  #1  
Old 1/31/08, 12:03 AM
thance thance is offline
New User
 
Join Date: Sep 2007
Location: Eastsound, WA
Posts: 92
Please Note: thance is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Closet Incandescent Clearance ?

I know that surface incandescent bulbs should be fully enclosed and kept a minimum of 12" from storage, but how far do they need to be from the wall? Here, this one is 3.5" which seems way too close.
Attached Thumbnails
closet-incandescent-clearance-kalal-house-pictures-119.jpg  
Reply With Quote
  #2  
Old 1/31/08, 1:50 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Closet Incandescent Clearance ?

Closet: no open incadescent bulbs allowed
Reply With Quote
  #3  
Old 1/31/08, 2:26 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Closet Incandescent Clearance ?

In new construction.
Reply With Quote
  #4  
Old 1/31/08, 2:59 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Closet Incandescent Clearance ?

I old construction reccomend flourescent bulb if cleareance is 6"
Reply With Quote
  #5  
Old 1/31/08, 5:28 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Closet Incandescent Clearance ?

Porcelain or plastic lampholders of the key less or pull chain types are not, and never were allowed in a clothes closet, because they are not considered as a fixture. See 410.8 in the NEC.
Reply With Quote
  #6  
Old 1/31/08, 6:19 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Closet Incandescent Clearance ?

Joe is 100 percent correct......The use of a sqigly flour (CFL) is not allowed in a keyless in your example to circumvent the requirements of 410.8

Suggest they replace it with a REAL fixture with an enclosed bulb.....is your best suggestion to them.

Ok....Im off to work...Gotta FAIL people...lol



Paul W. Abernathy
Reply With Quote
  #7  
Old 1/31/08, 7:55 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Closet Incandescent Clearance ?

Pay close attention to what Joe said in the part that I have highlited in Bold.

Quote:
Originally Posted by jtedesco1
Porcelain or plastic lampholders of the key less or pull chain types are not, and never were allowed in a clothes closet, because they are not considered as a fixture. See 410.8 in the NEC.
Reply With Quote
  #8  
Old 1/31/08, 8:26 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Closet Incandescent Clearance ?

Yeah, but thousands upon thousands were installed in closets by licensed electricians through the years, were approved by the AHJ, and remain in service.

You guys kill me
Reply With Quote
  #9  
Old 1/31/08, 8:52 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Closet Incandescent Clearance ?

Quote:
Originally Posted by jfarsetta
Yeah, but thousands upon thousands were installed in closets by licensed electricians through the years, were approved by the AHJ, and remain in service.
Quote:
Originally Posted by jfarsetta

You guys kill me
Joe I would say that that is a very broad assumption as there are areas in out nation today that still don’t have licensing requirements or inspections.

Some areas of our nation have had licensing requirements and inspections departments for less than 20 years and even less time than that.

To simply assume that because it was installed that it was done by a licensed electrician and also inspected by a code official would simply be a wrong assumption.

I have seen lamp holders installed in closets by Mr. Homeowner or some handyman that he hired to replace the light that was installed simply because the ballast burn out. A keyless is $1.29 ballast is $25 so the choice is easy for a penny pincher.

So to say a keyless is there so it must have been installed by a licensed electrician and inspected by a code official would be a very broad statement.

With the same breath I will say that our system is not flawless. There has been many an innocent man put to death by our legal system and many have spent years incarcerated to later be proven innocent.
I am sure that there are many keyless fixtures that were installed by licensed electricians and passed by the code officials. This is one of the reasons that we depend on the Home Inspector, is it not?
Reply With Quote
  #10  
Old 1/31/08, 9:01 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Closet Incandescent Clearance ?

Cut the crap, Mike.

NY has been doing inspections under the Board of Fire Underwriters forever. Up until, I believe 2002, all I say were porcelain fixtures in closets in new construction.

Now, I know that Harry the Homeowner does dumb things all the time, but that is not what I am talking about. I always recommend a covered fixture, for safety sake.

Here's the type of stuff we face...

Just got off the phone with an electrical contractor. Brand new construction. Electrical panel ramset directly to poured concrete foundation wall. Cables are not secured above panel. Two circuits in panel with ground and neutral commoned under single lugs. I call out these conditions, and only ask for ground/neutral conditins to be corrected. get a call from contractor, and asks me for an NEC reference before he'll do anything.
Reply With Quote
  #11  
Old 1/31/08, 9:27 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Closet Incandescent Clearance ?

Quote:
Originally Posted by jfarsetta

Here's the type of stuff we face...

Just got off the phone with an electrical contractor. Brand new construction. Electrical panel ramset directly to poured concrete foundation wall. Cables are not secured above panel. Two circuits in panel with ground and neutral commoned under single lugs. I call out these conditions, and only ask for ground/neutral conditins to be corrected. get a call from contractor, and asks me for an NEC reference before he'll do anything.
Now come on.....How much time and money does the Electrician really think he/she is saving by securing the panel to a concrete foundation. It's not that hard and it doesn't take that long to secure a lousy piece of plywood (or OSB) to the foundation and then secure the electrical panel to this backing with short wood screws and now they've got a surface to staple the branch wires to within 12 inches of the panel.
Name:  headbang.gif
Views: 180
Size:  983 BytesWORK SMARTER, NOT HARDER
Reply With Quote
  #12  
Old 1/31/08, 11:23 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Closet Incandescent Clearance ?

Quote:
Originally Posted by dvalley
Now come on.....How much time and money does the Electrician really think he/she is saving by securing the panel to a concrete foundation. It's not that hard and it doesn't take that long to secure a lousy piece of plywood (or OSB) to the foundation and then secure the electrical panel to this backing with short wood screws and now they've got a surface to staple the branch wires to within 12 inches of the panel.
Attachment 18163WORK SMARTER, NOT HARDER
In the building codes in Article 319 we will find that any lumber such as the OSB referred to above would be required to be pressure treated so OSB would not work.
Reply With Quote
  #13  
Old 1/31/08, 11:50 AM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Closet Incandescent Clearance ?

Here is a couple of examples from this week of stupid installation practices by someone other than the homeowner. This is a home with an EIFS exterior. Someone in one of the trades screw mounted the panel and the conduit clamps thru the EIFS. There were also numerous exterior light fixtures simply mounted. It was a comedy of errors from the EIFS installation right down to the last piece of trim. And yes, those are drywall screws holding the clip on and self tapping sheet metal screws on the panel mounting flange.

Last edited by dedwards; 2/17/08 at 2:56 PM..
Reply With Quote
  #14  
Old 1/31/08, 12:18 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Closet Incandescent Clearance ?

Quote:
Originally Posted by jfarsetta
Yeah, but thousands upon thousands were installed in closets by licensed electricians through the years, were approved by the AHJ, and remain in service.

You guys kill me
Joe:

I agree and did not find out that the subject of our discussion was an issue until 1981 after I started with NFPA as a Staff Liaison, the UL person on the Code Panel was the one who mentioned the differences. I too have approved the open bulb in closets, but we have to agree that it is a fire hazard.
Reply With Quote
  #15  
Old 1/31/08, 6:04 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Closet Incandescent Clearance ?

Joe T. while we are on the same subject here do you recall when the NEC did enforce this code [ 410.8 ] what year they start doing that ??

The reason why i try to back track how far it did start the enforceing that part.

the oldest code book i have is 1993 but it printed in French for me the later ones are in engish.

Thanks

Merci, Marc
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
service drop clearance belliott Electrical Inspections 28 6/1/07 1:23 PM
Newbie here with a slab "standards" question Robert Young, #3 Structural Inspections 17 4/10/07 10:48 AM
Range Clearance dsmith6 Interior Inspections 18 1/7/07 9:55 PM
Service panel clearance wwarner Electrical Inspections 13 8/12/06 12:07 PM
Siding to Ground Clearance tneumann Exterior Inspections 14 2/8/06 11:48 PM


All times are GMT -4. The time now is 5:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts