Ran into this today doing a new construction final. Any issues with having the low voltage network cable in the main electrical panel enclosure or in the conduit with the other wires? The builder said it is for future smart meter installation but I don't know why it would be in the panel for that.


Any input would be appreciated.

Thanks
Attached Thumbnails
cat-5-wire-main-electrical-panel-008.jpg  




Josh Lutz
Southwest Premier Home Inspection, LLC

Phoenix Home Inspection

Phoenix Home Inspectors

Visit our Phoenix Home Inspection Blog

Serving the entire Phoenix Metro area including Glendale, Scottsdale, Tempe, Paradise Valley, Peoria and more...
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/8/10, 7:44 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Cat 5 wire in main electrical panel

Not allowed.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 10/8/10, 7:53 PM
Joshua D. Lutz Joshua D. Lutz is offline
InterNACHI Member
 
Join Date: May 2008
Location: Glendale, AZ
Posts: 32
Default Re: Cat 5 wire in main electrical panel

Thanks Jeff, I was pretty certain it wasn't allowed but had to follow up and check. Would you be able to point me in the direction of some documentation to send the builder?

Thanks




Josh Lutz
Southwest Premier Home Inspection, LLC

Phoenix Home Inspection

Phoenix Home Inspectors

Visit our Phoenix Home Inspection Blog

Serving the entire Phoenix Metro area including Glendale, Scottsdale, Tempe, Paradise Valley, Peoria and more...
Reply With Quote
  #4  
Old 10/8/10, 8:22 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Cat 5 wire in main electrical panel

It's covered in Article 800 of the NEC (maybe a sparkie can help out with the best reference for this case), but it's referenced as "separation from other conductors."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 10/8/10, 8:24 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Cat 5 wire in main electrical panel

The issue is that in case of a wiring fault you could have high voltage on the low voltage conductors and going to equipment and insulation systems that aren't designed to handle it.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #6  
Old 10/8/10, 9:18 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Cat 5 wire in main electrical panel

Looks like there may be more than just a problem with the CAT5 cables but here's the relevant section from the 2008 NEC:

Quote:
800.133 Installation of Communications Wires, Cables, and Equipment.
Communications wires and cables from the protector to the equipment or, where no protector is required, communications wires and cables attached to the outside or inside of the building shall comply with 800.133(A) through (C).
(A) Separation from Other Conductors.
(1) In Raceways, Cable Trays, Boxes, and Cables.
(a)Other Power-Limited Circuits. Communications cables shall be permitted in the same raceway, cable tray, or enclosure with cables of any of the following:
(1) Class 2 and Class 3 remote-control, signaling, and power-limited circuits in compliance with Article 725
(2) Power-limited fire alarm systems in compliance with Article 760
(3) Nonconductive and conductive optical fiber cables in compliance with Article 770
(4) Community antenna television and radio distribution systems in compliance with Article 820
(5) Low-power network-powered broadband communications circuits in compliance with Article 830
(b) Class 2 and Class 3 Circuits. Class 1 circuits shall not be run in the same cable with communications circuits. Class 2 and Class 3 circuit conductors shall be permitted in the same cable with communications circuits, in which case the Class 2 and Class 3 circuits shall be classified as communications circuits and shall meet the requirements of this article. The cables shall be listed as communications cables.
Exception: Cables constructed of individually listed Class 2, Class 3, and communications cables under a common jacket shall not be required to be classified as communications cable. The fire-resistance rating of the composite cable shall be determined by the performance of the composite cable.
(c) Electric Light, Power, Class 1, Non–Power-Limited Fire Alarm, and Medium-Power Network-Powered Broadband Communications Circuits in Raceways, Compartments, and Boxes. Communications conductors shall not be placed in any raceway, compartment, outlet box, junction box, or similar fitting with conductors of electric light, power, Class 1, non–power-limited fire alarm, or medium-power network-powered broadband communications circuits.
Exception No. 1: Where all of the conductors of electric light, power, Class 1, non–power-limited fire alarm, and medium-power network-powered broadband communications circuits are separated from all of the conductors of communications circuits by a permanent barrier or listed divider.
Exception No. 2: Power conductors in outlet boxes, junction boxes, or similar fittings or compartments where such conductors are introduced solely for power supply to communications equipment. The power circuit conductors shall be routed within the enclosure to maintain a minimum of 6 mm (0.25 in.) separation from the communications circuit conductors.
Exception No. 3: As permitted by 620.36.
(2) Other Applications. Communications wires and cables shall be separated at least 50 mm (2 in.) from conductors of any electric light, power, Class 1, non–power-limited fire alarm, or medium-power network-powered broadband communications circuits.
Exception No. 1: Where either (1) all of the conductors of the electric light, power, Class 1, non–power-limited fire alarm, and medium-power network-powered broadband communications circuits are in a raceway or in metal-sheathed, metal-clad, nonmetallic-sheathed, Type AC, or Type UF cables, or (2) all of the conductors of communications circuits are encased in raceway.
Exception No. 2: Where the communications wires and cables are permanently separated from the conductors of electric light, power, Class 1, non–power-limited fire alarm, and medium-power network-powered broadband communications circuits by a continuous and firmly fixed nonconductor, such as porcelain tubes or flexible tubing, in addition to the insulation on the wire.
Reply With Quote
  #7  
Old 10/8/10, 10:18 PM
Joshua D. Lutz Joshua D. Lutz is offline
InterNACHI Member
 
Join Date: May 2008
Location: Glendale, AZ
Posts: 32
Default Re: Cat 5 wire in main electrical panel

Thanks for the info Robert. Other problems were noted in the report but my question was about the Cat 5.




Josh Lutz
Southwest Premier Home Inspection, LLC

Phoenix Home Inspection

Phoenix Home Inspectors

Visit our Phoenix Home Inspection Blog

Serving the entire Phoenix Metro area including Glendale, Scottsdale, Tempe, Paradise Valley, Peoria and more...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Green stuff on wire in main panel bforeman Electrical Inspections 6 12/21/09 8:09 PM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
Main Panel vs Sub-Panel and main disconnect? rbassett Electrical Inspections 11 10/24/09 6:16 PM
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts