Default Challenger Box

I inspected a home with a chalenger electrical panal last week and all was fine other than 1 breaker was Westinghouse and 1 was GE. The label indicated Challenger breakers be used. I suggested they be replaced.

My client aked the seller to make a few repairs and this was one. I was back there today to inspect the repairs. The seller left a note indicating several local hardware stores advised that Challenger boxes will accept Westinghouse, GE and a couple of other breakers. I can not find anything to confirm this.

Anyone have anything that will help?

Thanks



Steve Rinner
GLH Home Inspections
Norwalk, Ohio
Reply With Quote
Find an InterNACHI certified Alaska Home Inspector (and anywhere else in North America)
  #2  
Old 4/8/09, 2:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Challenger Box

Many panels will "accept" off-brand breakers. In most cases, there are no functionality issues, merely a "listing" issue.

Make your point by explaining the manufacturers requirements, and leave it at that.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 4/8/09, 5:16 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Challenger Box

Jeff, what exactly is a "listing issue" and how are we to know when a "functional issue" exists?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 4/8/09, 5:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Challenger Box

The panel is UL Listed based on the manufacturers installation requirements. So installation of off-brand breakers may be contrary to the listing of the equipment.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 4/8/09 at 5:30 PM..
Reply With Quote
  #5  
Old 4/8/09, 5:21 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Challenger Box

Quote:
Originally Posted by jfunderburk View Post
Jeff, what exactly is a "listing issue" and how are we to know when a "functional issue" exists?
Often the manufacturer will only label his device as being compatible with their own products.

BUT component manufactures can and do get a "Classified" label listings that state what products(in this case a panel) they are compatible with.

Classification Mark

Products carrying this mark have been evaluated for specific properties, a limited range of hazards, or suitability for use under limited or special conditions. Typically, products classified by UL fall into the general categories of building materials and industrial equipment.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI


Last edited by mlarson; 4/8/09 at 5:25 PM..
Reply With Quote
  #6  
Old 4/8/09, 5:25 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Challenger Box

So does it need to be evaluated by an electrician? That's what I've been telling people. (I never say they should be replaced...but that it should be evaluated by a licensed and competent electrician.)



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 4/8/09, 5:28 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Challenger Box

Quote:
Originally Posted by jfunderburk View Post
So does it need to be evaluated by an electrician? That's what I've been telling people. (I never say they should be replaced...but that it should be evaluated by a licensed and competent electrician.)
It's really up to the AHJ.

If the breakers are "classified" for use in that panel and teh AHJ accepts it, fine.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #8  
Old 4/8/09, 5:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Challenger Box

Quote:
Originally Posted by jfunderburk View Post
So does it need to be evaluated by an electrician? That's what I've been telling people. (I never say they should be replaced...but that it should be evaluated by a licensed and competent electrician.)
IMHO - Only if the breaker does not seat properly, or if it creates problems with the fit of the dead-front.

In any event, I make note of it, but not necessarily as a "defect."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 4/8/09, 5:35 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Challenger Box

Jeff is right. The manufacturers instructions, as per the NEC, will always outweigh any interpretation of any other code reference.

You are correct to call it out and then leave the negotiations of a remedy up to your client, the seller, and their agents.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #10  
Old 4/8/09, 5:41 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Challenger Box

Here is a very complete discussion of the issue.

in part it states:

The physical interchangeability is not an indication that they are electrically interchangeable. This must be verified by test. Unless the circuit breaker is marked on the panelboard as being acceptable or it is Classified as being acceptable, the circuit breakers have not been tested in the panelboards and should not be used.........

The Classified circuit breaker must be marked to clarify the limitations of use on short circuit applications and series ratings. In addition each breaker is required to have a Compatibility List which, according to the UL Listing Card for Classified circuit breakers, “... tabulates the company name, catalog number, number of poles and electrical rating of the Classified circuit breaker, in addition to the company name and catalog number of the applicable UL Listed panelboards,

Code Compliance

What about the requirements of 110-3(b) of the National Electrical Code? This Code Section requires that products be used in accordance with instructions included in their listing and labeling and the use of Classified circuit breakers does present a dilemma to some inspectors.

The panelboard is marked to indicate the only circuit breakers to be used in the panelboard are the specific Listed circuit breakers with which the panelboards were evaluated and Listed by the panelboard manufacturer. The Classified circuit breakers, on the other hand, also have instructions included in their listing and labeling indicating the specific Listed panelboards for which they have been evaluated for use in. These are not in conflict with each other. Each manufacturer is listing and marking in accordance with the testing they have done. The Classified circuit breaker manufacturer has done testing in addition to the testing done by the panelboard manufacturer.

The final decision on acceptance of Classified circuit breakers, as with any issue, rests with the Authority Having Jurisdiction (AHJ).



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #11  
Old 4/8/09, 5:49 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Challenger Box

Quote:
Originally Posted by mlarson View Post
It's really up to the AHJ.

If the breakers are "classified" for use in that panel and teh AHJ accepts it, fine.
And how do we tell if the particular breaker is "classified" for that use?

Unless the home is brand new, the AHJ's opinion is not relevant. (I think most inspectors on this board put way too much reliance in the expertise of the local gov'ment inspector. In my part of the country, they aren't at the house long enough to turn the car engine off.)



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 4/8/09, 5:50 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Challenger Box

Quote:
Originally Posted by jfunderburk View Post
And how do we tell if the particular breaker is "classified" for that use?

Unless the home is brand new, the AHJ's opinion is not relevant. (I think most inspectors on this board put way too much reliance in the expertise of the local gov'ment inspector. In my part of the country, they aren't at the house long enough to turn the car engine off.)
I understand your frustration Joe. We all share it.

Read that link I posted. It lays it out very well.

It really is beyond the scope of a home inspection as we don;t generally determine the suitability of components but being forewarned with knowledge can save your back side.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #13  
Old 4/8/09, 6:03 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Challenger Box

Good info Mike. . . Thanks!



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Find an InterNACHI certified Alaska Home Inspector (and anywhere else in North America)
  #14  
Old 4/12/09, 8:18 AM
Rollie Meyers Rollie Meyers is offline
New User
 
Join Date: Jul 2007
Location: People's Republic of Chico,CA
Posts: 40
Please Note: Rollie Meyers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Challenger Box

Westinghouse Electric owned Challenger for a number of years up until Eaton bought the electrical division from them & merged them into Eaton's Cutler-Hammer line. There may be some info allowing the Westinghouse breaker in the panel but doubt a GE is "classified" by UL to be used. After Westinghouse took over they discontinued the Challenger breakers & rebranded their BR frame breakers as Challenger, as a final note,some time after Eaton's purchase in 1995 they sold Challenger and the Westinghouse safety switch line to Thomas & Betts (T&B) which then in turned rebranded them as T&B, they were marketed for a few years and then disappeared from the market after that.

On a final note, T&B even got the rights to the beloved Zinsco brand too from what I heard UBI (Unique Breakers Inc.) has the rights now, they if you did not know build cheap quailty Chinese knock-offs of FPE Stab-Loc,Zinsco/Sylvania, & I-T-E Pushmatic C/B's that are sold in big box stores.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breakers in Challenger Service Panel bhartley Electrical Inspections 2 2/3/09 9:35 PM
Challenger Panel hmcclard Electrical Inspections 4 6/28/08 3:48 AM
Challenger Panel- tie bar srowe Electrical Inspections 8 4/20/06 10:30 PM


All times are GMT -4. The time now is 5:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts