This is a retrofit and the U/L listed terminal strip is extending the short neutrals. It is better than 12 wirenuts IMHO but it is a labelling violation since SqD does not say this is OK in their panel. The real question is if absence of a mention on the label is really prohibition.
|
|
#2
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Well look at that. I don't know what to think.
I am not even sure if it is a violation. I would think it is only a violation if it says you cannot install such a device. Somthing like "Use only listed Square D parts in this panel". Good picture, post and question Greg. |
|
#3
|
|||
|
|||
|
It is wrong
The current rating of the strip is the question. -- This strip has no rating - if the person cleaning up this panel had used a strip from his local electrical supplier or even home depot I would have been happier Me thinks I have seen this strip at Radio Shack rlb |
|
#4
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I have seen these strips very often in control panels and boards. The MUST have a certain rating. Hell, they are the exact same strips, only smaller, that hot tubs and spas use for thier line-in terminations. These are typically 60A circuits and 48A loads. What say you about that? |
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Google and 30 seconds = http://www.ebyelectro.com/europa_blocks/toc_eu.asp
|
|
#6
|
||||
|
||||
|
The installer spent more time on the terminal strip than it would have taken to twist on several caps onto these short neutrals.
|
|
#7
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Actually this was probably as fast as doing the wirenuts and it is a lot cleaner install to sort out later.
The only real trick is to find the right screwdriver for those strips. I ended up grinding my own so that it was a good fit. |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Cutler Hammer makes a panel that purposely has a splicing bar like that at the top.
I don't seen any issues with that install. That bar very likely has a UR (rated component) listing, and Square D does not prohibit this install. Heck, it's very normal and expected to have similar power distribution blocks in larger junction boxes and gutters in modern installs. I think it's a neat job. |
|
#9
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Good eye Petey, these are series 1000 40a strips.
BTW the guys over at IAEI and ECN said this was legal too. |
|
#10
|
|||
|
|||
|
Ok all you sparkies I have learned something today
I am not a code expert and gut feeling was wrong I do have a question though -- Does the below apply?? NEC 110.14 or 300.15 "Splices shall be made with an approved splice cap or "wire Nut"" This says to me that a "bar" would have to be used because it would not be a splice I know that my notes are not up to date and that I was wrong on the current rating thing but are my notes wrong on the NEC or am I reading it wrong Glad that I don't have to be a code person Help rlb |
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
110.14 Electrical Connections. Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use. Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment. FPN: Many terminations and equipment are marked with a tightening torque. 300.15 is more about the requirement for a box and similar associated fittings. If I saw an installation like this one, my only concern would be that the strip was rated for both the voltage of the conductors and the amperage that will be flowing through them. I am famalier with this particular barrier strip, and can say it's a sweet install. I may actually start doing this myself now. |
|
#12
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Just noticed that there appears to be circuit conductors exiting the top of the enclosure in ENT that don't appear to have a grounding conductor associated with them.
|
|
#13
|
|||
|
|||
|
Marc
I do not have a copy of 110.14 but a google search has the exact quote that I have in my notes that I took at a telecom training seminar for Quest Communications about 6 years ago Looks like I should get a real NEC book if I am going to get into things like this Or better yet use the NACH BB -- better than any code book any day because it covers all trades Am I still wrong?? rlb |
|
#14
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#15
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marc The ENT terminated in a plastic box that totally enclosed the device. There was nothing to bond.
Richard, this is what you are talking about 110.14(B) Splices. Conductors shall be spliced or joined with splicing devices identified for the use or by brazing, welding, or soldering with a fusible metal or alloy. Soldered splices shall first be spliced or joined so as to be mechanically and electrically secure without solder and then be soldered. All splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an insulating device identified for the purpose. This strip is an insulating device identified for the purpose. |
![]() |