On another post in relation to double tapped neutrals, parallel conductors was mentioned (see below). Can someone explain to me what is meant by that and how I could identify it?
Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor. Robert Sole, CMI 407-637-7288 Florida license numbers HI 169 and MRSA 92 Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties. RobertSole@REMinspections.com Check out my blog orlandohomeinspections.info/ REMinspections.com OrlandoHomeInspector.net |
| Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Where is that exception located? Are you asking a general question about what are parallel conductors?
|
|
#3
|
||||
|
||||
|
Yes. I am asking about parallel conductors. The exception is part of the NEC that says that only one neutral can be located under a screw on the neutral buss in the panel but it listed an exception if it is with parallel conductors (or circuits). I am trying to figure out what they are and how I could identify them by looking in the panel.
Robert Sole, CMI 407-637-7288 Florida license numbers HI 169 and MRSA 92 Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties. RobertSole@REMinspections.com Check out my blog orlandohomeinspections.info/ REMinspections.com OrlandoHomeInspector.net |
|
#4
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
OK, parallel conductors allow you to connect multiple conductors on both ends to create, in affect, one larger conductor. This is usually done in commercial work where the ampacities of circuits exceed 400 amps and it's easier or cheaper to install multiple sets of parallel conductors instead of installing one set of larger conductors.
The exception is pointing out that if you had a lug listed for more than one conductor it can be used to terminate two neutral conductors which are generally limited to one conductor per hole. Here's a few photo's: Lugs listed for one or two conductors: Parallel conductor terminations in a 500KVA transformer: |
|
#5
|
||||
|
||||
|
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#6
|
||||
|
||||
|
|
|
#7
|
||||
|
||||
|
Thanks for the information. I do understand parallel circuits in DC but it did not make sense in AC current. It doesn't look like I will run into this much in residential inspections.
Robert Sole, CMI 407-637-7288 Florida license numbers HI 169 and MRSA 92 Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties. RobertSole@REMinspections.com Check out my blog orlandohomeinspections.info/ REMinspections.com OrlandoHomeInspector.net |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Please Explain | jevans | Plumbing Inspections | 5 | 8/29/08 10:17 PM |
| A fake (temporary) site I built to help explain where we are going with this... | gromicko | Miscellaneous Discussion for Inspectors | 63 | 6/8/07 1:23 AM |
| Please explain.... | abolt | Electrical Inspections | 6 | 3/11/07 2:38 PM |