Quote:
Originally Posted by Russ J. Hensel
I was on a condo inspection the other day and found the following issue. I found a HVAC compressor without a heat pump with a 50 Amp breaker wired with #10 awg copper wiring. I stated in my report that the wiring was to small and was a safety issue and that an electrical contractor should evalaute and further evalaute and cure the situation.

The response from the contractor was that in this particualr case, this was acceptable given that it was a motor and peak power...blah blah blah....Is any of this right? I think I was getting some smoke up the keister because if this is the case in the 725 condo's then he is gonna have some splaining to do Lucy.........Just need to know if that in ANY case is a 50 amp breaker allowed and safe with a #10 AWG copper wire? Thanks!
Ask him for the SIGNED OFF permit from the Building Dept. or State Electrical Dept. and then call them yourself and ask what they have to say about it. In YOUR DEPT, Is a 50 amp breaker, 10 gauge wire ok in your book? Simple and to the point.

I WOULD and have many times over, written it up as a safety issue.
Reply With Quote
  #17  
Old 4/8/07, 9:56 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: The circuit breaker wiring confict!

Quote:
Originally Posted by rmccullough
Ask him for the SIGNED OFF permit from the Building Dept. or State Electrical Dept. and then call them yourself and ask what they have to say about it.
They will say the installation IS compliant.


Quote:
Originally Posted by rmccullough
In YOUR DEPT, Is a 50 amp breaker, 10 gauge wire ok in your book? Simple and to the point.
In who's dept?? In the "dept" of ANY licensed electrician or electrical inspector it is most certainly OK, as has been stated many times in this thread.
Because you persoanlly feel it is not "OK" you cannot write it up as "unsafe", simply becasue you do not know all the aspects of the codes for the things you are inspecting.



Quote:
Originally Posted by rmccullough
I WOULD and have many times over, written it up as a safety issue.
See above reply.
This is an incorrect and unfair action directed at the installer.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Article 240 : Overcurrent Protection Article pabernathy Electrical Inspections 0 5/23/07 11:40 AM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM


All times are GMT -4. The time now is 5:51 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts