Old 3/8/06, 1:32 PM
David C. Macy's Avatar
Default Calling all gurus!!
The panel today I made note of 10Gauge wire to 40 amp breakers.
My question is about more than 1 or 2 wires connected at the grounding or nuetral bars. I noted an area with 3 and there are some vacancies at the bus.
Do I need to call this out or am I being picky? Or Am I full of crap. (Just kidding)
Dave
Old 3/8/06, 2:06 PM
Jeffrey R. Pope's Avatar
Default Re: Calling all gurus!!
The appliance connected to the 40 amp breaker may be a condenser and possibly allowed. If you did not already do it, have a sparky confirm that while he/she is correcting the neutral/ground bus.
Multiple neutrals is a relatively new restriction, but I don't believe that grounds and neutrals were ever allowed to share a termination.
I ain't no Guru, but that's how I would call it.
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 3/8/06, 2:14 PM
David P. Valley's Avatar
David,
Write it up as "Double lugged neutrals". Each neutral wire must be on a separate terminal (408.21)
Only 1 neutral wire is allowed under a single lug. I see this defect every day and I also write it up every day.
Don't forget about the white "hot wire" on your second pic. It must be marked as a hot by having an Electrician wrapping black tape around the end of the wire.
Old 3/8/06, 2:22 PM
Thanks
Jeff may be right about the 40 amp breaker. There was no A/C just the shut off & old refrigerant lines.
I would disagree with you Jeff about not being a guru.
You always take the time to answer on this forum and you seem to know your stuff.
Dave
Old 3/8/06, 2:45 PM
...and, fortunately, he knows our stuff. too...