  #1  
Old 11/3/06, 7:57 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default calrifications needed.

The main was installed in a bathroom. The panel was recently installed.

When the new box is installed. Lets say in 2004. Is the electrician required to updqate the home to the latest NEC? There where no visible main ground connections, No exterior ground rod. Ect...

I know the box isnt allowed to be in the bathroom.

It looks like there are some 14 gauge wire to 20Amp breakers. Is the main aluminum wire rated for 100 amps. Looks like #1 or 2. This would be 80 Amps.

Any explanation would be appreciated.

Would like to also add about how other inspectors note bathrooms that have the older light fixture with receptacle? Am I correct in advising that they remove the old fixture & install a light bar and add a GFCI?

Can a 220 line be installed on a board? The one I observed the board was loose.

Thanks

Dave

Paul A. I am looking forward to your class in december. Please make a note that I am attending. I will register soon.
Attached Thumbnails
calrifications-needed-85106-cleve-038-small-.jpg.jpg
Views:	78
Size:	39.4 KB
ID:	6620   calrifications-needed-85106-cleve-035-small-.jpg.jpg
Views:	70
Size:	44.8 KB
ID:	6621   calrifications-needed-85106-cleve-040-small-.jpg.jpg
Views:	67
Size:	56.0 KB
ID:	6622   calrifications-needed-85106-cleve-041-small-.jpg.jpg
Views:	71
Size:	58.7 KB
ID:	6623  
Reply With Quote
  #2  
Old 11/3/06, 8:02 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: calrifications needed.

I've been told by some electricians, they had to do somethings messed up. "had to do", like this situation, the electrician probably had no choice since the service cables came in there, or the bathroom was a diy'er job, and it was originally a small office, or etc, etc, etc. The new electrician was following bad work previously made. I usually respond with, "you could have just walked away".

<walking away shaking head>

tom
Reply With Quote
  #3  
Old 11/3/06, 8:18 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: calrifications needed.

Is it safe???????????????

When and code are not something that we want to get into

GFCI while not required when work was done but is a very good safety recomendation

Look at the whole thing from a safety issue ... Grounding is a safety issue

I would pass the whole mess to an electrican --- safety

I would not go into NEC or local code at all

It might even have been sign off by the local BI -- who knowes

rlb
Reply With Quote
  #4  
Old 11/3/06, 8:35 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,646
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: calrifications needed.

I dont know how they do it in OHIO, but down here in Florida, they are SUPPOSED to pull a permit for and upgrade (like they ever do), which would require that the box be moved out of the bathroom and that GFCI's be installed. Also, the ceiling in that picture is not sealed.

I would write it up as an improper installation, listing all the defects that you noted, including that my client do a permit search, and recommend repair by a licensed electrician.
Reply With Quote
  #5  
Old 11/3/06, 10:56 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: calrifications needed.

This is an interesting situation.
Up until the 1993 NEC, the panels were permitted in bathrooms. So if this is an upgrade of an existing panel that was approved prior, then the question is would it be required to be relocated when upgraded??? I would call the building department and ask them.

But note that the toilet is directly below the panel... that has never been permitted. [110.26(A)]
Reply With Quote
  #6  
Old 11/3/06, 11:42 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: calrifications needed.

And would this be a plumbing violation or an electrical??


Again - lets stay away from code and say is there a safety problem here

Yes there is -- and thus call it as same

rlb
Reply With Quote
  #7  
Old 11/4/06, 1:14 AM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: calrifications needed.

But if you can't have the toilet in front of the panel, what are you going to stand on to check it?



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #8  
Old 11/4/06, 12:01 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: calrifications needed.

Quote:
Originally Posted by rbennett
And would this be a plumbing violation or an electrical??


rlb
Electrical...violates the SAFE workspace and dedicated space provision.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Oshawa inspector needed aspisak Canadian Inspectors 2 8/16/07 9:27 PM
Action needed in NY jruppert Legislation, Licensing & Legal Issues for Inspectors 1 6/14/07 9:53 PM
Action needed in NY jruppert Legislation, Licensing & Legal Issues for Inspectors 0 6/14/07 11:24 AM
Volunteer home inspectors needed to help elderly/disabled. gromicko Miscellaneous Discussion for Inspectors 1 11/13/06 7:33 AM
Greg Bell or someone in Titusville/Palm Bay Florida area needed to do inspections gromicko Miscellaneous Discussion for Inspectors 1 7/25/06 2:00 AM


All times are GMT -4. The time now is 2:59 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts