Default Re: Can you spot the problem?

Sorry guys!

I was out of town. Robert wins this one.
The mains are 60 Amps but there are two apartments with two stoves and two hot water tanks. They cannot have a dryer because the service is too small.
The three wires serve the grounds and neutrals to two units. The disconnects are for two apartments that makes it have service of 60 amps/apt. A stove needs 40 Amps.
The tell tale sign is the two grounds on one lug in 60 Amp panel.
Panel is only rated for 100 Amps this puts the panel at 20Amps over
Water was only warm and the element was broken on one oven.
I wonder why?



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 8/15/11 at 3:54 AM..
Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 8/15/11, 5:32 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Can you spot the problem?

Quote:
Originally Posted by kwood View Post
The mains are 60 Amps but there are two apartments with two stoves and two hot water tanks. They cannot have a dryer because the service is too small.
The three wires serve the grounds and neutrals to two units. The disconnects are for two apartments that makes it have service of 60 amps/apt. A stove needs 40 Amps.
The tell tale sign is the two grounds on one lug in 60 Amp panel.
Panel is only rated for 100 Amps this puts the panel at 20Amps over
Water was only warm and the element was broken on one oven.
I wonder why?
Sounds like a mess. But Im not really following what ya mean by the 100A panel is 20A over.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #18  
Old 8/15/11, 6:12 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Can you spot the problem?

Panel is only rated for 100 Amps. The panel is down stream from two 60 Amp main disconnects.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #19  
Old 8/15/11, 6:22 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Can you spot the problem?

Quote:
Originally Posted by kwood View Post
Panel is only rated for 100 Amps. The panel is down stream from two 60 Amp main disconnects.
That matters not the service is a 60 amp service .
It just says the panel can be used as part of a 100 amp service .
It goes back to the weakest link .

It is also cheaper now to buy a 100 amp panel then a 60 panel and it has room for more breakers .
Example
Just because some one puts in 2 inch conduit and a 200 amp panel it has wires for 150 amp and a 150 amp breaker it is a 150 amp service .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #20  
Old 8/15/11, 6:53 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Can you spot the problem?

It is not 60 Amps it is over 100 Amps I could not determine the size. There are two meters outside and a mess of ungrounded and reverse wiring.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #21  
Old 8/15/11, 7:13 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Can you spot the problem?

Quote:
Originally Posted by kwood View Post
It is not 60 Amps it is over 100 Amps I could not determine the size. There are two meters outside and a mess of ungrounded and reverse wiring.

Quote:
The panel is down stream from two 60 Amp main disconnects.
There can only be one service disconnect (main).



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #22  
Old 8/15/11, 7:17 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Can you spot the problem?

Quote:
Originally Posted by kwood View Post
It is not 60 Amps it is over 100 Amps I could not determine the size. There are two meters outside and a mess of ungrounded and reverse wiring.
Pictures?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #23  
Old 8/15/11, 7:22 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Can you spot the problem?

I only provided the one for education purposes.
Here is the other one.
I could not put my camera on Macro so this picture did not turn out well.
Attached Thumbnails
can-you-spot-problem-p6157666.jpg  



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #24  
Old 8/15/11, 7:35 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Can you spot the problem?

Quote:
Originally Posted by kwood View Post
I only provided the one for education purposes.
Here is the other one.
I could not put my camera on Macro so this picture did not turn out well.

Is the feed from the top in conduit?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #25  
Old 8/15/11, 8:12 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Can you spot the problem?

Yes it is



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #26  
Old 8/15/11, 11:21 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Can you spot the problem?

There likely is another breaker/fuse distribution panel somewhere. I have seen them in strange locations (e.g. behind a mirror in a 2nd floor bathroom, inside kitchen cabinets, behind pictures, etc). With two meters you would have the two main fused service disconnects (one for each meter/service), with each one of those likely feeding a separate distribution panel.

Probably a panel for each apartment. One would have a black-black-white (H-H-N) feeder from one of the 60A fused disconnects to a distribution panel, and the other one would have a black-red-white (H-H-N) feeder from the other 60A fused disconnect to another distribution panel. The conduit is likely the ground to the distribution panel. What were the number and color of the wires going to the 100A panel you did find?

Also in the fused service disconnect boxes it looks like 3-wire feeders (H-H-N) come in from the meters and go out to distribution panels in conduit, then there is a white wire used for the earth ground (GEC), and two brown wires used for the neutral-case/ground bond.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 8/15/11 at 11:32 PM..
Reply With Quote
  #27  
Old 8/16/11, 6:27 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Can you spot the problem?

I found one fuse panel in the upstairs apt.
I found two conduits going to one possible 100 Amp service. It cannot be two hundred amp because of the 100 Amp panel.
I am still stumped how this could have been wired.
I did not pay attention to anymore detail after I found the double wire situation in the neutral lugs.
I told my client to seek advice from certified electrician.
They are going to correct it by installing 200 Amp service and panel.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Weird water heater problem kweiss Plumbing Inspections 3 4/5/09 6:34 PM
cold spot showing in wall Fran Walters Thermal Imaging, Infrared Cameras & Energy Audits 4 3/31/09 4:54 PM
furnace problem ? Aaron lore General Inspection Discussion 11 2/5/09 1:04 PM
Internet browser problem bking Miscellaneous Discussion for Inspectors 33 1/26/09 1:45 AM
I have a problem cbottger Electrical Inspections 17 1/20/09 4:45 PM


All times are GMT -4. The time now is 5:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts