Default Code in Mobile homes

I know this isn't to code. There are no stupid questions when it comes to electrical, so here it goes. This is in a 1981 mobile after the inside has been remodeled. Is it possible that this panel was moved from the bedroom wall into the hot water closet? I've recommended that it be inspected by a licensed electrician, is that all I can do on the report, other than state that the valve isn't vented to the outside? Thanks
Attached Thumbnails
code-mobile-homes-hot-h20-and-elec-panel.jpg elec panel.jpg
Views:	82
Size:	66.0 KB
ID:	32827  
Reply With Quote
Find an InterNACHI certified Missouri Home Inspector (and anywhere else in North America)
  #2  
Old 10/24/09, 7:10 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Code in Mobile homes

Leah,

Either the panel or the water heater must be re-located. Code requires a 36" X 30" clearance around all electrical panels.
code-mobile-homes-panel-clearances.jpg
Reply With Quote
  #3  
Old 10/24/09, 7:11 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Code in Mobile homes

Quote:
Originally Posted by lvass View Post
is that all I can do on the report, other than state that the valve isn't vented to the outside? Thanks
The valve vented to the outside?

What valve?

If you're referring to the PTR valve on the water heater, it doesn't need to go outside. It simply needs an extension pipe installed to within 6" of the floor.
Reply With Quote
  #4  
Old 10/24/09, 7:16 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,643
Default Re: Code in Mobile homes

24 CFR 3280 governs the construction of mobile homes, but they are also required to meet the codes of the jurisdictions for which they are being built. If there are codes in your area, have your client do a permit search.

IMO, no reference to codes should be in your report. Simply state that the configuration is unsafe, the electrical panel is not safely accessible, and recommend that a qualified contractor repair it.
Reply With Quote
  #5  
Old 10/24/09, 7:18 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 831
Send a message via Skype™ to pbolliger
Default Re: Code in Mobile homes

From the view in the picture...Is that TPR valve "inside" the panel? Sure looks like that from the picture...maybe the angle is wrong from my perspective..
Reply With Quote
  #6  
Old 10/24/09, 7:20 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 2,778
Default Re: Code in Mobile homes

Agree with David and James above.

Is the TPR actually 'in' the panel, preventing the cover from being installed?

Definately submit the photo to: http://www.nachi.org/forum/f2/best-d...tml#post574722



"You cannot depend on your eyes when your imagination is out of focus"...Mark Twain


Jeffrey R. Jonas
Critical Eye Property Inspections
JRJ Consultants
Owatonna, Minnesota

NACHI07013103
IAC2-01-1567


Reply With Quote
  #7  
Old 10/24/09, 7:21 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 2,778
Default Re: Code in Mobile homes

Quote:
Originally Posted by pbolliger View Post
From the view in the picture...Is that TPR valve "inside" the panel? Sure looks like that from the picture...maybe the angle is wrong from my perspective..

Looks like you posted, while I was busy typing.



"You cannot depend on your eyes when your imagination is out of focus"...Mark Twain


Jeffrey R. Jonas
Critical Eye Property Inspections
JRJ Consultants
Owatonna, Minnesota

NACHI07013103
IAC2-01-1567


Reply With Quote
  #8  
Old 10/24/09, 7:23 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Code in Mobile homes

Nice location to test the PTR capabilities.....
Reply With Quote
  #9  
Old 10/24/09, 8:49 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Code in Mobile homes

Quote:
Originally Posted by lvass View Post
I've recommended that it be inspected by a licensed electrician
No additional inspection is required. This is an issue that needs to be corrected. The cost may be more, but my recommendation would likely be to move the panel from within the closet.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 10/24/09, 9:36 PM
Leah Vass Leah Vass is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Dolores, Co
Posts: 29
Default Re: Code in Mobile homes

The TPR in colorado must be vented outside at least 6 inches above ground. If the panel door was installed, the panel or the TPR valve could not be opened. There would be less then an inch between the two.

I agree that one of them needs to be moved. I won't state that it is a code issue, but I said "Water heater TPR valve vented to inside of electrical panel. Electrical panel has no cover. Recommend it to be addressed by licensed electrician. This is a serious safety issue." Will this cover it?

I've never seen a situation like this one.
Reply With Quote
  #11  
Old 10/25/09, 7:51 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Code in Mobile homes

Quote:
Originally Posted by lvass View Post
The TPR in colorado must be vented outside at least 6 inches above ground. If the panel door was installed, the panel or the TPR valve could not be opened. There would be less then an inch between the two.

I agree that one of them needs to be moved. I won't state that it is a code issue, but I said "Water heater TPR valve vented to inside of electrical panel. Electrical panel has no cover. Recommend it to be addressed by licensed electrician. This is a serious safety issue." Will this cover it?

I've never seen a situation like this one.
Leah,

You should also mention improper clearances to electrical panel. Not to mention the issues inside this panel.
Reply With Quote
  #12  
Old 10/25/09, 8:53 AM
Harry V. McBride, III's Avatar
Harry V. McBride, III Harry V. McBride, III is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Alachua, FL
Posts: 145
Default Re: Code in Mobile homes

That is unbelievable.
Reply With Quote
  #13  
Old 10/26/09, 10:38 AM
Ian A. Niquette's Avatar
Ian A. Niquette Ian A. Niquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,193
Send a message via ICQ to iniquette
Default Re: Code in Mobile homes

Leah, that is an amazing picture. Youshould submit that in the Best Defects Thread here on the board.



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network



What we've got here is......failure......to communicate.....
Reply With Quote
Find an InterNACHI certified Missouri Home Inspector (and anywhere else in North America)
  #14  
Old 10/26/09, 3:04 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: Scottville, Mi
Posts: 930
Default Re: Code in Mobile homes

Quote:
Originally Posted by iniquette View Post
Leah, that is an amazing picture. Youshould submit that in the Best Defects Thread here on the board.
I agree!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Inspector Listings jbowman Misc. Discussion 128 10/27/09 5:28 PM
What's this video worth? jtedesco1 Education 5 4/18/08 10:24 AM
No "H" clips? jbreazeale Structural 7 5/17/07 3:28 PM


All times are GMT -4. The time now is 2:02 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts