I've seen that setup. Usually found while checking the A/C unit and finding a fried relay, contactor or compressor.
The homeowner was usually the culprit, and usually said S*** alot when he heard how much it would cost to repair his handy work.
Reply With Quote
  #15  
Old 11/15/07, 8:26 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A/C electrical disconnect fuses

What are these red squares and how do I get one?

Last edited by brian winkle; 11/15/07 at 8:38 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 3:58 PM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 1:14 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 1:48 AM


All times are GMT -4. The time now is 5:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts