Default What caused this?

This is a doorbell transformer that has soot on the wall above it. Any ideas?
Attached Thumbnails
caused-img_9243.jpg  
Reply With Quote
  #2  
Old 7/15/08, 12:23 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: What caused this?

Ghosting unless the transformer smoked from getting real buzzed at some time in the past



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #3  
Old 7/15/08, 12:24 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: What caused this?

Tab, Any idea what is on the other side of that wall?




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #4  
Old 7/15/08, 12:24 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,564
Default Re: What caused this?

did the door bell work Tab....looks like it might be time for a new transformer.....jim



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #5  
Old 7/15/08, 12:27 AM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What caused this?

Okay, Great replies! The master bath is on the other side of the wall. The doorbell works..
Reply With Quote
  #6  
Old 7/15/08, 12:28 AM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: What caused this?

Those D_mn sales people keep bothering us.
Transformer fried? or overheated.



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #7  
Old 7/15/08, 12:29 AM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What caused this?

Barry, The transformer could have smoked and they did not clean the wall after replacement.
Reply With Quote
  #8  
Old 7/15/08, 12:31 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,564
Default Re: What caused this?

according to Barry it sounds like You need ghost busters....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #9  
Old 7/15/08, 12:32 AM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What caused this?

who you gonna call!!
Reply With Quote
  #10  
Old 7/15/08, 12:42 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: What caused this?

The reason I asked is at the top of the transformer cover plate, it almost looks like there is some dust. If the transformer was put in a wall that uses the void as ducting, there could be an air leak at the top of the cover plate and when the hvac unit is in use it could blow dust / impurities along the same pathway up the wall. How's that for outside the box....... The only reason I don't think it would be ghosting is that normally occurs where a stud is located. In this instance the transformer would have been installed in a junction box in the middle of a stud? This is interesting.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County

Last edited by sstanczyk; 7/15/08 at 12:45 AM..
Reply With Quote
  #11  
Old 7/15/08, 3:29 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: What caused this?

Quote:
Originally Posted by sstanczyk
The only reason I don't think it would be ghosting is that normally occurs where a stud is located. In this instance the transformer would have been installed in a junction box in the middle of a stud? This is interesting.
maybe you missed this in the link

"A wall's thermal characteristics, construction practices, and climatic conditions influence wall surface temperatures."

ghosting does not have to be throughout or outline studs. I've seen this isolated above the individual hollywood type make-up mirror bulbs and above lamps on ceilings I'll look for pix later if proof is required

transformer is a continual heat source, heat rises, particles/soot/smoke adhere and telegraph the heat rise...has anyone ever tried to clean this?

for all I know it's the dreaded toxic crap the media and lawyers smoke over...that's the ticket it's lawyer smoke...

anything according to me is ghosts and smoke



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #12  
Old 7/15/08, 6:53 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What caused this?

Quote:
Originally Posted by badair
maybe you missed this in the link

"A wall's thermal characteristics, construction practices, and climatic conditions influence wall surface temperatures."

ghosting does not have to be throughout or outline studs. I've seen this isolated above the individual hollywood type make-up mirror bulbs and above lamps on ceilings I'll look for pix later if proof is required

transformer is a continual heat source, heat rises, particles/soot/smoke adhere and telegraph the heat rise...has anyone ever tried to clean this?

for all I know it's the dreaded toxic crap the media and lawyers smoke over...that's the ticket it's lawyer smoke...

anything according to me is ghosts and smoke
Hard to make a good, honest and correct call these days, Barry!!
Reply With Quote
  #13  
Old 7/15/08, 6:55 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What caused this?

Quote:
Originally Posted by badair
transformer is a continual heat source, heat rises, particles/soot/smoke adhere and telegraph the heat rise...has anyone ever tried to clean this?
BINGO!

My mother has had this for years. She burns a lot of candles and just the soot from the candles will do this.
Electric basebaord heaters are one of the worst culprits.
Reply With Quote
  #14  
Old 7/15/08, 8:14 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,564
Default Re: What caused this?

Quote:
Originally Posted by badair
maybe you missed this in the link

"A wall's thermal characteristics, construction practices, and climatic conditions influence wall surface temperatures."

ghosting does not have to be throughout or outline studs. I've seen this isolated above the individual hollywood type make-up mirror bulbs and above lamps on ceilings I'll look for pix later if proof is required

transformer is a continual heat source, heat rises, particles/soot/smoke adhere and telegraph the heat rise...has anyone ever tried to clean this?

for all I know it's the dreaded toxic crap the media and lawyers smoke over...that's the ticket it's lawyer smoke...

anything according to me is ghosts and smoke

good information Barry...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #15  
Old 7/15/08, 8:48 AM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,828
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: What caused this?

Jehovah witness?

Sorry...couldn't resist.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What caused this gporter Interior Inspections 10 6/22/06 2:27 AM


All times are GMT -4. The time now is 2:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts