I had a client call me and complain today. I did an inspection on her home 2 months ago. She said she plugged her radio and coffee maker into a receptacle outlet in the kitchen. The new radio died (fried) and the coffee maker steamed and smelt burnt. There was no GFCI in the breaker panel or receptacles for the kitchen. I told her to call an electrician. She isnt very happy. Any suggestions?
Reply With Quote
  #2  
Old 9/15/08, 12:51 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Client complaint

Sounds like an open neutral that an electrician would need to track down and fix. I'm assuming this wasn't the first time she used the receptacles.

Jeff
Reply With Quote
  #3  
Old 9/15/08, 2:57 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Client complaint

Did you schedule a visit to check it out while sparky is there?

www.mauihomeinspections.com
Reply With Quote
  #4  
Old 9/15/08, 4:32 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Client complaint

I fail to see how this is remotely your problem two months down the road.
Tell her to call an electrician.
Reply With Quote
  #5  
Old 9/15/08, 4:49 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Client complaint

I guess she's mad at you because you don't use a crystal ball when you inspect? She needs to go pound sand.
Reply With Quote
  #6  
Old 9/15/08, 4:52 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Client complaint

Senice you are from BC area.,,

I have a hunch { rough idea } the kitchen have MWBC { multiwire branch circuit } and somehow the netural went bad and cause the voltage get unbalanced.

That person need to get ahold of electrician to trobleshooting that one.

Merci,Marc
Reply With Quote
  #7  
Old 9/15/08, 7:04 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Client complaint

Quote:
Originally Posted by Speedy Petey View Post
I fail to see how this is remotely your problem two months down the road.
Tell her to call an electrician.
IMO, It doesn't hurt to offer some free advice even 2 years after the inspection, it's good PR. She does need an electrician. Talk is cheap, though.
Assuming it's a typical split duplex outlet, the upper and lower receptacles would be on separate circuits, but they may be sharing a neutral, right?

Jo0hn Kogel
www.allsafehome.ca
Reply With Quote
  #8  
Old 9/15/08, 7:38 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Client complaint

Quote:
Originally Posted by mnicholet View Post
I had a client call me and complain today. I did an inspection on her home 2 months ago. She said she plugged her radio and coffee maker into a receptacle outlet in the kitchen. The new radio died (fried) and the coffee maker steamed and smelt burnt. There was no GFCI in the breaker panel or receptacles for the kitchen. I told her to call an electrician. She isnt very happy. Any suggestions?
I had a radio like that once.

Lexapro might make her Happy, you might suggest that.
Reply With Quote
  #9  
Old 9/15/08, 7:48 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Client complaint

Quote:
Originally Posted by bkelly2 View Post
Lexapro might make her Happy, you might suggest that.
Maybe some of this?:

Reply With Quote
  #10  
Old 9/15/08, 8:50 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Client complaint

Quote:
Originally Posted by jkogel View Post
IMO, It doesn't hurt to offer some free advice even 2 years after the inspection, it's good PR. She does need an electrician. Talk is cheap, though.
Oh I agree. I guess I took it that she was mad at Mark for not catching it before it happened.
I am all for good PR, but ultimately this is not Mark's fault.
Reply With Quote
  #11  
Old 9/15/08, 9:30 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Client complaint

Fair enough. Even if she'd never used that outlet, Mark tested it, top and bottom, and it was ok, right?

BTW, for BC inspectors, the new code allows for 20A kitchen outlets which are not split, and you can now have two, but only two adjacent outlets on the same #12 conductor.
The 15A split duplex circuits are still allowed as well, and i don't know which uses less copp$$er. Seeing mostly 20A being installed.

John Kogel
www.allsafehome.ca
Reply With Quote
  #12  
Old 9/15/08, 10:24 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Client complaint

I talked to an electrician today and he said it was likely an open neutral as well, he will be going out to the home. I pull a face plate(s) off kitchen receptacles to ensure top and bottom are wired on seperate circuits. There was no open circuit on any of the receptacles I tested on the day of the inspection. So how does an open neutral happen? A white conductor splice/connection comes apart all by itself? Was this condition most likely present on the day of the inspection? The only electrical mods she has made since the inspection is, her hubby added a GFCI receptacle in the bathroom and installed a new dishwasher.
Reply With Quote
  #13  
Old 9/15/08, 10:30 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Client complaint

Quote:
Originally Posted by mnicholet View Post
her hubby added a GFCI receptacle in the bathroom and installed a new dishwasher.
You may have found the problem, and have also been cleared from any responsibility.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #14  
Old 9/15/08, 11:18 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Client complaint

Actually... the keyword is 'hubby'.

Jeff
Reply With Quote
  #15  
Old 9/16/08, 6:14 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Client complaint

Quote:
Originally Posted by mnicholet View Post
The only electrical mods she has made since the inspection is, her hubby added a GFCI receptacle in the bathroom and installed a new dishwasher.
Sounds like this may be the source of the problem!! Did Hubby, most likely NOT an electrician, try to steal a circuit for the dishwasher from a split receptacle set (2 allowed per 14-3 circuit) and screw up the neutral or do a poor Marr/Marette connection for the neutral that eventually let go?

Story:
Did a 12 year old semi-detached inspection a few years ago. The electrical panel was close to perfect with all wires arranged in parallel, plainly labbeled, etc.......you know, the one you find every few years that you want to take a picture of as an example of really good work!

So I figured this place should be a breeze electrically until I started testing the kitchen counter receptacles. There were 3 but #'s 1 & 3 were not split....just standard 120 V recepts. Stood back and looked......and then it hit me. These were starter semis and did not have dishwashers as part of the original package. This unit had a dishwasher installed in front of #3 recept. Took the cover off #3 recept and found that someone (the electrician that lived in the other semi !!!!!) had stolen a circuit from the split recepts to feed the dishwasher. This saved 4-6 hours of time to run a new dedicated circuit from the panel. Since #1 & 3 recepts were on the same 14-3 circuit, #1 was also lost as a split receptacle.

So....... a licensed electrician took something that was legal/required and altered it to not meet codes in order to save some time!!! This was the last inspection of that week done late on Friday.......I get a call from the electrician early Sunday evening!! He firstly asks if I was a licensed electrician to which I said "No". He begins to berate me for calling something like this "not being an electrician", to which I stopped him and replied "Buddy, do you know that I have been twice asked to join the local Electrical Inspectors Association , once by the Chief Electrical Inspector and once by a Field Inspector that I had the chance to do a presentation with to the local Realtors Association". (many years ago)

That stopped him in his tracks and then I quoted the code on these items from memory......to which he asked "Do you have your code book open in front of you?" "No", I said.......... Silence for a few seconds until he said "Well, since you're going to report me, I might as well give you my license # now!" I told him I would not report him but would expect that item to be corrected (for free) by the closing date!!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Someone invite the other Canadian Associations to this NACHI event on Wed please. gromicko Canadian Inspectors 28 9/13/06 1:28 PM