Default Can anyone tell me when

they started using three wire Romex (grounded) in res construction?

I think I know this but I'm having a senior's moment
Cheers



Doug Cossar CMI, NHI
Accurate Home Inspection
Services Inc.
Whitby Ontario
www.accuratehomeinspections.ca
05021384
Reply With Quote
  #2  
Old 7/18/08, 9:59 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Can anyone tell me when

Quote:
Originally Posted by dcossar
they started using three wire Romex (grounded) in res construction?

I think I know this but I'm having a senior's moment
Cheers
Hi Doug I belive type NM (thermoplastic) "romex" started in the early 1960's

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 7/18/08, 10:19 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Can anyone tell me when

Quote:
Originally Posted by gbeaumont
Hi Doug I belive type NM (thermoplastic) "romex" started in the early 1960's

Regards

Gerry
Hi. Gerry

I found this in http://en.wikipedia.org/wiki/Electri...wiring_methods


About 1950, PVC insulation and jackets were introduced, especially for residential wiring. About the same time, single conductors with a thinner PVC insulation and a thin nylon jacket became common.

Marcel
Reply With Quote
  #4  
Old 7/18/08, 10:26 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Can anyone tell me when

Quote:
Originally Posted by mcyr
Hi. Gerry

I found this in http://en.wikipedia.org/wiki/Electri...wiring_methods


About 1950, PVC insulation and jackets were introduced, especially for residential wiring. About the same time, single conductors with a thinner PVC insulation and a thin nylon jacket became common.

Marcel
Hi Marcel, thanks for that, I knew the "romex" brand started in the 1920's with the rubber and cloth braided stuff, but I didn't know that the thermoplastics started that early, I have never seen in in an unimprooved home built before the early 60's.

I see it mostly from when outlet grounds were required which I think was 1963.

Here's a link to the history of Romex

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 7/18/08, 11:46 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Can anyone tell me when

Thanks for the Link Gerry.

1922 whow! You must remember that don't you. ha. ha.

Marcel
Reply With Quote
  #6  
Old 7/18/08, 12:15 PM
Douglas Cossar's Avatar
Douglas Cossar Douglas Cossar is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Whitby, On
Posts: 1,152
Default Re: Can anyone tell me when

Quote:
Originally Posted by gbeaumont
Hi Marcel, thanks for that, I knew the "romex" brand started in the 1920's with the rubber and cloth braided stuff, but I didn't know that the thermoplastics started that early, I have never seen in in an unimprooved home built before the early 60's.

I see it mostly from when outlet grounds were required which I think was 1963.

Here's a link to the history of Romex

Regards

Gerry
Thanks Gerry... sooooo grounded outlets were first required in 1963?

Cheers



Doug Cossar CMI, NHI
Accurate Home Inspection
Services Inc.
Whitby Ontario
www.accuratehomeinspections.ca
05021384
Reply With Quote
  #7  
Old 7/18/08, 12:56 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Can anyone tell me when

Quote:
Originally Posted by dcossar
Thanks Gerry... sooooo grounded outlets were first required in 1963?

Cheers
That requirement came in in the 1962 NEC, so was locally adopted in 1963/4 in most cases.

There is a nice history of residential wiring here

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #8  
Old 7/18/08, 4:12 PM
Douglas Cossar's Avatar
Douglas Cossar Douglas Cossar is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Whitby, On
Posts: 1,152
Default Re: Can anyone tell me when

Excellent info thanks Gerry

Cheers



Doug Cossar CMI, NHI
Accurate Home Inspection
Services Inc.
Whitby Ontario
www.accuratehomeinspections.ca
05021384
Reply With Quote
  #9  
Old 7/18/08, 4:18 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Can anyone tell me when

Quote:
Originally Posted by dcossar
Excellent info thanks Gerry

Cheers
You're welcome, just remember what I have quoted is from the U.S. Canadian code may be a bit different.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #10  
Old 7/18/08, 6:14 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Can anyone tell me when

Quote:
Originally Posted by gbeaumont
That requirement came in in the 1962 NEC, so was locally adopted in 1963/4 in most cases.

There is a nice history of residential wiring here

Regards

Gerry
That's good reading! Thanks Gerry.
Reply With Quote
  #11  
Old 7/18/08, 6:16 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Can anyone tell me when

I don't know about the ground wire itself, but the "reduced ground" went away in 1969. I know I've worked on wiring from the late 50's that had a ground wire in it, but installers often had no idea what to do with it. Regrettably, it was often just cut off flush with the jacket.
Reply With Quote
  #12  
Old 7/18/08, 6:43 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Can anyone tell me when

Quote:
Originally Posted by gbeaumont
You're welcome, just remember what I have quoted is from the U.S. Canadian code may be a bit different.

Regards

Gerry
Hey, I thought you were Brit. all this time.
Reply With Quote
  #13  
Old 7/18/08, 8:28 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Can anyone tell me when

We lived in a house built in 1952-53 PG county, right over the DC line. It had the reduced size ground wire in an asphalt/paper jacket Romex and SqD breaker panel.
My father said it had to do with "GI" inspection. I assume from what I have heard fom around the country, this may have only been enforced near DC.
I know when I bought my first house in 71, the builder said it wouldn't go "GI" (aluminum wire) but by then you could get cheaper financing from a regular bank.
Reply With Quote
  #14  
Old 7/18/08, 8:33 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Can anyone tell me when

Quote:
Originally Posted by Marc D. Shunk
I don't know about the ground wire itself, but the "reduced ground" went away in 1969. I know I've worked on wiring from the late 50's that had a ground wire in it, but installers often had no idea what to do with it. Regrettably, it was often just cut off flush with the jacket.
I have to admit to having written up a couple of reduced grounds years ago before I new that they had previously been allowed

I had forgotten all about them again until just now.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #15  
Old 7/18/08, 8:41 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Can anyone tell me when

Hey Mark and Gerry, that is exactly the wiring in my own house.

The old 14/2 with ground conductor 16 gauge and all cut off at the jacket.
Some I was able to fix with the slack and some are not.

House was built in 1967. And the wiring romex is still the cloth fabric type. I forget the word for it already.

Marcel
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 10:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts