How can I find out if this is code or not for the state of TN? ELECTRICAL: PANEL PROB: THE GROUND AND NEUTRAL WIRES HAVE BEEN SEPARATED, HOWEVER THERE ARE NOW DOUBLE LUGGED GROUND WIRES AT THE BUS BAR INSIDE THE MAIN PANEL. |
| Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Contact your local code official.
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Is this from an inspection report? You would need a few photo's or more information to provide an answer.
|
|
#4
|
||||
|
||||
|
Normally that is not an issue.
|
|
#5
|
||||
|
||||
|
That depends on other factors, Bob. Also, she want's to know about "code", not what is necessarily "safe".
Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#6
|
||||
|
||||
|
Then tell her it is a minor issue at best
|
|
#7
|
||||
|
||||
|
Nope, not me. Not without more information and a couple of quality pic's.
Quote:
But... the first thing that jumps into mind (by the OP's question) is if this is actually the service panel, or a sub-panel, and are they properly bonded? Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#8
|
||||
|
||||
|
When has a double tap GROUND wire ever been an issue?
If they are the same size/ type wire, not an issue. Where do you live? There are many places in TN without code enforcement. If the house was inspected by the AHJ, you must talk to the inspector that did the inspection. "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#9
|
|||
|
|||
|
Ok....when I read the original statement I have to examine what they are actually asking. So with that said let me re-post what the question was that the original poster was asking.
Quote:
2.) The grounded conductors ( neutrals in this case ) should be directly connected to the grounding conductors ( ground/bar conductors in this case) at the main service equipment. Separation of these at the source is a problem that has to be addressed as it brings into more questions for me... Q1: Was their a main bonding jumper at this service equipment and did it provide for the connection of the grounded conductor, grounding conductors and equipment case to all come together? If yes then the separation is fine as long as something is bonding them all together.Thus their only separated in bus design but not in physical design. Q2: Panel manufacturers will allow multiple ( check the listed for just how many ) equipment grounding conductors (ground in your question) to be under a single lug as long as it meets the listing of the termination. This is found on the manufacturers equipment label but we can use some common sense here....If there are (2) 14 AWG conductors under a single lug for the EGC's then no harm..no foul. If you see (1) 12 AWG and (1) 14 AWG under the same lug...mention it as it would be impossible to properly torque a 12 AWG properly and still have it torque a 14 AWG properly. Remember that the National Electrical Code is a safety standard no matter how you wish to slice it. The integrity of the available fault current path is reduced when proper terminations and torquing is not maintained. As for code in TN....simply follow the logic of the basic principles of the NEC® and you will be supported. Paul W. Abernathy |
|
#10
|
||||
|
||||
|
Agreed. The NEC does not prohibit "double-tapping" of the grounding conductors.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#11
|
||||
|
||||
|
The information is usually Listed inside the Pane.
|
![]() |