Default A/C Feeder size Question 14 ga on 20 amp?

When inspecting service panels, I compare the wire sizes to the breaker sizes. #14 AWG (Cu) - Max 15 amp breaker, #12 AWG (Cu) - Max 20 amp, and so on. Many times I will catch a #14 AWG (Cu) attached to a 20 amp breaker and call that out as a potential safey hazard.

Here's the question, What is correct call when there is a #14 AWG (Cu)attached to a 20 AMP 220V breaker for an A/C unit? The namplate of the A/C is attached.

Minimum Circuit amps 12.6 (#14 AWG Cu is OK)
Running Load Amps 9.0 x 125% = 11.25 (#14 AWG CU is OK)
Maximum breaker size 20 amps OK

14 AWG Cu on a 20 amp breaker. Circuit breaker too large for wire capacity. Recommend evaluation by a licensed electrician

I evidently ticked off the electrician when he was called back to this property because of this. Without being technically exhaustive (knowing what circuits feed what in the home) How should this be reported?

I will be talking with the local AHG on Monday morning. I've also have seen #12 AWG on a 25 amp and 30 amp breakers in the past.
Attached Thumbnails
c-feeder-size-question-14-ga-20-amp-c-panel.jpg   c-feeder-size-question-14-ga-20-amp-c-plate.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America)
  #2  
Old 4/4/09, 3:43 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: A/C Feeder size Question 14 ga on 20 amp?

The #14 on the 20 amp breaker was fine. It goes by manufacturer's recommendations. When you have any type of a/c, follow the nameplate info on the back. As you stated, the min ckt amps is 12.6. The #14 will be the minimum you can use. It is also stated that 20 amp is the max OCPD you can use.
If you want to follow along in the code book 2005 NEC). 204.4(G) says to follow table 204.4(G). The table in turn says to follow the rules in 440 art III. 440.22 (C) says to follow manufacturer's values.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #3  
Old 4/4/09, 3:44 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: A/C Feeder size Question 14 ga on 20 amp?

Don't know why the electrician was p.o'd. He got some money on a call for doing nothing.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #4  
Old 4/4/09, 3:54 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: A/C Feeder size Question 14 ga on 20 amp?

It's perfectly acceptable and common practice. The breaker size will almost always exceed the conductor-ampacity in the circuit for the condenser unit.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 4/4/09, 6:53 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: A/C Feeder size Question 14 ga on 20 amp?

Quote:
Originally Posted by jpope View Post
It's perfectly acceptable and common practice. The breaker size will almost always exceed the conductor-ampacity in the circuit for the condenser unit.
So to correctly evaluate a service panel with an A/C system, the manufacture's data takes precidence. HMMM... So one has to be a little more careful while doing this inspection and actually be a little more technically exhaustive.

What I'm getting at is it's better to call out for an electrician to evaluate the system if the components are not identified on the panel in the first place rather than assuming the conductors actually go to the a/c if they happen to be undersized.

What happens for well pumps when the manufacture's data plate is rarely available? According to the NEC, these conductors could also be undersized for the breaker attached.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sump Pit/Pump Question Joey D'Adamo Plumbing Inspections 4 11/26/08 1:04 PM
Wire size? nbhi Electrical Inspections 50 3/4/08 1:10 PM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical Inspections 13 2/8/07 1:18 PM
Flue Size when size matters? msylvester Inspecting HVAC Systems 14 1/20/07 11:29 PM
Rule of Thumb A/C sizing question from Practice Exam gliebig Inspecting HVAC Systems 9 5/25/06 1:38 AM


All times are GMT -4. The time now is 5:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts