Default Closet Light

I saw this light in a kitchen pantry today. It doesn't have a globe. This is new construction. I thought lights in a closet had to have a globe or some sort of cover over them in new homes. Can someone confirm if there is an exception? The light isn't near any shelving. Thanks a bunch.
Attached Thumbnails
closet-light-img_1656.jpg  
Reply With Quote
  #2  
Old 5/27/08, 6:16 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Closet Light

Skip,

Article 410 Luminaries (Lighting Fixture), Lampholders, and Lamps

Article 410.8 (B) Luminaries (Fixture) Types Permitted. Listed. The following types of light fixtures shall be permitted to be installed in a closet. Closets (Clothes and storage) eight ( square feet (0.74 m²) or larger one of the following type of light fixtures shall be installed:

1. A recessed incandescent fixture with a completely enclosed lamp operated by a wall switch.

2. A surface mounted or recessed fluorescent fixture with a completely enclosed tube(s) operated by a wall switch.

410.8 (C) Luminaries (Fixture) Types Not Permitted. The following fixtures are not permitted:

1. Surface mounted incandescent fixture with enclosed, partially enclosed or open bulbs.
2. Pendant Style
3. Lampholders

Exception:
Walk-in closets of larger area where no storage exists within forty (40) inches (1016 mm) in any direction of a vertical line extending from the floor to ceiling, away from the wall, incandescent fixtures with totally enclosed bulb(s) may be used. Said light fixtures shall be operated by a wall switch.
Reply With Quote
  #3  
Old 5/27/08, 7:10 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Closet Light

Pantry isn't a closet. I see them all the time in pantrys most of which is new construction.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #4  
Old 5/28/08, 1:51 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Closet Light

Quote:
Originally Posted by dvalley
Skip,

Article 410 Luminaries (Lighting Fixture), Lampholders, and Lamps

Article 410.8 (B) Luminaries (Fixture) Types Permitted. Listed. The following types of light fixtures shall be permitted to be installed in a closet. Closets (Clothes and storage) eight ( square feet (0.74 m²) or larger one of the following type of light fixtures shall be installed:

1. A recessed incandescent fixture with a completely enclosed lamp operated by a wall switch.

2. A surface mounted or recessed fluorescent fixture with a completely enclosed tube(s) operated by a wall switch.

410.8 (C) Luminaries (Fixture) Types Not Permitted. The following fixtures are not permitted:

1. Surface mounted incandescent fixture with enclosed, partially enclosed or open bulbs.
2. Pendant Style
3. Lampholders

Exception:
Walk-in closets of larger area where no storage exists within forty (40) inches (1016 mm) in any direction of a vertical line extending from the floor to ceiling, away from the wall, incandescent fixtures with totally enclosed bulb(s) may be used. Said light fixtures shall be operated by a wall switch.
Where did this information come from?
Reply With Quote
  #5  
Old 5/28/08, 2:25 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Closet Light

Unless things have changed drastically, what David posted is not what I see in new construction here in NY. Enclosed incandescant bulbs as a part of a surface mounted fixture are used all the time. The 40" rule aint adhered to. I never see florescent or recessed in closets
Reply With Quote
  #6  
Old 5/28/08, 6:06 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Closet Light

I don't have a copy of the NEC, but is this all interpetation of the Code or what?
This seems to read different than what David posted.


Closets
1. Closet light fixtures are listed for the use and are installed per NEC 410 (
a. Surface mounted incandescent fixtures installed on the wall above the door or on the ceiling have a minimum clearance of 12" between the fixture and the nearest point of storage. Fluorescent fixtures have a 6" minimum clearance.
b. Recessed fluorescent fixtures or recessed incandescent fixtures with a completely enclosed lamp installed in a wall or the ceiling have a minimum 6" clearance between the fixture and the nearest point of storage space.


Marcel
Reply With Quote
  #7  
Old 5/28/08, 6:48 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Closet Light

The National Electrical Code-2002

Clothes Closet. A non-habitable room or space intended primarily for storage of garments and apparel.

Last edited by jtedesco1; 6/12/08 at 4:39 PM..
Reply With Quote
  #8  
Old 5/28/08, 7:33 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Closet Light

Thanks Joe.

I went out and talked to my electrician and looked at the NEC 2005 in 410.8 D. And it appears to read as such;



Closets
1. Closet light fixtures are listed for the use and are installed per NEC 410.8D (a. Surface mounted incandescent fixtures installed on the wall above the door or on the ceiling have a minimum clearance of 12" between the fixture and the nearest point of storage.


Is this correct?

Thanks

Marcel
Reply With Quote
  #9  
Old 5/28/08, 7:41 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Closet Light

Quote:
Originally Posted by mcyr
Thanks Joe.

I went out and talked to my electrician and looked at the NEC 2005 in 410.8 D. And it appears to read as such;




Closets
1. Closet light fixtures are listed for the use and are installed per NEC 410.8D (a. Surface mounted incandescent fixtures installed on the wall above the door or on the ceiling have a minimum clearance of 12" between the fixture and the nearest point of storage.


Is this correct?

Thanks

Marcel
Exact wording from 2005 NEC:

"(D) Location Luminaires (fixtures) in clothes closets shall be permitted to be installed as follows:

(1) Surface-mounted incandescent luminaires (fixtures) installed on the wall above the door or on the ceiling, provided there is a minimum clearance of 300 mm (12 in.) between the luminaire (fixture) and the nearest point of a storage space

(2) Surface-mounted fluorescent luminaires (fixtures) installed on the wall above the door or on the ceiling, provided there is a minimum clearance of 150 mm (6 in.) between the luminaire (fixture) and the nearest point of a storage space

(3) Recessed incandescent luminaires (fixtures) with a completely enclosed lamp installed in the wall or the ceiling, provided there is a minimum clearance of 150 mm (6 in.) between the luminaire (fixture) and the nearest point of a storage space"

Just remember that lampholders, like the one posted in the first message, are not permitted in clothes closets.
Reply With Quote
  #10  
Old 5/28/08, 8:08 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Closet Light

That is what I read.

Thanks Joe.

Marcel
Reply With Quote
  #11  
Old 5/28/08, 9:49 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Closet Light

Quote:
Originally Posted by Skip Erwin
I saw this light in a kitchen pantry today. It doesn't have a globe. This is new construction. I thought lights in a closet had to have a globe or some sort of cover over them in new homes. Can someone confirm if there is an exception? The light isn't near any shelving. Thanks a bunch.
Skip, the idea is to prevent people from stacking boxes or other materials that can start a fire in contact with the bulb.

The codes have been referenced above, but since it's not a code inspection (unless you do code inspections) then just think about the safety of the situation. Make your call from there.

Also what would be the difference in safety between "new homes" (my red above) and older homes?
Reply With Quote
  #12  
Old 5/28/08, 10:56 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Closet Light

Exactly Rick, which is why I simply warn of the risks,and suggest.(on this subject matter).
Reply With Quote
  #13  
Old 5/28/08, 9:06 PM
mjohnson6's Avatar
mjohnson6 mjohnson6 is offline
Active Poster
 
Join Date: Aug 2007
Location: NH
Posts: 175
Send a message via Yahoo to mjohnson6
Please Note: mjohnson6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Closet Light

For those that are intrested I would be happy assist you in your purchase of the nec. http://search.barnesandnoble.com/Nat...7657903/?itm=7
Reply With Quote
  #14  
Old 6/4/08, 8:56 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Closet Light

Regardless of the "Electrical" placement concerns in regards to a Clothes Closet....depending on the location the HI needs to make their client aware of the potential fire danger from the placement. The example is not a clothes closet obviously.

However lets all be aware of another provision of the NEC that comes into play in other areas as well.

410.5 Luminaires (Fixtures) Near Combustible Material.

Luminaires (fixtures) shall be constructed, installed, or
equipped with shades or guards so that combustible material
is not subjected to temperatures in excess of 90°C
(194°F).



Paul W. Abernathy
Reply With Quote
  #15  
Old 6/5/08, 3:34 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Closet Light

Codes aside, I always call out bare bulb fixtures as a safety hazard. Certainly, there are any number of flammable materials in a pantry. In addition, even in rooms that are not specifically defined as closets (laundry rooms, for example) it is very common to see combustible items hanging on make-shift hooks or rods (hopefully not from the lamp itself) !!



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
CFL Bulb Breaks: Leave For 15 min. jmckenna1 Miscellaneous Discussion for Inspectors 44 7/19/08 5:34 PM
Trouble Shooting the Simple Light Bulb mcyr Electrical Inspections 20 1/6/08 3:47 AM
End of the light bulb as we know it!! mcyr General Inspection Discussion 3 12/19/07 3:42 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 7:22 PM
How many forum members to change a light bulb? kshepard Miscellaneous Discussion for Inspectors 9 8/2/06 9:56 AM


All times are GMT -4. The time now is 5:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts