Default Re: Can an AFCI offer GFCI protection

Quote:
Originally Posted by pabernathy
"The standard AFCIs have GFP and not GFCI protection built in. The term GFCI should be reserved for "people protective eqquipment". A GFCI has a ground fault trip level of 4 to 6 mA, but the GFP in an AFCI has a trip level of 30 to 50 mA." from Mike Holt Forum.
As stated...

Quote:
Originally Posted by pabernathy
"They have TWO different functions......but NO ONE can deny they are MERGING as we speak.....if the standards is SIMPLY the function......then yes they do TWO different things......but one device CAN do both....

Just remember and this is important....if someone has a AFCI breaker...DO NOT let them assume it also has GFCI protection.....chances are VERY high it does not....and IF it did the breaker would say so.....very important...read my COMPARE of the different models above.......
Quote:
Originally Posted by pabernathy

If I again HAD to tell someone to have AFCI and GFCI protection in a panel that does NOT have a dual AFCI/GFCI listing breaker available....they should use a STANDARD AFCI for the panel and replace the FIRST receptacle in the branch with a GFCI receptacle...and they will effectivly have the protection....


However keep in mind the newer models of AFCI/GFCI combination do provide both...as previously posted...but in basic terms....again a standard AFCI does not offer any level of GFCI " Personal Protection "



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #17  
Old 7/6/06, 10:30 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Can an AFCI offer GFCI protection

APPOLOGIES to Gerry.........We did not keep it simple.....sorry!



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #18  
Old 7/6/06, 10:33 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Can an AFCI offer GFCI protection

You need to verify which one is installed but there are combo AFCI/GFCIs
Reply With Quote
  #19  
Old 7/6/06, 10:37 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Can an AFCI offer GFCI protection

Agreed....

"The FIRE-GUARD™ Arc Fault Circuit Interrupter (AFCI) is a residential circuit breaker with an integrated processor which recognizes the unique current and/or voltage signatures associated with arcing faults, and acts to interrupt the circuit to reduce the likelihood of an electrical fire. With the Cutler-Hammer FIRE-GUARD AFCI, protection from arcing faults is combined with conventional thermal and magnetic overloads as found in standard residential circuit breakers protecting wiring from excessive heat or damage due to overloading or short circuits. FIRE-GUARD AFCI can also be equipped with 5 mA ground fault protection to protect from personal shock hazards. Now, there is a residential circuit breaker that provides protection from arcing faults, conductor damage due to thermal overloads and short circuits, as well as 5 mA ground fault protection in one integrated design."



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #20  
Old 7/7/06, 12:45 AM
Joe Lyvers, CMI's Avatar
Joe Lyvers, CMI Joe Lyvers, CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Gulf Breeze, FL
Posts: 101
Default Re: Can an AFCI offer GFCI protection

Quote:
Originally Posted by rcooke
Great article thanks . Just did a condo really perfect . Pushed GFCI test buton heard the snap but the power did not go of .
Used my tester no response.
This was 12 years old and for 12 years they have had no GFCI protection.
For this the person was very glad he had a home inspector .
You just never know .
No idea what was wrong this was for the condo to fix.
Roy sr
Roy, I encounter this problem very frequently. It's been my experience to learn that the LINE and LOAD wires are switched. Some installers just don't read the instructions on the back.



Joe Lyvers
Gulf Breeze, Florida
NACHI04040881
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 1:29 PM
double GFCI protection rperkerewicz Electrical Inspections 11 10/9/07 7:06 PM
Stacking AFCI, GFCI breakers abolt Electrical Inspections 6 4/17/07 11:57 AM


All times are GMT -4. The time now is 4:41 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts