Default Checking temperature of breakers

It seems that several inspectors are checking the temperature of breakers in panels.....

Here are some things you should understand and be able to explain if you are offering this type of inspection:


Do you realize that a bad connection can exist at a breaker or a problem at a load device that will cause the breaker to get hot AND it will not always indicate a high temperatue when you measure it?

Also do you know what the normal temperature would be for a 30 amp breaker feeding a water heater that has been heating for 45 minutes?

Do you realize that a warm 200 amp breaker in the top of a panel does not always indicate a problem with the breaker or excess current? Do you know what else could be wrong?
Reply With Quote
  #2  
Old 7/16/06, 2:11 AM
jmichalski's Avatar
jmichalski jmichalski is offline
Active Poster
 
Join Date: Aug 2004
Location: Souderton, PA
Posts: 2,532
Please Note: jmichalski is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking temperature of breakers

Bruce - I typically test the breaker temps in relation to one another to provide some frame of reference.

I do not claim to know what the normal operating temp is for any breaker - but I do know that when one jumps through the roof - it isn't good. I am not relying on the temp as the sole method of identification of a problem, but it doesn't hurt either.

If you have any information to share with relation to standard operating temps, I would be interested in reading it.
Reply With Quote
  #3  
Old 7/16/06, 7:58 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking temperature of breakers

If you don't know what is the common temp or the minimum or max temp, how can you say diffenitively it is abnormal?
Reply With Quote
  #4  
Old 7/16/06, 9:53 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Checking temperature of breakers

The important thing to remember is that any temperature reading will first require each and every circuit to be adequately loaded for a period of time (at least 30 minutes) then the temperature check made.

I doubt anyone is doing this, so remember to state in your report that all circuit breakers were not checked for abnormal heat during operational conditions.
ie. if you report one hot breaker and did not properly load, wait and test the others you only did a partial inspection for hot breakers.

I do not have any data for standard operating temperatures and do not believe it exists due to many factors such as type of panel, manuf. of breaker, size of wire, ambient temperature, load, load time period, location of breaker in the panel, temperature of adjacent breakers etc.
Reply With Quote
  #5  
Old 7/16/06, 10:08 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Checking temperature of breakers

Quote:
If you don't know what is the common temp or the minimum or max temp, how can you say diffenitively it is abnormal?
Test the amp draw on the ones that are hot. Compare to 80% of the breaker rating. If it is not drawing much current, there is something you need to look into.
Reply With Quote
  #6  
Old 7/16/06, 11:08 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,948
Default Re: Checking temperature of breakers

I must be missing some thing where am I to get the time to check all these things some are talking about .
Why would a home inspector get into checking water pressure water flow per minute ,voltage drop,
current draw, slope of the roof ,How about getting into poor power factor and how to correct it also.
Camera in the chimney how about a bore camera too .
I take about three hours to do my inspections.
Some people must be super man to do all the things people talk about.
How do you transport all the tools you must have and how do you pay for them .
This must just dumbfound some of the new inspectors in what he must learn and carry
I still do the simple inspection with the tools I can carry in my pocket .
Flush the toilet ,turn on tap water comes out must be OK .Check water temp and note it
Marble on the floor little movement slope is fine .
Feel the breakers with back of my fingers not to hot A OK .
Turn up furnace it blows warm are after a few minutes
Thats Good. when it shuts down try AC it starts check split good air movement ,
Thats good.try Bath exhaust Toilet paper test air is exhausting , Thats good .
I do not check amount of air being draw out of Bath exhaust or how much air comes out of register
or what the voltage drop is at Hot water tank .
I still like the KISS (keep it simple stupid ) .
There are a million tests you can get into if you want .
Not for me others may agree.
Roy Cooke Sr. ..Royshomeinspection.com
Reply With Quote
  #7  
Old 7/16/06, 12:46 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Checking temperature of breakers

I agree with most of that Roy,

I just started this thread to help the other guy's that are using test equipment without knowing how and why and what to and not to report about it.

If one NACHI inspector gets in the news over a major problem then we all could look bad.
Reply With Quote
  #8  
Old 7/16/06, 12:53 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking temperature of breakers

Taking those sort of measurements is way beyond any SOP. If they are not part of the SOP how can we all look bad. Its no different in my opinion than reporting on heat loss calculations....
Reply With Quote
  #9  
Old 7/16/06, 1:04 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking temperature of breakers

The value would be in finding something that you should be giving a better visual inspection of. There have been enough pictures of overheated lugs here for you to see what one looks like. The thermo scan might actually let you be able to say a loose connection was fixed too. If the suspect circuit is loaded and the terminal is cool, they fixed it but it still shows the wound.
Reply With Quote
  #10  
Old 7/16/06, 2:04 PM
Jay Schwartz's Avatar
Jay Schwartz Jay Schwartz is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Pembroke Pines, FL
Posts: 593
Default Re: Checking temperature of breakers

Here is a pic of a thermo camera I took a few weeks ago.

My infrared thermometer picked up the same thing.
Attached Thumbnails
checking-temperature-breakers-100_0806-wince-.jpg.jpg
Views:	120
Size:	10.6 KB
ID:	4633   checking-temperature-breakers-100_0805-wince-.jpg.jpg
Views:	100
Size:	13.0 KB
ID:	4634  



Jay Schwartz

Coast To Coast Home Services, Inc
Your Florida Home Inspection Company TM
Corporate Office: 954-673-3479
Naples Office: 239-298-4396
1-877-79-Windstorm

www.CoastToCoastHomeServices.com
www.SaveOnWindStorm.com

South Florida Home Inspectors Association

Southeast Florida NACHI Chapter - VP
Reply With Quote
  #11  
Old 7/16/06, 2:15 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking temperature of breakers

But if its drawing current as it should be, would it not be heating up anyway? Just because its warm does not indicate a problem does it?
Reply With Quote
  #12  
Old 7/16/06, 2:36 PM
jwortham1 jwortham1 is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Bolingbrook, IL
Posts: 721
Default Re: Checking temperature of breakers

Used infrared thermometers all the time when I did industrial electronics.

Regularly found loose breakers connections with no other indications except an elevated temperature reading.

I didn't need to know the "operating temperatures" or what the temperature of a breaker used on a water heater under load should read.

Resistance becomes heat. Since a breaker connection should not have resistance, all the breakers should read roughly the same temperature. If I read 80, 82, 83, 114, 85, I can be relatively sure I have a loose connection. No breaker characteristics needed.

I choose to use the infrared. You may not. Doesn't make either of us wrong. It's just another tool in the box.
Reply With Quote
  #13  
Old 7/16/06, 4:33 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Checking temperature of breakers

Can someone check a water heater breaker that has been heating for at least 30 minutes and has tight connections and tell us the breaker temp. and the ambient temp please?

I am guessing over 100deg F at ambient of 75F would be normal.
Reply With Quote
  #14  
Old 7/16/06, 4:47 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Checking temperature of breakers

I just checked my breakers with my infra red therm. and the basement temp is approx. 53 F. The breakers and the A/C (running) were all reading 57-58 F.
Reply With Quote
  #15  
Old 7/16/06, 5:29 PM
jwortham1 jwortham1 is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Bolingbrook, IL
Posts: 721
Default Re: Checking temperature of breakers

Quote:
I am guessing over 100deg F at ambient of 75F would be normal.
I don't have an electric water heater so I can't test this for you, but over 30% variance in temperature between 2 breakers in the same panel would be anything BUT normal.

Even 200 amps pulled through a breaker should not increase the temperature of that breaker significantly over ambient. If so, there's an impedance issue to be resolved.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Whats the normal temperature for breakers jtaylor5 Electrical Inspections 15 11/6/07 10:15 PM
All Breakers on left side of bus mcotten Electrical Inspections 18 2/1/07 2:24 PM
A/C Temperature Differential cthorsen General Inspection Discussion 3 7/26/06 2:47 PM


All times are GMT -4. The time now is 10:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts