Default Checking for proper size wire

Here is some interesting information on wire diameters including the insulation..... (since we don't disconnect wires to check the bare conductor)

Newer 10 gauge wire measures around 3.6 mm including the insulation.

Older 12 gauge type TW wire measures around 4 mm including the insulation.


Be careful, a 30 amp breaker with nice fat wire in an older home could very well be type TW 12 gauge wire!

Note: the newer 12 gauge wire is around 3 mm including the insulation.
Reply With Quote
  #2  
Old 7/12/06, 11:08 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Checking for proper size wire

Bruce, are those dimensions good for all manufacturers of NM cable?

Where did you buy your caliper?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 7/12/06, 12:12 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Checking for proper size wire

It would be nice if the manufacturers would help on this to be sure on the others.

Plastic Calipers are available at the online inspection tool vendors and northern tool has them too.
Reply With Quote
  #4  
Old 7/13/06, 10:29 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking for proper size wire

How is checking the 'size' of a wire within a visual inspection?

Are we now EE's? And if you do not know what a EE is then you most certainly must not be inspecting electrical systems.
Reply With Quote
  #5  
Old 7/13/06, 10:56 PM
rmoore's Avatar
rmoore rmoore is offline
Active Poster
 
Join Date: Feb 2004
Location: Seattle, WA
Posts: 113
Please Note: rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking for proper size wire

How is NOT checking the proper wire sizes at breakers OK for a normal home inspection? If we see a #14 on a 20-amp breaker, you are saying we shouldn't report it? I guess we should also ignore a #14 on a 60-amp breaker according to you!

Mike...I believe an EE is something you constantly put in your mouth with these types of comments.
Reply With Quote
  #6  
Old 7/13/06, 11:02 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking for proper size wire

Richard
A 14awg on a 60amp breaker is not allowed but a 12awg on a 60amp breaker IS.

If I piss you off that is because you do not understand the code.

You made my point.
Reply With Quote
  #7  
Old 7/13/06, 11:24 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking for proper size wire

Richard

My first post was not clear.

I meant that you should not measure wires not look at their awg.

Can we play fair again?
Reply With Quote
  #8  
Old 7/13/06, 11:29 PM
rmoore's Avatar
rmoore rmoore is offline
Active Poster
 
Join Date: Feb 2004
Location: Seattle, WA
Posts: 113
Please Note: rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking for proper size wire

Quote:
Originally Posted by Mike Parks
Richard
A 14awg on a 60amp breaker is not allowed but a 12awg on a 60amp breaker IS.

If I piss you off that is because you do not understand the code.

You made my point.
I'm sure you can come up with some exotic situation where a #12 is Ok on a 60-amp breaker...just to prove your "superiority" over us lowly home inspectors, but this is a home inspectors electrical forum and it is generally understood that, unless otherwise stated, we are talking about NORMAL residential panels and circuits. And yes, I understand the code very well for those.

But you are correct on one issue...you do "piss me off" with your constant inference that HIs should do little more than stand in the middle of a room and stare at the receptacles...and you have been doing so for a few years now. It's a very minor irritation though as, usually, I "consider the source" and ignore you. I think I'll go back to that. Have a nice day.
Reply With Quote
  #9  
Old 7/13/06, 11:36 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking for proper size wire

Richard

I'll give you that I am an ***. That said I took the time to become certified to make the comments that I do.

My posts are to keep inspectors from having their *** sued off.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM
Service wire size to breaker panel sfalvey Electrical Inspections 12 10/31/06 5:28 PM
30 amp breaker wire size kweiss Electrical Inspections 18 10/10/06 10:53 PM