Default Child proof covers?

Hi Inspectors,

When you are doing inspections on receptacles, do you remove those plastic child proofing plug-ins to test them?(the receptacles)
Inspected a house today, and almost every receptacle had these in it. I just figured I was not permitted to remove them? Your thoughts?

Regards,
Reply With Quote
  #2  
Old 1/27/07, 4:10 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Child proof covers?

There are times where I must inspect at least one receptacle per room and I find that every last one is either being utilized or contains a child proof cover. I then don't have a choice but to remove one or two, once in a while.
Reply With Quote
  #3  
Old 1/27/07, 5:06 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Child proof covers?

Same as David. Then I say in my report, "Many receptacles were equipped with child-proof covers. In most circumstances, these covers were not removed for testing."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 1/27/07, 9:58 AM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,067
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Child proof covers?

I pull them out....test the receptacle...put them back in....it is very difficult and painstaking, but I do it anyway for my client.
Reply With Quote
  #5  
Old 1/27/07, 11:18 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Child proof covers?

I think the covers can be considered installed to prevent children from touching receptacles. So the inspector, with a client that has a copy of the SOP's would understand the requirement to remove the covers and replace. I would only make a note that you asked the home owner to verify all caps are secured, to second check your securing of the caps again.

Just a guess....

tom
Reply With Quote
  #6  
Old 1/27/07, 12:12 PM
bsumpter bsumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 232
Default Re: Child proof covers?

I pull and replace every one I can reach.



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #7  
Old 1/27/07, 12:57 PM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 418
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Child proof covers?

Quote:
Originally Posted by tneumann
I pull them out....test the receptacle...put them back in....it is very difficult and painstaking, but I do it anyway for my client.
Tony,
My question was not involved with effort in mind, rather, leaving the things the way the home owner has them, or defacing property.
I have heard of inspectors removing these,(and replacing them), then the home owner saying they were not replaced back properly, and then guess who is at fault if something happens to little Joey if he sticks a bobby pin in it?! So effort was not in mind with this post, covering an inspectors behind was. I was interested in feedback involving this.

Regards
Reply With Quote
  #8  
Old 1/27/07, 2:00 PM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 367
Default Re: Child proof covers?

Doesn't even come close to defacing property etc...No different than taking the electrical panel off for inspection or opening a cupboard door to check under the sink for leaks etc. Just remember to always put things back the way they were when you arrived. It's just a pain in the ***** to R/R them, but we do. The argument that it wasn't put back in correctly........................give me a break, I don't even know how to respond to something that asinine

I'll take my chances and keep removing/replacing them. How does any one know which ones were removed and which ones were not anyway? Usually most are just here and there from my past experiences.



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #9  
Old 1/27/07, 2:42 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Child proof covers?

I remove them when I am testing....just have to be very aware to put them back....but again I would remove them as it is better safe than sorry.

I can just see a homeowner putting them in because they know they have some bootleg grounds or rev. polarity and you don't check them. It could get nasty.

Since you are only doing a sampling by the SOP if you are following it to the letter ( most do not and go a little beyond )...it would be well within your SOP to not test them but heck it only takes a second.

SO my opinion ( which is MY opinion and not an invitation to debate me )...is remove them as needed to check the receptacle on the minimum sampling...but for the record I test ALL receptacles...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 1/27/07, 3:19 PM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 418
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Child proof covers?

Quote:
The argument that it wasn't put back in correctly........................give me a break, I don't even know how to respond to something that asinine
I completely agree. Didn't know if it was one of those horror stories that may be a little too common. Ya hear it all I guess.
Reply With Quote
  #11  
Old 1/27/07, 5:56 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Child proof covers?

One problem I have seen with these is they tend to be thicker than a plug blade and they loosen up the socket
Reply With Quote
  #12  
Old 1/27/07, 6:00 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Child proof covers?

Ahh...you mean decrease the GRAB of the plug itself.....excellent observation greg....I would have never figured that as I though they were about the same thickness.

Must be the ONES made in CHINA



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 1/27/07, 6:20 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: Child proof covers?

Quote:
Originally Posted by dhadler
Doesn't even come close to defacing property etc...No different than taking the electrical panel off for inspection or opening a cupboard door to check under the sink for leaks etc. Just remember to always put things back the way they were when you arrived. It's just a pain in the ***** to R/R them, but we do. The argument that it wasn't put back in correctly........................give me a break, I don't even know how to respond to something that asinine

I'll take my chances and keep removing/replacing them. How does any one know which ones were removed and which ones were not anyway? Usually most are just here and there from my past experiences.
Totally agree - but then, who am I, really?



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #14  
Old 1/27/07, 6:24 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Child proof covers?

When I moved in this house I had to replace every receptacle that had a child plug in it. They wouldn't hold a plug. I just ended up doing them all.
I like spec grade stuff anyway. This may just be a problem with the 39 cent devices that were here, even though they didn't look that old.
Reply With Quote
  #15  
Old 1/27/07, 10:47 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Child proof covers?

Quote:
Originally Posted by jwilliams4
Totally agree - but then, who am I, really?
Hey...thats my line....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Child eviscerated by pool drain mthomas2 Ancillary Inspection Services & Additional Topics 26 7/16/07 5:27 PM
Disposable Shoe Covers jfunderburk General Inspection Discussion 30 4/3/06 9:03 PM