Old 3/13/06, 11:54 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
Default Can someone tell me what is wrong with this picture. Can you cite a code?
http://www.nachi.org/whatswronghere1.htm
Find a Home Inspector
Old 3/14/06, 12:09 AM
Terrance D. Kelley Terrance D. Kelley is offline
Default Re: Can someone tell me what is wrong with this picture. Can you cite a code?
A Pool Filter Needs to be on it's own gfi breaker
Old 3/14/06, 12:17 AM
Bruce A. King's Avatar
1. The gfci outlet there is missing the cover.
2. The conduit appears to have 90 deg. fittings that are not rated for electrical use. (white vs gray)
3. Trip hazard on the sidewalk.
4. Conduit is not properly secured.
5. Recommend electrician correct the installation and check the pool for other improper practices.
www.BAKingHomeInspections.com
704 301-3207
Old 3/14/06, 12:43 AM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
ditto
Old 3/14/06, 1:57 AM
rmoore's Avatar
rmoore rmoore is offline
Please Note: rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Not really needed but...
2 (b) ...and even if they were allowed the unprotected PVC elbows will deteriorate in sunlight and become brittle.
Old 3/14/06, 2:04 AM
Harvey L. Gordon's Avatar
Harvey L. Gordon Harvey L. Gordon is offline
Yea you posted it!
Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________
Old 3/14/06, 4:02 AM
jclark1's Avatar
jclark1 jclark1 is offline
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Not to mention subject to physical damage (across sidewalk).
Old 3/14/06, 4:47 AM
Russel Ray's Avatar
The title of this thread says, "Can you cite a code?"
No one is citing a code yet. Where are all the code citers? Out with the apple ciders?
Old 3/14/06, 10:57 AM
dmcauley's Avatar
dmcauley dmcauley is offline
Please Note: dmcauley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Bruce is on the right track with the multiple errors on this.
Old 3/14/06, 11:53 AM
David Nice's Avatar
David Nice David Nice is offline
Duh, trip hazard?
David Nice
National Certified Inspection Services, Inc.
Wauwatosa, WI
http://www.nationalcertified.com
414-979-6900
President WiNACHI
http://www.winachi.com
Wisconsin InterNACHI Chapter
Old 3/14/06, 11:59 AM
Jeffrey R. Pope's Avatar
Here's a couple.
406.8 Receptacles in Damp or Wet Locations.
(A) Damp Locations. A receptacle installed outdoors in a location protected from the weather or in other damp locations shall have an enclosure for the receptacle that is weatherproof when the receptacle is covered (attachment plug cap not inserted and receptacle covers closed).
An installation suitable for wet locations shall also be considered suitable for damp locations.
(B) Wet Locations.
(1) 15- and 20-Ampere Outdoor Receptacles. 15- and 20-ampere, 125- and 250-volt receptacles installed outdoors in a wet location shall have an enclosure that is weatherproof whether or not the attachment plug cap is inserted.
352.6 Listing Requirements.
RNC, factory elbows, and associated fittings shall be listed.
352.12 Uses Not Permitted.
(C) Physical Damage. Where subject to physical damage unless identified for such use.
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 3/14/06, 12:44 PM
Paul W. Abernathy's Avatar
On the rare chance if I do CITE code I will get rapped accross the coals by some California HillBilly....I take the 5th....
And RR...I dont even like Apple Cider....
Paul W. Abernathy,CMI,CPI,CME
Old 3/14/06, 1:11 PM
I know you won't like the answer but I could not get my AHJ (Lee County Fla) to tag a RNC running across a sidewalk in a very similar installation. They said it was OK. The elbows and lack of "in use" cover are still clear violations.
Old 3/14/06, 1:16 PM
msaxton msaxton is offline
can't tell by the pic, but it also needs to be a minimum of 5 feet from the water
"If God was one of us, would he recommend a detailed analysis by a structural engineer for the world?"
Michael S. Saxton
http://www.duluthhomeinspections.com
Old 3/14/06, 1:21 PM
Russel Ray's Avatar
And I thought you were up to a challenge.
Coeur d'Alene, ID Home Inspectors rspriggs Miscellaneous Discussion for Inspectors 12 1/8/09 6:16 PM
Importance of the AHJ check mcyr General Inspection Discussion 6 2/21/07 9:18 PM