A Pool Filter Needs to be on it's own gfi breaker
|
|
#3
|
||||
|
||||
|
1. The gfci outlet there is missing the cover.
2. The conduit appears to have 90 deg. fittings that are not rated for electrical use. (white vs gray) 3. Trip hazard on the sidewalk. 4. Conduit is not properly secured. 5. Recommend electrician correct the installation and check the pool for other improper practices. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#4
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
||||
|
||||
|
Please Note:
rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Not really needed but...
2 (b) ...and even if they were allowed the unprotected PVC elbows will deteriorate in sunlight and become brittle. |
|
#6
|
||||
|
||||
|
Yea you posted it!
Harvey Gordon - President - FloridaNACHI (The OFFICIAL Florida State Chapter of NACHI) SEFloridaNACHI (Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties) ______________ Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org ______________ |
|
#7
|
||||
|
||||
|
Please Note:
jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Not to mention subject to physical damage (across sidewalk).
|
|
#8
|
||||
|
||||
|
The title of this thread says, "Can you cite a code?"
No one is citing a code yet. Where are all the code citers? Out with the apple ciders? |
|
#9
|
||||
|
||||
|
Please Note:
dmcauley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Bruce is on the right track with the multiple errors on this.
|
|
#10
|
||||
|
||||
|
Duh, trip hazard?
David Nice National Certified Inspection Services, Inc. Wauwatosa, WI http://www.nationalcertified.com 414-979-6900 President WiNACHI http://www.winachi.com Wisconsin InterNACHI Chapter |
|
#11
|
||||
|
||||
|
Here's a couple.
406.8 Receptacles in Damp or Wet Locations. (A) Damp Locations. A receptacle installed outdoors in a location protected from the weather or in other damp locations shall have an enclosure for the receptacle that is weatherproof when the receptacle is covered (attachment plug cap not inserted and receptacle covers closed). An installation suitable for wet locations shall also be considered suitable for damp locations. (B) Wet Locations. (1) 15- and 20-Ampere Outdoor Receptacles. 15- and 20-ampere, 125- and 250-volt receptacles installed outdoors in a wet location shall have an enclosure that is weatherproof whether or not the attachment plug cap is inserted. 352.6 Listing Requirements. RNC, factory elbows, and associated fittings shall be listed. 352.12 Uses Not Permitted. (C) Physical Damage. Where subject to physical damage unless identified for such use. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 3/14/06 at 11:13 AM.. |
|
#12
|
|||
|
|||
|
On the rare chance if I do CITE code I will get rapped accross the coals by some California HillBilly....I take the 5th....
And RR...I dont even like Apple Cider.... Paul W. Abernathy |
|
#13
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I know you won't like the answer but I could not get my AHJ (Lee County Fla) to tag a RNC running across a sidewalk in a very similar installation. They said it was OK. The elbows and lack of "in use" cover are still clear violations.
|
|
#14
|
|||
|
|||
|
can't tell by the pic, but it also needs to be a minimum of 5 feet from the water
"If God was one of us, would he recommend a detailed analysis by a structural engineer for the world?" Michael S. Saxton http://www.duluthhomeinspections.com |
|
#15
|
||||
|
||||
|
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Coeur d'Alene, ID Home Inspectors | rspriggs | Miscellaneous Discussion for Inspectors | 12 | 1/8/09 5:16 PM |
| Importance of the AHJ check | mcyr | General Inspection Discussion | 6 | 2/21/07 8:18 PM |
| Chicagoland Electrical Code Ordinance | jtedesco1 | Electrical Inspections | 0 | 6/16/06 2:10 PM |