Quote:
Originally Posted by gkay View Post
Quality, safety, true rms.

This link takes you to flukes' ABC's of multi meter safety. Take the time to learn what makes a quality meter and how to use them safely.

http://support.fluke.com/find-sales/...16_eng_h_w.pdf
If it makes a difference to you I used to test product to UL/CSA 61010-1.

When you say quality, safety and true RMS are you saying one has it and the other doesn't?
Do have a source of more detailed info?
I couldn't verify that from the specs.

BTW-Fluke products are great and I have used them for 40 years.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #17  
Old 3/11/09, 7:15 PM
Sonny C. Shipler Sonny C. Shipler is offline
InterNACHI Member
 
Join Date: May 2007
Location: Beloit, WI
Posts: 79
Default Re: Clamp amp meters

I use a Fieldpiece sc67. Does everything you need. Vac,Vdc,Ohms,amps,temp,continuity,mfd. I think I paid 175.
Reply With Quote
  #18  
Old 3/11/09, 8:35 PM
gkay gkay is offline
New User
 
Join Date: Jan 2009
Location: Olkanagan Valley British Columbiia Canada eh
Posts: 50
Please Note: gkay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clamp amp meters

When you say quality, safety and true RMS are you saying one has it and the other doesn't?
Do have a source of more detailed info?
I couldn't verify that from the specs.

No Michael thats not what I'm saying. I'm sure the P3 you suggested has its applications but in my opinion I didn't think it would suit D.C. Macey's needs. Since he also seems to be new at using electrical meters I thought the price range of $25 dollars coming from a respectable person as yourself might mislead him into buying an inferior meter. The site I refered to was for safety and operation. I am sure there are many less expensive meters that would suit the same purposes.
I'm sure Fluke would be happy to verify any questions regarding specs.
Reply With Quote
  #19  
Old 3/11/09, 9:08 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Clamp amp meters

Quote:
Originally Posted by tphillips View Post
Jeff,
I don't use one. Thinking about it though. Could you explain what you use it for on every inspection?
Tom
As William stated, I use it to check the load on condenser units - remember, I'm in CA, so there's rarely a case where I won't run the A/C. So that's the "every inspection" part. I guess the exception would be when the home does not have A/C.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #20  
Old 3/11/09, 9:11 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,719
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clamp amp meters

I have a Fluke 332. Cost about $125. Here's more info on clamp meters:
http://us.fluke.com/usen/products/Fluke+330.htm

Check out the info on the bottom left.
Reply With Quote
  #21  
Old 3/11/09, 10:08 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,553
Default Re: Clamp amp meters

Quote:
Originally Posted by jpope View Post
As William stated, I use it to check the load on condenser units - remember, I'm in CA, so there's rarely a case where I won't run the A/C. So that's the "every inspection" part. I guess the exception would be when the home does not have A/C.
I have a question for you. When you are testing the load on a condenser what are your parameters for checking. Do you go off the manufacturer's data plate.

I guess since I have never used a clamp meter or tested a condenser with one I was just curious how you went about testing.
Reply With Quote
  #22  
Old 3/12/09, 7:35 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Clamp amp meters

There is a rating on the nameplate for compressor and fan motor.

Note: The compressor will run at all different loads and the amp draw will change all over the place as well.

There are name plates on all motors and compressors themselves as well.

There are three wires (legs) going to a single phase compressor; common, start & run. The amperage in not going to be the same threw all three legs (so you must select your wires wisely).

Three phase (three wire) compressors should have a balanced load across all three.

None of the amp readings should exceed nameplate.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #23  
Old 3/12/09, 10:28 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 7,641
Default Re: Clamp amp meters

http://www.amprobe.com/cgi-bin/pdc/v...in_e&type=elec
I have the older version but works the same , I have all attachments also comes in handy if you need them
Reply With Quote
  #24  
Old 3/12/09, 10:16 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Clamp amp meters

Quote:
Originally Posted by dmacy View Post
I have a question for you. When you are testing the load on a condenser what are your parameters for checking. Do you go off the manufacturer's data plate.

I guess since I have never used a clamp meter or tested a condenser with one I was just curious how you went about testing.
There are no "hard and fast" rules when checking condensers. But generally, you should expect the condenser to be drawing 60% to 75% of its maximum circuit rating. Higher draws may indicate that the unit is working to hard and may be near to failing.

Lower draws may indicate that the system is low on refrigerant, and the compressor is not working hard at all.

In any event, you should never rely solely on the readings of your meter. As with most meters/equipment, you should be looking and/or listening for other indicators that there are problems with the system.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 3/12/09 at 10:20 PM..
Reply With Quote
  #25  
Old 3/13/09, 12:43 AM
tphillips's Avatar
tphillips tphillips is offline
InterNACHI Member
 
Join Date: May 2008
Location: Eau Claire, WI
Posts: 63
Default Re: Clamp amp meters

Thanks for the info guys



T & D Inspection Service
Serving the Chippewa Valley and beyond
http://www.eauclairehomeinspector.com
Reply With Quote
  #26  
Old 3/13/09, 2:53 PM
Joseph Burkeson, CMI's Avatar
Joseph Burkeson, CMI Joseph Burkeson, CMI is offline
InterNACHI Member
 
Join Date: May 2003
Location: Greater Tampa Bay
Posts: 16,102
Default Re: Clamp amp meters

Quote:
Originally Posted by wthacker View Post
It can be used to check running load amps (RLA) of the outside A/C unit. RLA info is typically on the nameplate data.
That is fairly outside a generalist inspection wouldn't you say? What would be your next step when discovering a high amp reading?



"By three methods we may learn wisdom: First, by reflection, which is noblest; Second, by imitation, which is easiest; and third by experience, which is the bitterest." -Confucius


Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector

Square-One Inspection "Assurance begins here"
Reply With Quote
  #27  
Old 3/13/09, 5:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Clamp amp meters

It's just an indicator Joe. A unit with an excessive load could mean the compressor is failing or nearing the end of its useful life.

Often in these cases, I will stress the importance (in writing) of keeping a home-warranty plan in place, to cover the "likely" event that the unit may fail in the very near future.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #28  
Old 3/13/09, 11:39 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clamp amp meters

It's just an indicator. A unit with an excessive load could mean the compressor is failing or nearing the end of its useful life.

Excellent point. It can be very helpful in warding off that call 'you inspected my AC unit and said it was workig. I moved in and the compressor died.' That reading has helped me and probably saved me grief many times. If the fan is easily accessible, I will also take a reading on that too. It is listed on the labe.
Reply With Quote
Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America)
  #29  
Old 3/16/09, 2:00 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,852
Default Re: Clamp amp meters

Quote:
Originally Posted by jpope View Post
It's just an indicator Joe. A unit with an excessive load could mean the compressor is failing or nearing the end of its useful life.

Often in these cases, I will stress the importance (in writing) of keeping a home-warranty plan in place, to cover the "likely" event that the unit may fail in the very near future.

I had that exact phrase used against me in a Lawsuit. I no longer mention Warranty companies in my report.
Reply With Quote
  #30  
Old 3/16/09, 12:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Clamp amp meters

Can you elaborate on this Brian? What was their argument?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical Inspections 10 4/17/11 2:43 PM
15% Off Moisture Meters jmckenna1 Thermal Imaging, Infrared Cameras & Energy Audits 0 3/11/09 12:19 PM
Ground rod clamp kmalone Electrical Inspections 10 11/12/08 11:42 PM
Does the ground wire need a clamp? jkogel Electrical Inspections 7 10/9/08 6:30 AM
Noise from Meters?? mlong Electrical Inspections 9 2/3/07 9:08 PM


All times are GMT -4. The time now is 12:33 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts