Ran into this today doing a new construction final. Any issues with having the low voltage network cable in the main electrical panel enclosure or in the conduit with the other wires? The builder said it is for future smart meter installation but I don't know why it would be in the panel for that.
Any input would be appreciated. Thanks Josh Lutz Southwest Premier Home Inspection, LLC Phoenix Home Inspection Phoenix Home Inspectors Visit our Phoenix Home Inspection Blog Serving the entire Phoenix Metro area including Glendale, Scottsdale, Tempe, Paradise Valley, Peoria and more... |
| Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Not allowed.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Thanks Jeff, I was pretty certain it wasn't allowed but had to follow up and check. Would you be able to point me in the direction of some documentation to send the builder?
Thanks Josh Lutz Southwest Premier Home Inspection, LLC Phoenix Home Inspection Phoenix Home Inspectors Visit our Phoenix Home Inspection Blog Serving the entire Phoenix Metro area including Glendale, Scottsdale, Tempe, Paradise Valley, Peoria and more... |
|
#4
|
||||
|
||||
|
It's covered in Article 800 of the NEC (maybe a sparkie can help out with the best reference for this case), but it's referenced as "separation from other conductors."
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
The issue is that in case of a wiring fault you could have high voltage on the low voltage conductors and going to equipment and insulation systems that aren't designed to handle it.
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Looks like there may be more than just a problem with the CAT5 cables but here's the relevant section from the 2008 NEC:
Quote:
|
|
#7
|
|||
|
|||
|
Thanks for the info Robert. Other problems were noted in the report but my question was about the Cat 5.
Josh Lutz Southwest Premier Home Inspection, LLC Phoenix Home Inspection Phoenix Home Inspectors Visit our Phoenix Home Inspection Blog Serving the entire Phoenix Metro area including Glendale, Scottsdale, Tempe, Paradise Valley, Peoria and more... |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Green stuff on wire in main panel | bforeman | Electrical Inspections | 6 | 12/21/09 8:09 PM |
| Main panel...recommendation ? | dnasser | Electrical Inspections | 6 | 11/22/09 9:55 PM |
| Main Panel vs Sub-Panel and main disconnect? | rbassett | Electrical Inspections | 11 | 10/24/09 6:16 PM |
| Subpanel wired as main panel. | jlybolt | Electrical Inspections | 15 | 5/23/07 4:10 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |