Does anyone have a good diagram or picture of the recommended/required clearance in front of a residential electrical panel?




BEN GROMICKO
Director of InterNACHI Online Education
President of NACHI.TV - Online Training Videos
President of Mountain Warranty Corporation
ben@nachi.tv
(303)862-2611 ben@mountainwarranty.com

IMPROVE YOUR REPORT

Reply With Quote
  #2  
Old 1/14/08, 11:28 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance in front of electrical panel

Quote:
Originally Posted by bgromicko
Does anyone have a good diagram or picture of the recommended/required clearance in front of a residential electrical panel?
36 inches in front of the panel enclosure mesuring from the enclosure door.




from side to side needs to be 30 inches with the hinged door swing to no less than 90 degrees



Hope this helps

Last edited by Mike Whitt; 1/14/08 at 11:32 PM..
Reply With Quote
  #3  
Old 1/14/08, 11:43 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: Clearance in front of electrical panel

Also try this one
Attached Thumbnails
clearance-front-electrical-panel-electrical-228-.jpg.JPG
Views:	998
Size:	21.6 KB
ID:	17514  
Reply With Quote
  #4  
Old 1/14/08, 11:50 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,096
Default Re: Clearance in front of electrical panel

...and this one:
clearance-front-electrical-panel-panel-clearances.jpg
Reply With Quote
  #5  
Old 1/15/08, 12:11 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance in front of electrical panel

Michael, do you know where that graphic came from? The side to side clearance is not nearly correct. Should be 30" wide (minimum) total.

I use the lower one Mike W posted. It shows all aspects clearly. I'm pretty sure it's a Mike Holt graphic.
Reply With Quote
  #6  
Old 1/15/08, 12:19 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 3,207
Default Re: Clearance in front of electrical panel

Did an inspection today. 600 Amps to this gigantic home.

Main panels did not meet the minimum clearances between.

One of the sub-panels had a 3-wire feed, with no metallic conduit between main and sub, and no 4th conductor. 120 and 240 volt circuits abound. Where's the ground. Neutral bar was isolated, BTW, so we've got THAT going for us

Inspection sticker proudly displayed.

What am I missing here?

Transformer on site. Water all around it. Conduit from transformer to inside of basement has water POURING from it, into 3'x3' distribution cabinet. BIG cables, and large metallic conductor bars. Meter is connected in parallel, and conduited outside.

Really dangerous situation with the water. Weep holes drilled in bottom of this cabinet for "drainage" Unfortunately, it drains directly onto two side-by-side disconnects to two more sub-panels elsewhere in the dwelling. Builder had electrical contractor try and fix problems. Dug trench at one side of xformer, no catch basin. No drain pipe. Caulked inside of conduit where it entered dwelling.

As to the pretty pictures, I do like the graphics, but it may only make us look stupid if we call these things out. Builder stated that house passed electrical inspection, and its not his problem.

Last edited by jfarsetta; 1/15/08 at 12:25 AM..
Reply With Quote
  #7  
Old 1/15/08, 12:29 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance in front of electrical panel

Quote:
Originally Posted by Gromyko
Does anyone have a good diagram or picture of the recommended/required clearance in front of a residential electrical panel?
Ben:

Please do not use any of these images, most of which are copyrighted!

Find a refrigerator box, these dimentions are very much the same as for working spaces about electrical equipment.

The width at the working space is required to be at least 30 inches, and does not have to be centered.

In some cases there are rules that will allow less than the required height of 6' - 6"
Reply With Quote
  #8  
Old 1/15/08, 12:30 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,096
Default Re: Clearance in front of electrical panel

Quote:
Originally Posted by Speedy Petey
Michael, do you know where that graphic came from? The side to side clearance is not nearly correct. Should be 30" wide (minimum) total.
That graphic is from The Illustrated Home by Dearborn Publishing & Carson Dunlop 2003. Doesn't it show 30-36" clearance? I think I know what you are getting at but the other one shows the same thing, right?
Reply With Quote
  #9  
Old 1/15/08, 12:38 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance in front of electrical panel

Quote:
Originally Posted by jfarsetta
Did an inspection today. 600 Amps to this gigantic home.

Main panels did not meet the minimum clearances between.

One of the sub-panels had a 3-wire feed, with no metallic conduit between main and sub, and no 4th conductor. 120 and 240 volt circuits abound. Where's the ground. Neutral bar was isolated, BTW, so we've got THAT going for us

Inspection sticker proudly displayed.

What am I missing here?

Transformer on site. Water all around it. Conduit from transformer to inside of basement has water POURING from it, into 3'x3' distribution cabinet. BIG cables, and large metallic conductor bars. Meter is connected in parallel, and conduited outside.

Really dangerous situation with the water. Weep holes drilled in bottom of this cabinet for "drainage" Unfortunately, it drains directly onto two side-by-side disconnects to two more sub-panels elsewhere in the dwelling. Builder had electrical contractor try and fix problems. Dug trench at one side of xformer, no catch basin. No drain pipe. Caulked inside of conduit where it entered dwelling.

As to the pretty pictures, I do like the graphics, but it may only make us look stupid if we call these things out. Builder stated that house passed electrical inspection, and its not his problem.
I agree, did you see the empty envelope?
Reply With Quote
  #10  
Old 1/15/08, 12:41 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance in front of electrical panel

Quote:
Originally Posted by mboyett
That graphic is from The Illustrated Home by Dearborn Publishing & Carson Dunlop 2003. Doesn't it show 30-36" clearance? I think I know what you are getting at but the other one shows the same thing, right?
That image comes from the NECH and is the correct interpretation related to width. Note that all equipment doors are to be capable of opening to not less tha 90 degrees.
Reply With Quote
  #11  
Old 1/15/08, 12:54 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance in front of electrical panel

Quote:
Originally Posted by mboyett
That graphic is from The Illustrated Home by Dearborn Publishing & Carson Dunlop 2003. Doesn't it show 30-36" clearance? I think I know what you are getting at but the other one shows the same thing, right?
The way I see your's is 30-36" on BOTH sides. It should be 30" minimum side to side total as the other graphic shows. The panel can be anywhere in that 30" space.
Reply With Quote
  #12  
Old 1/15/08, 12:56 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance in front of electrical panel

Quote:
Originally Posted by jtedesco1
Find a refrigerator box, these dimentions are very much the same as for working spaces about electrical equipment.
You guys will just need to make some room in the back of your trucks to carry it around.
Reply With Quote
  #13  
Old 1/15/08, 12:57 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance in front of electrical panel

Quote:
Originally Posted by bgromicko
Does anyone have a good diagram or picture of the recommended/required clearance in front of a residential electrical panel?
Here's an interesting item, move the building in order to provide the necessary working space.



That space there in Boulder near the AC unit is just about right.

Listen to this guy too.
Reply With Quote
  #14  
Old 1/15/08, 2:11 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance in front of electrical panel

Jim Pauley was the first one I heard use the refrigerator box analogy but it does work.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Electrical Safety Information jtedesco1 Electrical 0 2/19/06 2:48 AM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 1:25 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts