Question What is code and what is not?

How can I find out if this is code or not for the state of TN?

ELECTRICAL: PANEL
PROB: THE GROUND AND NEUTRAL WIRES HAVE BEEN SEPARATED, HOWEVER THERE ARE NOW DOUBLE LUGGED GROUND WIRES AT THE BUS BAR INSIDE THE MAIN PANEL.

Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/10/11, 8:53 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: What is code and what is not?

Quote:
Originally Posted by Tammy D. Smith View Post
How can I find out if this is code or not for the state of TN?


ELECTRICAL: PANEL
PROB: THE GROUND AND NEUTRAL WIRES HAVE BEEN SEPARATED, HOWEVER THERE ARE NOW DOUBLE LUGGED GROUND WIRES AT THE BUS BAR INSIDE THE MAIN PANEL.

Contact your local code official.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 6/10/11, 9:04 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is code and what is not?

Quote:
Originally Posted by Tammy D. Smith View Post
How can I find out if this is code or not for the state of TN?

ELECTRICAL: PANEL
PROB: THE GROUND AND NEUTRAL WIRES HAVE BEEN SEPARATED, HOWEVER THERE ARE NOW DOUBLE LUGGED GROUND WIRES AT THE BUS BAR INSIDE THE MAIN PANEL.

Is this from an inspection report? You would need a few photo's or more information to provide an answer.
Reply With Quote
  #4  
Old 6/10/11, 9:06 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: What is code and what is not?

Quote:
Originally Posted by Tammy D. Smith View Post
How can I find out if this is code or not for the state of TN?

ELECTRICAL: PANEL
PROB: THE GROUND AND NEUTRAL WIRES HAVE BEEN SEPARATED, HOWEVER THERE ARE NOW DOUBLE LUGGED GROUND WIRES AT THE BUS BAR INSIDE THE MAIN PANEL.

Normally that is not an issue.
Reply With Quote
  #5  
Old 6/10/11, 11:01 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: What is code and what is not?

Quote:
Originally Posted by belliott View Post
Normally that is not an issue.
That depends on other factors, Bob. Also, she want's to know about "code", not what is necessarily "safe".
Reply With Quote
  #6  
Old 6/10/11, 11:47 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: What is code and what is not?

Then tell her it is a minor issue at best
Reply With Quote
  #7  
Old 6/11/11, 8:00 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: What is code and what is not?

Quote:
Originally Posted by belliott View Post
Then tell her it is a minor issue at best
Nope, not me. Not without more information and a couple of quality pic's.

Quote:
ELECTRICAL: PANEL
PROB: THE GROUND AND NEUTRAL WIRES HAVE BEEN SEPARATED, HOWEVER THERE ARE NOW DOUBLE LUGGED GROUND WIRES AT THE BUS BAR INSIDE THE MAIN PANEL.
Generally speaking, in and of itself, I have no problem with the above. In fact, I prefer it. It shows that the sparky takes pride in his wormanship. It is always nice inspecting these panels. Sure, it would be nice if the grounds weren't doubled, but that normally no biggie, if done right.

But... the first thing that jumps into mind (by the OP's question) is if this is actually the service panel, or a sub-panel, and are they properly bonded?
Reply With Quote
  #8  
Old 6/11/11, 9:05 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: What is code and what is not?

When has a double tap GROUND wire ever been an issue?

If they are the same size/ type wire, not an issue.

Where do you live? There are many places in TN without code enforcement.
If the house was inspected by the AHJ, you must talk to the inspector that did the inspection.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #9  
Old 6/11/11, 11:27 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: What is code and what is not?

Ok....when I read the original statement I have to examine what they are actually asking. So with that said let me re-post what the question was that the original poster was asking.

Quote:
How can I find out if this is code or not for the state of TN?

ELECTRICAL: PANEL
PROB: THE GROUND AND NEUTRAL WIRES HAVE BEEN SEPARATED, HOWEVER THERE ARE NOW DOUBLE LUGGED GROUND WIRES AT THE BUS BAR INSIDE THE MAIN PANEL.
1.) I will assume that this ( assuming is not a good thing ) is a main service panel enclosure since nothing was said regarding it being a remote distribution panel enclosure.
2.) The grounded conductors ( neutrals in this case ) should be directly connected to the grounding conductors ( ground/bar conductors in this case) at the main service equipment. Separation of these at the source is a problem that has to be addressed as it brings into more questions for me...

Q1: Was their a main bonding jumper at this service equipment and did it provide for the connection of the grounded conductor, grounding conductors and equipment case to all come together? If yes then the separation is fine as long as something is bonding them all together.Thus their only separated in bus design but not in physical design.

Q2: Panel manufacturers will allow multiple ( check the listed for just how many ) equipment grounding conductors (ground in your question) to be under a single lug as long as it meets the listing of the termination. This is found on the manufacturers equipment label but we can use some common sense here....If there are (2) 14 AWG conductors under a single lug for the EGC's then no harm..no foul. If you see (1) 12 AWG and (1) 14 AWG under the same lug...mention it as it would be impossible to properly torque a 12 AWG properly and still have it torque a 14 AWG properly.

Remember that the National Electrical Code is a safety standard no matter how you wish to slice it. The integrity of the available fault current path is reduced when proper terminations and torquing is not maintained. As for code in TN....simply follow the logic of the basic principles of the NEC® and you will be supported.



Paul W. Abernathy
Reply With Quote
  #10  
Old 6/11/11, 5:08 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: What is code and what is not?

Quote:
Originally Posted by belliott View Post
Normally that is not an issue.
Agreed. The NEC does not prohibit "double-tapping" of the grounding conductors.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 6/11/11, 11:37 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: What is code and what is not?

Quote:
Originally Posted by Tammy D. Smith View Post
How can I find out if this is code or not for the state of TN?

ELECTRICAL: PANEL
PROB: THE GROUND AND NEUTRAL WIRES HAVE BEEN SEPARATED, HOWEVER THERE ARE NOW DOUBLE LUGGED GROUND WIRES AT THE BUS BAR INSIDE THE MAIN PANEL.

The information is usually Listed inside the Pane.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 5:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts