Default Cables through sub panel

I know that cables are not allowed to pass through service panels without landing on a terminal or bus bar. Can they pass through sub panels? This cable comes from the service panel, is spliced in the sub (different sized wires) and continues on to an exterior disconnect. It does land on the ground bus, but that's all.
Attached Thumbnails
cables-through-sub-panel-sub.jpg  



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #2  
Old 2/26/09, 2:42 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Cables through sub panel

Bill,

It appears to be a simple splice to extend the cable. Looks good to me.
Reply With Quote
  #3  
Old 3/2/09, 1:51 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cables through sub panel

Will you take a look again ?

Look at red taped white tape conductor what it landed behind the conductors that don't add up right.

Have a electrician check out the system.

Is this in the pool pumphouse ?

If so that need to be check more futher by electrician.

Merci,Marc
Reply With Quote
  #4  
Old 3/5/09, 10:19 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cables through sub panel

Looks wrong to me. Unless the box is specifically rated to be used as a raceway (which none of them are) then it is wrong. It does not, however, probably affect anything.
Reply With Quote
  #5  
Old 3/5/09, 10:51 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Cables through sub panel

Bill what type of conduit was that?.
Off subject,but I am curious.
Reply With Quote
  #6  
Old 3/5/09, 11:12 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Cables through sub panel

NFG...

Looks like a through-splice, which is prohibited.
Reply With Quote
  #7  
Old 3/6/09, 5:45 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Cables through sub panel

Quote:
Originally Posted by jfarsetta View Post
NFG...

Looks like a through-splice, which is prohibited.

Joe,

Please expand....Why isn't this splice allowed?
Reply With Quote
  #8  
Old 3/6/09, 5:20 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Cables through sub panel

There is nothing in code that prohibits splicing or passing through a panelbox. I take that back, if the % fill is exceeded, then it is illegal.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #9  
Old 3/7/09, 6:31 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Cables through sub panel

Quote:
Originally Posted by jwicklander View Post
There is nothing in code that prohibits splicing or passing through a panelbox. I take that back, if the % fill is exceeded, then it is illegal.

Jeff
That's my thought.
Reply With Quote
  #10  
Old 3/7/09, 11:10 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Cables through sub panel

My understanding that a splice within a panel is permitted, providing however that the terminus is within the panel, itself.
Reply With Quote
  #11  
Old 3/7/09, 11:39 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Cables through sub panel

Quote:
Originally Posted by jfarsetta View Post
My understanding that a splice within a panel is permitted, providing however that the terminus is within the panel, itself.

Well, this is new to me.

If this is true, I'd like a reference please.
Reply With Quote
  #12  
Old 3/9/09, 5:59 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Cables through sub panel

I stand corrected by Jeff and David.

Through-splices are indeed allowed providing that there is adequate space and that the power is from the same service.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Commercial Electrical Inspections jtedesco1 Commercial Inspections 29 1/12/08 5:03 AM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts