Default Clearance requirement for raceway/trough

Is there a clearance requirement the above?
If so, what is it?
Check out the image where it's below the panels.
Attached Thumbnails
clearance-requirement-raceway-trough-100_5746-small-.jpg.JPG
Views:	85
Size:	32.1 KB
ID:	37112  
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/23/10, 9:00 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance requirement for raceway/trough

As a minimum what you have is a buried junction box you do not have proper access to.
Reply With Quote
  #3  
Old 5/23/10, 8:04 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance requirement for raceway/trough

Quote:
Originally Posted by Jim Port View Post
As a minimum what you have is a buried junction box you do not have proper access to.
Called a "splitter box" in my area.
Reply With Quote
  #4  
Old 5/23/10, 8:07 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance requirement for raceway/trough

The wall also encroaches on the required working space in front of the electrical equipment. This is from the NECH:

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Texas E&O Requirement Position Statement mboyett Texas/TPREIA Inspectors 40 3/21/10 9:45 PM
Service Drop & SEC Clearance Requirements pbennett1 Electrical Inspections 5 4/20/09 6:48 PM
Walking surface and wall clearance dbucknavich Exterior Inspections 9 5/27/08 6:07 AM
Clearance Testing tfarmer Ancillary Inspection Services & Additional Topics 15 2/26/08 5:41 PM
Range Clearance dsmith6 Interior Inspections 18 1/7/07 9:55 PM


All times are GMT -4. The time now is 5:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts