InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Electrical

Notices

Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera.

View Poll Results: Do you use a clamp meter?
Yes 27 54.00%
No 18 36.00%
What is a clamp meter. 0 0%
Thinking about using one. 5 10.00%
Voters: 50. You may not vote on this poll

Reply
 
LinkBack Thread Tools
  #16  
Old 3/11/09, 5:53 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 20,868
Default Re: Clamp amp meters

Quote:
Originally Posted by gkay View Post
Quality, safety, true rms.

This link takes you to flukes' ABC's of multi meter safety. Take the time to learn what makes a quality meter and how to use them safely.

http://support.fluke.com/find-sales/...16_eng_h_w.pdf
If it makes a difference to you I used to test product to UL/CSA 61010-1.

When you say quality, safety and true RMS are you saying one has it and the other doesn't?
Do have a source of more detailed info?
I couldn't verify that from the specs.

BTW-Fluke products are great and I have used them for 40 years.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #17  
Old 3/11/09, 6:15 PM
Sonny C. Shipler Sonny C. Shipler is offline
InterNACHI Member
 
Join Date: May 2007
Location: Beloit, WI
Posts: 75
Default Re: Clamp amp meters

I use a Fieldpiece sc67. Does everything you need. Vac,Vdc,Ohms,amps,temp,continuity,mfd. I think I paid 175.
Reply With Quote
  #18  
Old 3/11/09, 7:35 PM
gkay gkay is offline
New User
 
Join Date: Jan 2009
Location: Olkanagan Valley British Columbiia Canada eh
Posts: 50
Please Note: gkay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clamp amp meters

When you say quality, safety and true RMS are you saying one has it and the other doesn't?
Do have a source of more detailed info?
I couldn't verify that from the specs.

No Michael thats not what I'm saying. I'm sure the P3 you suggested has its applications but in my opinion I didn't think it would suit D.C. Macey's needs. Since he also seems to be new at using electrical meters I thought the price range of $25 dollars coming from a respectable person as yourself might mislead him into buying an inferior meter. The site I refered to was for safety and operation. I am sure there are many less expensive meters that would suit the same purposes.
I'm sure Fluke would be happy to verify any questions regarding specs.
Reply With Quote
  #19  
Old 3/11/09, 8:08 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,440
Default Re: Clamp amp meters

Quote:
Originally Posted by tphillips View Post
Jeff,
I don't use one. Thinking about it though. Could you explain what you use it for on every inspection?
Tom
As William stated, I use it to check the load on condenser units - remember, I'm in CA, so there's rarely a case where I won't run the A/C. So that's the "every inspection" part. I guess the exception would be when the home does not have A/C.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #20  
Old 3/11/09, 8:11 PM
Linas I. Dapkus's Avatar
Linas I. Dapkus Linas I. Dapkus is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Lockport, IL
Posts: 4,548
Default Re: Clamp amp meters

I have a Fluke 332. Cost about $125. Here's more info on clamp meters:
http://us.fluke.com/usen/products/Fluke+330.htm

Check out the info on the bottom left.




Linas Dapkus
Lockport,Il. 60441
#06012294
Reply With Quote
  #21  
Old 3/11/09, 9:08 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,644
Default Re: Clamp amp meters

Quote:
Originally Posted by jpope View Post
As William stated, I use it to check the load on condenser units - remember, I'm in CA, so there's rarely a case where I won't run the A/C. So that's the "every inspection" part. I guess the exception would be when the home does not have A/C.
I have a question for you. When you are testing the load on a condenser what are your parameters for checking. Do you go off the manufacturer's data plate.

I guess since I have never used a clamp meter or tested a condenser with one I was just curious how you went about testing.
Reply With Quote
  #22  
Old 3/12/09, 6:35 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 4,015
Default Re: Clamp amp meters

There is a rating on the nameplate for compressor and fan motor.

Note: The compressor will run at all different loads and the amp draw will change all over the place as well.

There are name plates on all motors and compressors themselves as well.

There are three wires (legs) going to a single phase compressor; common, start & run. The amperage in not going to be the same threw all three legs (so you must select your wires wisely).

Three phase (three wire) compressors should have a balanced load across all three.

None of the amp readings should exceed nameplate.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #23  
Old 3/12/09, 9:28 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 3,195
Default Re: Clamp amp meters

http://www.amprobe.com/cgi-bin/pdc/v...in_e&type=elec
I have the older version but works the same , I have all attachments also comes in handy if you need them
Reply With Quote
  #24  
Old 3/12/09, 9:16 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,440
Default Re: Clamp amp meters

Quote:
Originally Posted by dmacy View Post
I have a question for you. When you are testing the load on a condenser what are your parameters for checking. Do you go off the manufacturer's data plate.

I guess since I have never used a clamp meter or tested a condenser with one I was just curious how you went about testing.
There are no "hard and fast" rules when checking condensers. But generally, you should expect the condenser to be drawing 60% to 75% of its maximum circuit rating. Higher draws may indicate that the unit is working to hard and may be near to failing.

Lower draws may indicate that the system is low on refrigerant, and the compressor is not working hard at all.

In any event, you should never rely solely on the readings of your meter. As with most meters/equipment, you should be looking and/or listening for other indicators that there are problems with the system.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 3/12/09 at 9:20 PM..
Reply With Quote
  #25  
Old 3/12/09, 11:43 PM
Thomas D. Phillips's Avatar
Thomas D. Phillips Thomas D. Phillips is offline
InterNACHI Member
 
Join Date: May 2008
Location: Eau Claire, WI
Posts: 63
Default Re: Clamp amp meters

Thanks for the info guys



T & D Inspection Service
Serving the Chippewa Valley and beyond
http://www.eauclairehomeinspector.com
Reply With Quote
  #26  
Old 3/13/09, 1:53 PM
Joseph T. Burkeson, CMI's Avatar
Joseph T. Burkeson, CMI Joseph T. Burkeson, CMI is offline
InterNACHI Member
 
Join Date: May 2003
Location: Riverview, FL
Posts: 10,120
Default Re: Clamp amp meters

Quote:
Originally Posted by wthacker View Post
It can be used to check running load amps (RLA) of the outside A/C unit. RLA info is typically on the nameplate data.
That is fairly outside a generalist inspection wouldn't you say? What would be your next step when discovering a high amp reading?



"The path of the righteous man is beset on all sides by the iniquities of the selfish and the tyranny of evil men." ~ Pulp Fiction



Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector
Member, American Society of Home Inspectors (ASHI)

Square-One Inspection "Assurance begins here"
Reply With Quote
  #27  
Old 3/13/09, 4:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,440
Default Re: Clamp amp meters

It's just an indicator Joe. A unit with an excessive load could mean the compressor is failing or nearing the end of its useful life.

Often in these cases, I will stress the importance (in writing) of keeping a home-warranty plan in place, to cover the "likely" event that the unit may fail in the very near future.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #28  
Old 3/13/09, 10:39 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,896
Default Re: Clamp amp meters

It's just an indicator. A unit with an excessive load could mean the compressor is failing or nearing the end of its useful life.

Excellent point. It can be very helpful in warding off that call 'you inspected my AC unit and said it was workig. I moved in and the compressor died.' That reading has helped me and probably saved me grief many times. If the fan is easily accessible, I will also take a reading on that too. It is listed on the labe.



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
Find an InterNACHI certified Arizona Home Inspector (and anywhere else in North America)
  #29  
Old 3/16/09, 1:00 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 12,605
Default Re: Clamp amp meters

Quote:
Originally Posted by jpope View Post
It's just an indicator Joe. A unit with an excessive load could mean the compressor is failing or nearing the end of its useful life.

Often in these cases, I will stress the importance (in writing) of keeping a home-warranty plan in place, to cover the "likely" event that the unit may fail in the very near future.

I had that exact phrase used against me in a Lawsuit. I no longer mention Warranty companies in my report.



"Never ever threaten anyone in Camoflage"
Tim Wilson

Reply With Quote
  #30  
Old 3/16/09, 11:29 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,440
Default Re: Clamp amp meters

Can you elaborate on this Brian? What was their argument?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
15% Off Moisture Meters jmckenna1 Thermal Imaging, Infrared Cameras & Energy Audits 0 3/11/09 11:19 AM
Ground rod clamp kmalone Electrical 10 11/12/08 10:42 PM
Does the ground wire need a clamp? jkogel Electrical 7 10/9/08 5:30 AM
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical 5 2/16/07 12:19 PM
Noise from Meters?? mlong Electrical 9 2/3/07 8:08 PM


All times are GMT -4. The time now is 6:11 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts