I used properly sized wire nuts and a pigtail wire to connect the grounding wires in my outlet. So the wire nut has three grounding wires in it - one from the wire coming into the box, one feeding the outlet, and the other going on to the next outlet.
I'm told by my contractor that I cannot use wire nuts, that I *have* to use crimp connectors for the grounding wire. Is this true? I've got about 75 connections done this way so I'd like confirmation before taking the effort to change it all before the inspection. I want to do it right according to code and will change them if needed, but I thought wire nuts were an acceptable alternative for grounding wires?? |
| Need a home inspection in Texas? Check out InterNACHI's listing of Texas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
No idea where you live but it's OK in my area and I expect it is approved in most places.... Roy
Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#3
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
There is nothing in the NEC to prohibit this. Is this a local amendment?
|
|
#4
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Unless there's a local amendment as Jim mentioned standard wire connectors are fine for EGC's. You just cannot use the Greenie wire nuts (with the hole in the end) for ungrounded and neutral conductors.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Evaluating your home's wiring system | mcyr | Electrical Inspections | 0 | 12/30/09 1:31 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |