Default Clearance of primary to roof slope

I vebally advised my clients to check the survey for possible easement encroachment problems with this (see pictures). The pole was about 3 feet from the house and the transmission line was about six feet above the roof.

My experience tells me there should be an eight foot easement on each side of the pole. Don't know the proper clearance of the lines to the roof but I could have easily grabbed the line from the roof slope.

It doesn't look right. Haven't written the report yet. Any comments?
Attached Thumbnails
clearance-primary-roof-slope-primaryclose.jpg   clearance-primary-roof-slope-primaryclose1.jpg   clearance-primary-roof-slope-primaryclose2.jpg  



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #2  
Old 8/23/06, 7:23 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Clearance of primary to roof slope

John, I wouldn't want them babies laying on my home during a storm....

Something is wrong alright...

What was this a SELLERS inspection?.....
Reply With Quote
  #3  
Old 8/23/06, 7:44 PM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,659
Default Re: Clearance of primary to roof slope

New construction inspection, Houston Texas, Ashton Woods Homes.

I guess we all know clearance of service drops to this particular roof slope is three feet. Primary power rarely comes into play in our field however. There's just a wee bit more voltage involved here.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #4  
Old 8/23/06, 7:50 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance of primary to roof slope

WOW!!
You have got to be joking me that that is new construction!
I was going to say the home looks pretty new, and ask which was there first, the home or the pole. From the sound of it the pole was.

The builder sounds like a buffoon for putting the house so close. I would agree that there MUST be some sort of easment or right of way along the path of those wires. And I'd bet dollars that it is more than 3'.

Like the others have said Michael, that chart doesn't have much relavance in this situation. Infact the NEC has no relavance. This is a POCO or municipality issue.
Reply With Quote
  #5  
Old 8/23/06, 7:56 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Clearance of primary to roof slope

No, I realize that the graphic is not directly applicable but my thought was that if the existing lines violated any of those criteria then that would be a place to start. The higher voltage distribution lines certainly wouldn't have less stringent criteria associated with them. I'll delete the graphic so as to not confuse anyone.
Reply With Quote
  #6  
Old 8/23/06, 8:02 PM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,659
Default Re: Clearance of primary to roof slope

Mike,

I actually made that last post without seeing yours. I was probably typing when you were posting.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #7  
Old 8/23/06, 8:45 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Clearance of primary to roof slope

Now that's just "fub-duck."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 8/24/06, 6:51 AM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,659
Default Re: Clearance of primary to roof slope

No comments from the resident Sparkies? Must be over their heads (excuse the pun).



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #9  
Old 8/24/06, 8:17 AM
Emmanuel J. Scanlan Emmanuel J. Scanlan is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Josephine, TX
Posts: 1,036
Default Re: Clearance of primary to roof slope

John,

Houston local code from www.municode.com:

Quote:
Sec. 10-32. Permit to construct--Required.
It shall be unlawful for any person to build, erect, or construct, or cause to be built, erected or constructed any building, structure or edifice for any use or occupancy whatsoever in, upon, over or across any easement, or any part thereof, granted to the city for sanitary sewer, storm water, water main, or electric line conduit purposes, or a combination of same, or upon, over, or across any privately constructed sanitary sewer, storm sewer, water main, or electric line conduit managed, supervised, or controlled by the city or connected with the sanitary sewer system, storm sewer system, water main system or electric line conduit system of the city when such person has actual or constructive notice of such privately constructed sewers, mains, or conduits, without first procuring a written permit to do so from the utility official.

(Code 1968, § 10-32; Ord. No. 90-635, § 24, 5-23-90)
The only problem is they do not list standard easement distances and this appears to be for buried lines (??). Most I have seen are generally 10 feet or better for any utility. You would need to check with the city on their easement amounts for overhead utilities and supporting poles.



Knowledge is power, but sharing knowledge brings peace!

http://www.psinspection.com

TREC License# 7593

Professional Real Estate Inspections for the counties of Collin, Rockwall, Hunt, Dallas, Tarrant, Kaufman and all surrounding areas. If you want the the best you will find it with PS Inspection & Property Services LLC!
Reply With Quote
  #10  
Old 8/24/06, 10:03 AM
Claude Lawrenson's Avatar
Claude Lawrenson Claude Lawrenson is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Tecumseh-Windsor, ON
Posts: 2,122
Default Re: Clearance of primary to roof slope

How but the issue of EMF? Electro-magnetic forces.



Cheers, Claude Lawrenson NACHI03121515
Inspection Support Services Inc.
"Those who can do. Those who CARE, teach" or
“Teaching is the highest form of understanding.” Aristotle
Reply With Quote
  #11  
Old 8/24/06, 10:06 AM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,659
Default Re: Clearance of primary to roof slope

Quote:
Originally Posted by clawrenson
How but the issue of EMF? Electro-magnetic forces.
I suppose the benefit would be getting free power through induction by installing several coils in the attic space!



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #12  
Old 8/24/06, 1:06 PM
dcameron1 dcameron1 is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Brookfield, MO
Posts: 1
Default Re: Clearance of primary to roof slope

John,

There are codes governing this type of problem. Do you know what the voltage is for the distribution line that is shown in your pictures? The voltage determines which of the codes would apply. I will be online this evening and will have looked it up in the code book, if you could reply, with the line voltage.

I have over 40 years of experience in the electrical distribution field and feel we can work to give an accurate report to your client.

Dale Cameron
Cameron Home Inspections
Brookfield, MO
Reply With Quote
  #13  
Old 8/24/06, 4:37 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Clearance of primary to roof slope

WOW

I hope those are not 12,500 volt???

In Chicago those are in alleys next to buildings. The Squirrels use them for access ways to the neighborhoods.... ZZZZZAAAAAAPPP!!

Where are the ..."Electrical professionals" A.K.A. Sparkies (expression soon to be removed from my vocabulary)....


What did the electrician say when he got jolted by an electrical coil?
"DAM! That Hertz"

Sorry bad joke....
Reply With Quote
  #14  
Old 8/24/06, 5:48 PM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,659
Default Re: Clearance of primary to roof slope

Quote:
Originally Posted by dcameron1
John,

There are codes governing this type of problem. Do you know what the voltage is for the distribution line that is shown in your pictures?
I don't know the volatage. My guess is around 13,000volts. I sent the report to my client this morning and wrote it up like this:

Clearance of primary power distribution pole to structure is about three feet (picture 1). The clearance of the primary power distribution lines appears to be about six feet from the roof slope (picture 2). Inspection of primary power distribution lines is outside of the scope of a standard home inspection but the condition appears to be non-standard and in need of further due diligence by the prospective buyer. The verification of clearances of primary distribution lines is a function of the local power company. I recommend that you consult with the local power utility company to determine if the clearance of the primary power distribution in relation to the structure, conforms to their standards. Another place to obtain verification might be the code department at the local municipality. It is also possible that the structure encroaches upon the utility easement at the right side. I recommend that you check the property survey to determine the location of the utility easements and to determine whether or not the structure encroaches upon them.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #15  
Old 8/24/06, 5:50 PM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,659
Default Re: Clearance of primary to roof slope

Of course the builder told them it was checked and is okay. I told my client to have them put it in writing.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 8:10 AM
Ice Gaurd membrane dmacy Exterior Inspections 36 6/14/07 12:21 AM
Roof Repair? Maybe NO jhagarty Exterior Inspections 9 2/15/07 1:19 AM
Service Drop Clearance Over Roof mlong Electrical Inspections 6 12/19/06 7:39 AM


All times are GMT -4. The time now is 2:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts